Yes. As in years ago the dry sidewall sprinklers which weren't listed for residential use but required on porches
Sent from my iPhone On Jul 10, 2013, at 3:24 PM, Roland Huggins <[email protected]> wrote: > I have to say I disagree and based on several actions in NFPA 13. the > technical committee think that the code (or installation standard) trumps the > listing. > > Roland Huggins, PE - VP Engineering > American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives > Dallas, TX > http://www.firesprinkler.org > > > > > > On Jul 10, 2013, at 12:10 PM, <[email protected]> wrote: > >> "Code trumps listings is the way I read it and this new section says nothing >> about DI." >> >> Code can never trump manufacturers listing limitations otherwise you're >> using the product outside of the mfgrs intended use. NFPA 13-2013 6.3.7.1 & >> 6.3.7.1.1 >> > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org