Is this "forward flow test" now part of the required code? I was just on a  
job the other day. New Construction. I noticed that all the systems had a 
setup  with (2) 2 1/2" hose valves after the backflow and alarm valve, in 
addition to  the 2" main drain. I take it that these 2 1/2's are for this test?
 
 
In a message dated 7/29/2013 3:57:24 P.M. Eastern Daylight Time,  
[email protected] writes:

That  isn't what the intent of the code is as stated.....just flow at  
system
demand. I can only speak for us, but we do a LOT of risers with only  a 250
gpm or so demand...sometimes even less.

A 4" drain is well  over what we need to open it up enough for system
demand. I would bet a 2"  drain gets really close.


On Mon, Jul 29, 2013 at 2:52 PM, David  Autry <[email protected]> wrote:

> Wouldn't it be easier, if  you have a 4" backflow preventer you run 4" out
> the wall, 3" BFP, 3"  out the wall, etc...
> That should open her up all the  way.
>
>
> David Autry
>
> Meininger Fire  Protection Inc.
> 2521 W L St. Suite No.4
> Lincoln, Ne  68522
> Voice (402) 466-2616
> Fax (402) 466-2617
>  [email protected]
>
> -----Original Message-----
> From:  [email protected]
>  [mailto:[email protected]] On Behalf Of  
Greg
> McGahan
> Sent: Monday, July 29, 2013 2:35 PM
> To:  [email protected]
> Subject: Re: SIGN for Backflow  Prevention Assembly Forward Flow Test
>
> What would be simple and  helpful would be a table similar to the one used
> for sizing fire pump  Suction/Discharge/Relief Valve Piping etc.
>
> Since you are not  measuring pressure, you could say 2" up to X gallons,
> 2.5" for Y  etc....
>
> A 2-1/2" Main drain is much easier and cheaper than  some of the
> arrangments left / required on backflow  preventers.
>
> Greg
>
>
> On Mon, Jul 29, 2013  at 12:46 PM, Ron Greenman
>  <[email protected]>wrote:
>
> > Better but it is  still interpretable as requiring a measured flow be
> > established  (if using the main drain location then the BOR design 
data).
> > Then  you'd need a port that flowed that much, main drain or otherwise,
> >  and then measure your annual test against anticipated flow to make
>  > sure you are meeting or exceeding the required flow. Or am I  missing
> > something? I'm pretty certain that newer fire service  rated backflows
> > don't fail any more often than normal FS checks,  and that that type of
> > failure is either catastrophic (doesn't  open or barely opens) wouldn't
> > a simple main drain test with  decent flow demonstrate that the valve
> > is working? just a Forum  question as this is a done deal and I wasn't
> > invited to join the  exclusive
> > 25 club.
> >
> >
> > On Mon,  Jul 29, 2013 at 7:11 AM, Roland Huggins
> >  <[email protected]>wrote:
> >
> > > the  next edition has been cleaned-up on this issue.
> > >
> >  > _______________________________________________________________
>  > > 25-271
> > Log
> > > #CP15 Final Action:  Accept
> > > (13.6.2.1, 13.6.2.2 (New))
> > >  _______________________________________________________________
> >  Submitter:
> > > Technical Committee on Inspection, Testing, and  Maintenance of
> > Water-Based
> > > Systems,
>  > >
> > > Recommendation: Revise 13.6.2.1 to read as  follows:
> > > 13.6.2.1 All backflow preventers installed in fire  protection system
> > > piping shall be exercised annually by  conducting a forward flow test
> > > at a minimum flow rate of the  system design.
> > > Add new 13.6.2.2 and renumber subsequent  sections accordingly:
> > > 13.6.2.2 Where hydrants or inside hose  stations are located
> > > downstream of the backflow preventer,  the forward flow test shall
> > > include hose stream demand.  Substantiation: This change was needed
> > > to better reflect  that the backflow preventer is not a precise test
> > > whereby  the flow through it must be measured but effort to exercise
> > >  the device at flows as near as
> > possible
> > > to the  system demand.
> > > Committee Meeting Action: Accept
> >  > Number Eligible to Vote: 33
> > > Ballot Results:  Affirmative: 32 Negative: 1 Explanation of Negative:
> > >
>  > > RAY, R.: This proposal should have been accepted in principle:  the
> > wording
> > > "at a minimum flow rate" is  confusing and should be reworded.
