The hanger requirements are for pendent heads through a suspended ceiling and 
should be from the maximum pressure that the system at that elevation could 
see.  In this case, the max pressure would be at the churn of your pump added 
to the static pressure as if the pump had just kicked on.  This is probably 
going to be in excess of 160 psi(depending on the churn pressure of your 
specific pump).  At 160 psi, you would have to elevate almost 140 ft above the 
pump discharge flange before the system would not see pressure of 100 psi.  You 
also need to consider if you are exceeding 175 psi on any portion of your 
system (if your pump churn exceeds 95 psi which it could per NFPA 20 (2010) 
Section 6.2.2) as you will need to add high pressure fittings on the 
appropriate downstream system sections or a pressure reducing valve.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-3662

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Craig 
Leadbetter
Sent: Thursday, May 09, 2013 9:08 AM
To: [email protected]
Subject: Hanger Requirement

I am working on a building that has a static pressure of 80 PSI and a residual 
pressure of 50 PSI. The building has a fire pump rated at 750 gal
70 psi.

The questions was raised about the maximum arm over length for sprinklers on 
the 6th floor of the project that is 93' high to the head location. Do I 
determine the working pressure from the static or residual pressure when 
determining if the working pressure is over the 100 PSI requirement to require 
hangers at a maximum of 12"

Thanks in advance for any comments



--
Craig Leadbetter
Safeguard of Marquette
PO Box 116
Marquette, MI 49855

(O) 906-475-9955
(F) 906-475-5474
(C) 906-362-5393

[email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to