The project is a Class IC storage facility storing lampricide in 5 gallon
containers with rack storage that is 2400 sqft. With a required .45/3000
plus 500 PGM for two hours the cost of the water supply is going to
outweigh the cost of the building.

The site is remote and there is no municipal water available.   If I have
done my research through NFPA 30 correctly we are looking at a tank that is
200,000 gallons or more. Unfortunately the site has existing buildings and
the site plan does not allow the space for a non-protected building

I was just trying to come up with a reasonable costing fire protection
system although there may be nothing that is reasonable for this facility.


On Mon, May 13, 2013 at 2:17 PM, <[email protected]> wrote:

> Is it bigger than a breadbox?
>
> Dry chem. Is typically reserved for protecting areas inside equipment.
>  Not occupied or potentially occupied spaces.
>
> For large areas there are so many problems with keeping the area tight to
> contain gas such as FM-200 that it would be virtually impossible. Also gas
> systems aren't going to suitable for every commodity.  And lastly, if the
> Codes require sprinkler protection, most AHJ's aren't going to go along
> with a gas only system as primary.
>
> So the questions arises as to why do you want to use gas instead of
> sprinklers?
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Craig
> Leadbetter
> Sent: Monday, May 13, 2013 1:56 PM
> To: [email protected]
> Subject: Extra Hazard storage
>
> Can an extra hazard storage facility be protected by a gas system or dry
> chemical system?
>
>
>
> --
> Craig Leadbetter
> Safeguard of Marquette
> PO Box 116
> Marquette, MI 49855
>
> (O) 906-475-9955
> (F) 906-475-5474
> (C) 906-362-5393
>
> [email protected]
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Craig Leadbetter
Safeguard of Marquette
PO Box 116
Marquette, MI 49855

(O) 906-475-9955
(F) 906-475-5474
(C) 906-362-5393

[email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to