Ryan, Thanks. That was what I was leaning toward but I wanted to make sure my thinking was correct.
On Thu, May 9, 2013 at 10:23 AM, Hinson, Ryan <[email protected]> wrote: > The hanger requirements are for pendent heads through a suspended ceiling > and should be from the maximum pressure that the system at that elevation > could see. In this case, the max pressure would be at the churn of your > pump added to the static pressure as if the pump had just kicked on. This > is probably going to be in excess of 160 psi(depending on the churn > pressure of your specific pump). At 160 psi, you would have to elevate > almost 140 ft above the pump discharge flange before the system would not > see pressure of 100 psi. You also need to consider if you are exceeding > 175 psi on any portion of your system (if your pump churn exceeds 95 psi > which it could per NFPA 20 (2010) Section 6.2.2) as you will need to add > high pressure fittings on the appropriate downstream system sections or a > pressure reducing valve. > > Ryan Hinson > Burns & McDonnell > Direct: 952-656-3662 > > -----Original Message----- > From: [email protected] [mailto: > [email protected]] On Behalf Of Craig > Leadbetter > Sent: Thursday, May 09, 2013 9:08 AM > To: [email protected] > Subject: Hanger Requirement > > I am working on a building that has a static pressure of 80 PSI and a > residual pressure of 50 PSI. The building has a fire pump rated at 750 gal > 70 psi. > > The questions was raised about the maximum arm over length for sprinklers > on the 6th floor of the project that is 93' high to the head location. Do I > determine the working pressure from the static or residual pressure when > determining if the working pressure is over the 100 PSI requirement to > require hangers at a maximum of 12" > > Thanks in advance for any comments > > > > -- > Craig Leadbetter > Safeguard of Marquette > PO Box 116 > Marquette, MI 49855 > > (O) 906-475-9955 > (F) 906-475-5474 > (C) 906-362-5393 > > [email protected] > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Craig Leadbetter Safeguard of Marquette PO Box 116 Marquette, MI 49855 (O) 906-475-9955 (F) 906-475-5474 (C) 906-362-5393 [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org