Static or Residual pressure...whichever is greater per *9.2.3.4.4.1*

On Thu, May 9, 2013 at 9:07 AM, Craig Leadbetter
<[email protected]>wrote:

> I am working on a building that has a static pressure of 80 PSI and a
> residual pressure of 50 PSI. The building has a fire pump rated at 750 gal
> 70 psi.
>
> The questions was raised about the maximum arm over length for sprinklers
> on the 6th floor of the project that is 93' high to the head location. Do I
> determine the working pressure from the static or residual pressure when
> determining if the working pressure is over the 100 PSI requirement to
> require hangers at a maximum of 12"
>
> Thanks in advance for any comments
>
>
>
> --