> > >  _______________________________________________________________
> >  > 25-272
> > Log
> > > #121 Final Action:  Accept
> > >
> > > (13.6.2.1.1)
> >  >
> > >  _______________________________________________________________
> >  Submitter:
> > > Roland J. Huggins, American Fire Sprinkler  Association, Inc.
> > > Recommendation: Delete the following  text:
> > >
> > > 13.6.2.1.1 For backflow preventers  sized 2 in. (50 mm) and under,
> > > the forward flow test shall  be acceptable to conduct without
> > > measuring flow, where the  test outlet is of a size to flow the system
> demand.
> > >  Substantiation: This section implies that a measured flow is
> > >  required for Backflow preventers (BFP) larger than 2 in when nothing
>  > > in 13.6.2.1
> > states
> > > such a  requirement. There are other means to identify that the
> > >  system demand is flowing through the BFP as discussed in A.13.6.2.1
>  > > It also
> > needs
> > > to be kept in mind that  we are simply exercising the BFP to ensure
> > > it
> >  will
> > > fully open at approximately the system demand. A high  degree of
> > > accuracy regarding the volume of water is not  warranted.
> > > Additionally, BFP's are subjected to an annual  internal inspection
> > > as part of the cross
> >  connection
> > > protection program. Committee Meeting Action:  Accept Number Eligible
> > > to Vote: 33 Ballot Results:  Affirmative: 33
> > >
> > >
> > >
>  > > Roland Huggins, PE - VP Engineering
> > >
> >  > American Fire Sprinkler Assn.       ---     Fire Sprinklers Saves
> Lives
> > > Dallas,  TX
> > > http://www.firesprinkler.org
> > >
>  > >
> > >
> > >
> > >
> >  > On Jul 26, 2013, at 2:57 PM, Dwight Havens  <[email protected]>
> > wrote:
> > >
>  > > > Then they ought to say that in the code language.
> >  > >
> > > > Dwight
> > > >
> >  > >
> > > >
> > > >
> > > >  ________________________________
> > > > From: John Denhardt  <[email protected]>
> > > > To:  "[email protected]" <
> > >  [email protected]>
> > > > Sent:  Thursday, July 25, 2013 3:07 PM
> > > > Subject: RE: SIGN for  Backflow Prevention Assembly Forward Flow
> > > > Test
>  > > >
> > > >
> > > > While I do  disagree to some extent of what the NFPA 25 committee
> > > >  has
> > > done, Roland statement is correct.  I have had  numerous discussions
> > > with NFPA 25 committee members where  they have stated the intent was
> > > to
> >  exercise
> > > the device at near system demand.  The key  word to me was "Exercise".
> > > >
> > > >  John
> > > >
> > > > John August Denhardt, P.E.,  FSFPE
> > > > Strickland Fire Protection Incorporated
>  > > > 5113 Berwyn Road
> > > > College Park, Maryland  20740
> > > > Office Telephone Number:  301-474-1136  Mobile Telephone Number:
> > > > 301-343-1457 FIRE SPRINKLERS  SAVE LIVES - Can you live without
> > > > them?
> >  > >
> > > > -----Original Message-----
> > >  > From: [email protected] [mailto:
>  > > [email protected]] On Behalf Of  Forest
> > Wilson
> > > > Sent: Thursday, July 25,  2013 2:42 PM
> > > > To:  [email protected]
> > > > Subject: Re:  SIGN for Backflow Prevention Assembly Forward Flow
> > > >  Test
> > > >
> > > > Here is an email on this  topic that Roland addressed in the past:
> > > >
> >  > > Im not going to say it was one of those casual assumptions  that
> > > > all systems are calculated nor that all risers  have placards.  The
> > > > main thing to keep in mind  that the intent is simply to fully
> > > > EXERCISE the BFP at  what os expected to be the system demand.  If
> > > > no  data available, a discussion with the AHJ is warranted.  As for
>  > > > benchmarks, only the flow is pertinent and pressure is  irrelevant.
> > > >
> > > > Roland
> >  > >
> > > > On Dec 22, 2009, at 2:44 PM, Matthew J.  Willis wrote:
> > > >
> > > >>>
>  > > >>> On a more important matter: If a system was retrofitted  with a
> > > >>> backflow,
> > > >>  and
> > > >>> there is no hydraulic calc plaque attached  to the riser, and
> > > >>> NFPA requires forward flow  testing of backflows, how can you
> > > >>> conduct the  test without a benchmark to test against?
> > >  >>>
> > > >>> What is the recommended practice  in this scenario?
