You are correct, it all depends on the applicable code and approved ammendments.

NFPA 1:
18.4.5.2.1   Required fire flow shall be reduced by 75 percent when the 
building is protected throughout by an approved automatic sprinkler system. The 
resulting fire flow shall not be less than 1000 gpm (3785 L/min).
18.4.5.2.2   Required fire flow shall be reduced by 75 percent when the 
building is protected throughout by an approved automatic sprinkler system, 
which utilizes quick response sprinklers throughout. The resulting fire flow 
shall not be less than 600 gpm (2270 L/min).

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Steve Leyton [mailto:[email protected]] 
Sent: Monday, May 13, 2013 2:16 PM
To: [email protected]
Subject: RE: Sizing tanks with hydrants?

But the IFC says that fire flow MAY be reduced up to 75% as approved by the 
Fire Official.  Most jurisdictions that accept a reduction - at least out here 
in CA - offer 50%, but not 75%.  I have dealt with fire departments that only 
offer 25% when certain more hazardous conditions exist, such as Type V wood 
framed buildings over a certain height, like three or four stories.  And we 
have one FD here in San Diego county that offers NO reduction, which makes for 
a lot of "Oh Sh*t!" moments on larger projects when the fire flow calc's out to 
4,500 or 5,000 gpm.
Usually followed by "The 2-Hour Wall Game" and fire sprinkler density upgrades 
...

Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson, 
Duane (NIH/OD/ORS) [C]
Sent: Monday, May 13, 2013 11:12 AM
To: [email protected]
Subject: RE: Sizing tanks with hydrants?

Forgot this one: 

NFPA 1:18.4.5.2.1   Required fire flow shall be reduced by 75 percent
when the building is protected throughout by an approved automatic sprinkler 
system. The resulting fire flow shall not be less than 1000 gpm (3785 L/min).

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor) Office of Research Services National 
Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Johnson, Duane (NIH/OD/ORS) [C]
Sent: Monday, May 13, 2013 2:10 PM
To: [email protected]
Subject: RE: Sizing tanks with hydrants?

NFPA 1:18.4.1* Scope.  

A.18.4.1   Section 18.4 and the associated tables are only applicable
for determining minimum water supplies for manual fire suppression efforts. 
Water supplies for fire protection systems are not addressed by this section. 
It is not the intent to add the minimum fire protection water supplies, such as 
for a fire sprinkler system, to the minimum fire flow for manual fire 
suppression purposes required by this section.

>From the Handbook:

The explanatory material in A.18.4.1 clarifies that the intent of the Code is 
not to add the fire flow calculated in accordance with Section
18.4 to an automatic sprinkler system demand. For sprinklered buildings, the 
required water supply should be the greater of either that specified by Section 
18.4 or the demand for the automatic sprinkler system.
Section 18.4 is used to calculate the required fire flow for manual 
fire-fighting purposes and does not take into account fire suppression systems 
or hose stream requirements required by other codes and standards, such as NFPA 
13, Standard for the Installation of Sprinkler Systems. Fire protection system 
water supply requirements are not permitted to take advantage of the reduction 
in fire flow in 18.4.5.

If you are in a rural area, see also NFPA 1142. There is another method to 
calculate the required water supply...

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor) Office of Research Services National 
Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"

-----Original Message-----
From: Bobby Gillett [mailto:[email protected]]
Sent: Monday, May 13, 2013 2:04 PM
To: [email protected]
Subject: RE: Sizing tanks with hydrants?

No. This is a tech school. 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
www.keyfireprotection.com
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Art Tiroly
Sent: Monday, May 13, 2013 12:48 PM
To: [email protected]
Subject: RE: Sizing tanks with hydrants?

The building will never be used for high piled storage right? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby 
Gillett
Sent: Monday, May 13, 2013 1:19 PM
To: [email protected]
Subject: Sizing tanks with hydrants?

When sizing a water storage tank feeding a fire pump for a new facility with 
multiple sprinkler systems and fire hydrants, do you have to include any type 
of allowance for the hydrants? The tank will be the sole source of supply for 
all (rural area). There will be no hose stations or standpipes, only interior 
sprinkler systems - OH Group II with monitored alarms.
Typically this would be an 18,000 gallon tank minimum (.20x1500x60 mins). I 
don't see anywhere that requires this, just making sure.

 

Thank you in advance.

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <http://www.keyfireprotection.com> www.keyfireprotection.com

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org



-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2241 / Virus Database: 3162/5820 - Release Date:
05/13/13

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.3336 / Virus Database: 3162/6313 - Release Date:
05/10/13

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to