But the IFC says that fire flow MAY be reduced up to 75% as approved by
the Fire Official.  Most jurisdictions that accept a reduction - at
least out here in CA - offer 50%, but not 75%.  I have dealt with fire
departments that only offer 25% when certain more hazardous conditions
exist, such as Type V wood framed buildings over a certain height, like
three or four stories.  And we have one FD here in San Diego county that
offers NO reduction, which makes for a lot of "Oh Sh*t!" moments on
larger projects when the fire flow calc's out to 4,500 or 5,000 gpm.
Usually followed by "The 2-Hour Wall Game" and fire sprinkler density
upgrades ...

Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Johnson, Duane (NIH/OD/ORS) [C]
Sent: Monday, May 13, 2013 11:12 AM
To: [email protected]
Subject: RE: Sizing tanks with hydrants?

Forgot this one: 

NFPA 1:18.4.5.2.1   Required fire flow shall be reduced by 75 percent
when the building is protected throughout by an approved automatic
sprinkler system. The resulting fire flow shall not be less than 1000
gpm (3785 L/min).

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor) Office of Research Services
National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Johnson, Duane (NIH/OD/ORS) [C]
Sent: Monday, May 13, 2013 2:10 PM
To: [email protected]
Subject: RE: Sizing tanks with hydrants?

NFPA 1:18.4.1* Scope.  

A.18.4.1   Section 18.4 and the associated tables are only applicable
for determining minimum water supplies for manual fire suppression
efforts. Water supplies for fire protection systems are not addressed by
this section. It is not the intent to add the minimum fire protection
water supplies, such as for a fire sprinkler system, to the minimum fire
flow for manual fire suppression purposes required by this section.

>From the Handbook:

The explanatory material in A.18.4.1 clarifies that the intent of the
Code is not to add the fire flow calculated in accordance with Section
18.4 to an automatic sprinkler system demand. For sprinklered buildings,
the required water supply should be the greater of either that specified
by Section 18.4 or the demand for the automatic sprinkler system.
Section 18.4 is used to calculate the required fire flow for manual
fire-fighting purposes and does not take into account fire suppression
systems or hose stream requirements required by other codes and
standards, such as NFPA 13, Standard for the Installation of Sprinkler
Systems. Fire protection system water supply requirements are not
permitted to take advantage of the reduction in fire flow in 18.4.5.

If you are in a rural area, see also NFPA 1142. There is another method
to calculate the required water supply...

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor) Office of Research Services
National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"

-----Original Message-----
From: Bobby Gillett [mailto:[email protected]]
Sent: Monday, May 13, 2013 2:04 PM
To: [email protected]
Subject: RE: Sizing tanks with hydrants?

No. This is a tech school. 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
www.keyfireprotection.com
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Art
Tiroly
Sent: Monday, May 13, 2013 12:48 PM
To: [email protected]
Subject: RE: Sizing tanks with hydrants?

The building will never be used for high piled storage right? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Bobby Gillett
Sent: Monday, May 13, 2013 1:19 PM
To: [email protected]
Subject: Sizing tanks with hydrants?

When sizing a water storage tank feeding a fire pump for a new facility
with multiple sprinkler systems and fire hydrants, do you have to
include any type of allowance for the hydrants? The tank will be the
sole source of supply for all (rural area). There will be no hose
stations or standpipes, only interior sprinkler systems - OH Group II
with monitored alarms.
Typically this would be an 18,000 gallon tank minimum (.20x1500x60
mins). I don't see anywhere that requires this, just making sure.

 

Thank you in advance.

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <http://www.keyfireprotection.com> www.keyfireprotection.com

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org



-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2241 / Virus Database: 3162/5820 - Release Date:
05/13/13

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.3336 / Virus Database: 3162/6313 - Release Date:
05/10/13

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to