> > > >>> Forest Wilson
> >  > >
> > > > Sent from my iPhone
> > >  >
> > > > On Jul 25, 2013, at 12:16 PM, Ron Greenman  <[email protected]>
> > > wrote:
> > >  >
> > > >> Then subjective good flow demonstrates a  working valve? If so all
> > > >> the numbers bantered  around are pretty meaningless.
> > > >>
> > >  >>
> > > >>
> > > >> On Thu, Jul 25,  2013 at 8:07 AM, Forest Wilson
> > > >>  <[email protected]
> > > >wrote:
> > >  >>
> > > >>> No.
> > > >>> The  intent is not to pitot the output but to exercise the valve.
> > >  >>>
> > > >>>
> > > >>>  Sent from my iPhone
> > > >>>
> > >  >>> On Jul 25, 2013, at 10:56 AM, Ron Greenman
> > >  >>> <[email protected]>
> > > wrote:
>  > > >>>
> > > >>>> Forest. What were  you flowing to discover these failures? Main
> > >  >>>> drain
> > > or
> > > >>>>  some special test header? Would a sign with the data requested
> >  > >>>> by
> > the
> > > >>>>  customer that started this thread have had any utility in
> > >  >>>> helping
> > you
> > > >>>>  discover the problem?
> > > >>>>
> > >  >>>> Then back to that perennial question of what's a "full flow  "
> > > >>>> test
> > and
> > >  >>> how
> > > >>>> do you do one? I think  Roland said the intent was to flow an
> > > equivalent
>  > > >>> to
> > > >>>> the design  discharge criteria. How do you do this? Do we run a
> > >  >>>> pitot somewhere on the system? Do we catch and  measure
> > > >>>> discharge? If so,
> > >  from
> > > >>>> where? How do we arrange the test  port(s)? Do we flow the
> > > >>>> design
> >  area
> > > or
> > > >>>> simulate it  elsewhere? Do we need results of at least or better
> > >  >>>> flow
> > > or
> > > >>>>  right on the money flow? If not either of those how do we judge?
> >  > >>>>
> > > >>>> Doesn't the hydraulic  data plate note the required psi per the
> > > >>>>  calcs
> > > at
> > > >>> the
> >  > >>>> BOR and the static? Isn't the difference the residual  drop at
> > > >>>> that
> > >  point
> > > >>>> relative to the design area? Wouldn't  a main drain with good
> > > >>>> flow
> > at  a
> > > >>> psi
> > > >>>> around  the BOR rating, and returning to close to the noted
> > >  >>>> static
> > when
> > > >>>>  terminated suggest a fully open valve, or an adequately open
> > >  >>>> valve
> > if
> > > the
> > >  >>>> UG is oversized? In the latter case the partially open valve  is
> > > >>> equivalent
> > >  >>>> to fully open for the system I just described. Am I  missing
> > something
> > > >>> here?
>  > > >>>> An erroneous a priori? My understanding of  hydraulics wrong?
> > > >>>> Main
> > >  drains
> > > >>>> are too small to simulate the result  of all design area heads
> > flowing
> > > as
>  > > >>>> the water passes through the BOR?
> > >  >>>>
> > > >>>>
> > >  >>>> On Thu, Jul 25, 2013 at 7:34 AM, Forest Wilson <
>  > [email protected]
> > > >>>> wrote:
>  > > >>>>
> > > >>>>> I still have  the check valve from a Ames that failed to open.
> > >  >>>>> It was jammed shut, discovered when I was called out  because
> > > >>>>> they
> > >  >>> couldn't
> > > >>>>> do the fire pump  test.
> > > >>>>>
> > >  >>>>> In another case, I tested a backflow and it failed (on a  Best
> > > >>>>> Buy
> > > >>>  store).
> > > >>>>> I opened the valve up and the  check was damaged, would only
> > > >>>>> open  a
> > > >>> third.
> > >  >>>>>
> > > >>>>>
> > >  >>>>>
> > > >>>>> Sent from my  iPhone
> > > >>>>>
> > >  >>>>> On Jul 24, 2013, at 8:53 PM, Ron Greenman
> >  > >>>>> <[email protected]>
> > >  >>> wrote:
> > > >>>>>
> > >  >>>>>> Worked well for plumbing and process piping  applications as
> > > >>>>>> they
> >  are
> > > >>>>>> constantly being  exercised.
> > > >>>>>>
> > >  >>>>>>
> > > >>>>>> On Wed,  Jul 24, 2013 at 5:12 PM, Dwight Havens <
> > >  [email protected]
> > > >>>>>>  wrote:
> > > >>>>>>
> > >  >>>>>>> I do remember the ones with the rods in the  center of the
> > > >>>>>>> valve
>  > > being
> > > >>>>>>> particularly  poor.
