Static or Residual pressure...whichever is greater per *9.2.3.4.4.1*
On Thu, May 9, 2013 at 9:07 AM, Craig Leadbetter <[email protected]>wrote: > I am working on a building that has a static pressure of 80 PSI and a > residual pressure of 50 PSI. The building has a fire pump rated at 750 gal > 70 psi. > > The questions was raised about the maximum arm over length for sprinklers > on the 6th floor of the project that is 93' high to the head location. Do I > determine the working pressure from the static or residual pressure when > determining if the working pressure is over the 100 PSI requirement to > require hangers at a maximum of 12" > > Thanks in advance for any comments > > > > -- > Craig Leadbetter > Safeguard of Marquette > PO Box 116 > Marquette, MI 49855 > > (O) 906-475-9955 > (F) 906-475-5474 > (C) 906-362-5393 > > [email protected] > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Greg McGahan Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org