Agree with Steve, with adding that the ceiling protection of the room the PB is in will need to be .4/2000. You probably meant this when you said "adjacent spaces".
Bob Knight, CET III 208-318-3057 www.firebyknight.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Friday, July 26, 2013 11:10 AM To: [email protected]; [email protected] Subject: RE: Paint booth Yes, but if it's not rated I would say you need to do a design for EH II that encompasses the booth, the mixing room, and adjacent spaces (assuming no 2-hour separations from adjacent uses) up to the required design area in 11.2.3.1.1. Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [email protected] on behalf of Douglas Hicks Sent: Fri 7/26/2013 10:09 AM To: [email protected] Subject: Paint booth I have been asked by a local school district about protecting an automotive paint booth. The catch, the booth is 2 x 4 framed, covered with sheet rock. The exhaust duct work does not have filters, and the exhaust fan may not be rated for hazardous paint fumes. The booth does not meet any UL standards, so I cannot install a dry chemical suppression system. Will a water based sprinkler work? _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ----- No virus found in this message. Checked by AVG - www.avg.com Version: 2013.0.3349 / Virus Database: 3209/6521 - Release Date: 07/25/13 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org