> > > >>>>>>>
> > >  >>>>>>> Dwight
> > >  >>>>>>>
> > >  >>>>>>>
> > >  >>>>>>>
> > >  >>>>>>>
> > > >>>>>>>  ________________________________
> > >  >>>>>>> From: Ron Greenman  <[email protected]>
> > > >>>>>>>  To: [email protected]
> > >  >>>>>>> Sent: Tuesday, July 23, 2013 11:25 PM
>  > > >>>>>>> Subject: Re: SIGN for Backflow  Prevention Assembly Forward
> > > >>>>>>>  Flow
> > > Test
> > >  >>>>>>>
> > >  >>>>>>>
> > > >>>>>>> By  the mid-nineties you have the early Ames models purpose
> > >  >>>>>>> built
> > > for
> > >  >>>>>>> sprinklers readily available, but many units  being installed
> > > >>>>>>> are
>  > > still
> > > >>>>> not
> > >  >>>>>>> listed for fire service as many jurisdictions  don't consider
> > > >>>>>>> the
> >  > fire
> > > >>>>> line
> > >  >>>>>>> a fire line until after the backflow, and a n  on-listed
> > > >>>>>>> device is
>  > > >>>>> cheaper
> > >  >>>>>>> than a listed one. Plus many go back to the  seventies and
> > > >>>>>>> many
> >  used
> > > >>>>> weights
> > >  >>>>>>> instead of springs and complicated lever systems  for joining
> > > >>>>>>> the
> >  > >>>>> clappers
> > >  >>>>>>> and weights. Wish I could post a picture.
>  > > >>>>>>>
> > >  >>>>>>>
> > > >>>>>>> On  Tue, Jul 23, 2013 at 7:33 PM, Dwight Havens <
> > >  [email protected]
> > > >>>>>>>>  wrote:
> > > >>>>>>>
> > >  >>>>>>>> Give me a time frame. My best recollection is  the mid 
'90's.
> > > >>>>>>>>
> >  > >>>>>>>> Dwight
> > >  >>>>>>>>
> > >  >>>>>>>>
> > >  >>>>>>>>
> > >  >>>>>>>>
> > >  >>>>>>>> ________________________________
> >  > >>>>>>>> From: Ron Greenman  <[email protected]>
> > >  >>>>>>>> To:  [email protected]
> > >  >>>>>>>> Sent: Tuesday, July 23, 2013 9:12 PM
>  > > >>>>>>>> Subject: Re: SIGN for Backflow  Prevention Assembly Forward
> > > >>>>>>>>  Flow
> > > Test
> > >  >>>>>>>>
> > >  >>>>>>>>
> > >  >>>>>>>> Were these the plumbing type before fire  service listed
> > > >>>>>>>>  devices
> > > >>>>> existed.
> > >  >>>>>>>>
> > >  >>>>>>>>
> > >  >>>>>>>> On Tue, Jul 23, 2013 at 4:32 PM, Dwight  Havens <
> > > >>> [email protected]
> >  > >>>>>>>>> wrote:
> > >  >>>>>>>>
> > >  >>>>>>>>> Yes, yes, and yes.  The original  proposal was based on
> > > >>>>>>>>>  observed
> > > >>>>>>> failures
> >  > >>>>>>>>> of BFPAs to operate properly during  main drain testing.
> > >  >>>>>>>>>
> > >  >>>>>>>>> Glendale, AZ public library specifically  comes to mind.
> > > >>>>>>>>>
>  > > >>>>>>>>> Dwight
> > >  >>>>>>>>>
> > >  >>>>>>>>>
> > >  >>>>>>>>>
> > >  >>>>>>>>>
> > >  >>>>>>>>> ________________________________
>  > > >>>>>>>>> From: Todd Williams  <[email protected]>
> > > >>>>>>>>>  To: "[email protected]" <
> > >  >>>>>>>>>  [email protected]>
> > >  >>>>>>>>> Sent: Monday, July 22, 2013 9:32  PM
> > > >>>>>>>>> Subject: Re: SIGN  for Backflow Prevention Assembly Forward
> > >  >>>>>>>>> Flow
> > > Test
> >  > >>>>>>>>>
> > >  >>>>>>>>>
> > >  >>>>>>>>> Has there ever been an instance of system  failure due to
> > > >>>>>>>>>  the
> > > >>> backflow
> > >  >>>>>>> not
> > >  >>>>>>>>> properly opening? How about detection of  a BFP problem
> > > >>>>>>>>> during  a
> > > full
> > > >>>>>>>  flow
> > > >>>>>>>>> test. How about  something subsequent to the initial
> acceptance?
