And the plenum and stack.

On Fri, Jul 26, 2013 at 10:17 AM, Bob <[email protected]> wrote:

> Agree with Steve, with adding that the ceiling protection of the room the
> PB
> is in will need to be .4/2000.  You probably meant this when you said
> "adjacent spaces".
>
> Bob Knight, CET III
> 208-318-3057
> www.firebyknight.com
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve
> Leyton
> Sent: Friday, July 26, 2013 11:10 AM
> To: [email protected];
> [email protected]
> Subject: RE: Paint booth
>
> Yes, but if it's not rated I would say you need to do a design for EH II
> that encompasses the booth, the mixing room, and adjacent spaces (assuming
> no 2-hour separations from adjacent uses) up to the required design area in
> 11.2.3.1.1.
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>
>
> -----Original Message-----
> From: [email protected] on behalf of Douglas
> Hicks
> Sent: Fri 7/26/2013 10:09 AM
> To: [email protected]
> Subject: Paint booth
>
> I have been asked by a local school district about protecting an automotive
> paint booth.  The catch, the booth is 2 x 4 framed, covered with sheet
> rock.
> The exhaust duct work does not have filters, and the exhaust fan may not be
> rated for hazardous paint fumes.  The booth does not meet any UL standards,
> so I cannot install a dry chemical suppression system.  Will a  water based
> sprinkler work?
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2013.0.3349 / Virus Database: 3209/6521 - Release Date: 07/25/13
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to