Yes, but if it's not rated I would say you need to do a design for EH II that 
encompasses the booth, the mixing room, and adjacent spaces (assuming no 2-hour 
separations from adjacent uses) up to the required design area in 11.2.3.1.1.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [email protected] on behalf of Douglas Hicks
Sent: Fri 7/26/2013 10:09 AM
To: [email protected]
Subject: Paint booth
 
I have been asked by a local school district about protecting an automotive 
paint booth.  The catch, the booth is 2 x 4 framed, covered with sheet rock.  
The exhaust duct work does not have filters, and the exhaust fan may not be 
rated for hazardous paint fumes.  The booth does not meet any UL standards, so 
I cannot install a dry chemical suppression system.  Will a  water based 
sprinkler work? 