Ryan,

Thanks. That was what I was leaning toward but I wanted to make sure my
thinking was correct.



On Thu, May 9, 2013 at 10:23 AM, Hinson, Ryan <[email protected]> wrote:

> The hanger requirements are for pendent heads through a suspended ceiling
> and should be from the maximum pressure that the system at that elevation
> could see.  In this case, the max pressure would be at the churn of your
> pump added to the static pressure as if the pump had just kicked on.  This
> is probably going to be in excess of 160 psi(depending on the churn
> pressure of your specific pump).  At 160 psi, you would have to elevate
> almost 140 ft above the pump discharge flange before the system would not
> see pressure of 100 psi.  You also need to consider if you are exceeding
> 175 psi on any portion of your system (if your pump churn exceeds 95 psi
> which it could per NFPA 20 (2010) Section 6.2.2) as you will need to add
> high pressure fittings on the appropriate downstream system sections or a
> pressure reducing valve.
>
> Ryan Hinson
> Burns & McDonnell
> Direct: 952-656-3662
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Craig
> Leadbetter
> Sent: Thursday, May 09, 2013 9:08 AM
> To: [email protected]
> Subject: Hanger Requirement
>
> I am working on a building that has a static pressure of 80 PSI and a
> residual pressure of 50 PSI. The building has a fire pump rated at 750 gal
> 70 psi.
>
> The questions was raised about the maximum arm over length for sprinklers
> on the 6th floor of the project that is 93' high to the head location. Do I
> determine the working pressure from the static or residual pressure when
> determining if the working pressure is over the 100 PSI requirement to
> require hangers at a maximum of 12"
>
> Thanks in advance for any comments
>
>
>
> --
> Craig Leadbetter
> Safeguard of Marquette
> PO Box 116
> Marquette, MI 49855
>
> (O) 906-475-9955
> (F) 906-475-5474
> (C) 906-362-5393
>
> [email protected]
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Craig Leadbetter
Safeguard of Marquette
PO Box 116
Marquette, MI 49855

(O) 906-475-9955
(F) 906-475-5474
(C) 906-362-5393

[email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to