> > >  >>>>>>>>>
> > >  >>>>>>>>> Todd G Williams, PE
> > >  >>>>>>>>> Fire Protection Design/Consulting  Stonington, CT
> > > >>>>>>>>>  860-535-2080
> > > >>>>>>>>>  www.fpdc.com
> > > >>>>>>>>>
>  > > >>>>>>>>>  _______________________________________________
> > >  >>>>>>>>> Sprinklerforum mailing list
> >  > >>>>>>>>>  [email protected]
> > >  >>>>>>>>>
> > >  >>>>>>>>>
> > >  >>>>>>>>
> > >  >>>>>>>
> > > >>>>>
>  > > >>>
> > >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> > > >>>>>>>>>  _______________________________________________
> > >  >>>>>>>>> Sprinklerforum mailing list
> >  > >>>>>>>>>  [email protected]
> > >  >>>>>>>>>
> > >  >>>>>>>>>
> > >  >>>>>>>>
> > >  >>>>>>>
> > > >>>>>
>  > > >>>
> > >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> > > >>>>>>>>>
>  > > >>>>>>>>
> > >  >>>>>>>>
> > >  >>>>>>>>
> > >  >>>>>>>> --
> > >  >>>>>>>> Ron Greenman
> > >  >>>>>>>> Instructor
> > >  >>>>>>>> Fire Protection Engineering Technology Bates  Technical
> > > >>>>>>>> College
>  > > >>>>>>>> 1101 So. Yakima Ave.
> >  > >>>>>>>> Tacoma, WA 98405
> > >  >>>>>>>>
> > >  >>>>>>>> [email protected]
> > >  >>>>>>>>
> > >  >>>>>>>>  http://www.bates.ctc.edu/fireprotection/
> > >  >>>>>>>>
> > >  >>>>>>>> 253.680.7346
> > >  >>>>>>>> 253.576.9700 (cell)
> > >  >>>>>>>>
> > >  >>>>>>>> Member:
> > >  >>>>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA,  NIBS, WSAFM,
> > > >>>>>>>> WFC,
>  > WFSC
> > > >>>>>>>>
> > >  >>>>>>>> They are happy men whose natures sort with  their vocations.
> > > -Francis
> > >  >>>>>>> Bacon,
> > >  >>>>>>>> essayist, philosopher, and statesman  (1561-1626)
> > > >>>>>>>>  _______________________________________________
> > >  >>>>>>>> Sprinklerforum mailing list
> > >  >>>>>>>>  [email protected]
> > >  >>>>>>>>
> > >  >>>>>>>>
> > >  >>>>>>>
> > > >>>>>
>  > > >>>
> > >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> > > >>>>>>>>  _______________________________________________
> > >  >>>>>>>> Sprinklerforum mailing list
> > >  >>>>>>>>  [email protected]
> > >  >>>>>>>>
> > >  >>>>>>>>
> > >  >>>>>>>
> > > >>>>>
>  > > >>>
> > >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> > > >>>>>>>>
> >  > >>>>>>>
> > >  >>>>>>>
> > >  >>>>>>>
> > > >>>>>>>  --
> > > >>>>>>> Ron Greenman
> >  > >>>>>>> Instructor
> > >  >>>>>>> Fire Protection Engineering Technology Bates  Technical
> > > >>>>>>> College
> >  > >>>>>>> 1101 So. Yakima Ave.
> > >  >>>>>>> Tacoma, WA 98405
> > >  >>>>>>>
> > > >>>>>>>  [email protected]
> > > >>>>>>>
>  > > >>>>>>>  http://www.bates.ctc.edu/fireprotection/
> > >  >>>>>>>
> > > >>>>>>>  253.680.7346
> > > >>>>>>> 253.576.9700  (cell)
> > > >>>>>>>
> > >  >>>>>>> Member:
> > >  >>>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS,  WSAFM, WFC,
> > > >>>>>>> WFSC
> >  > >>>>>>>
> > >  >>>>>>> They are happy men whose natures sort with their  vocations.
> > > -Francis
> > > >>>>>  Bacon,
> > > >>>>>>> essayist, philosopher,  and statesman (1561-1626)
> > > >>>>>>>  _______________________________________________
> > >  >>>>>>> Sprinklerforum mailing list
> > >  >>>>>>> [email protected]
>  > > >>>>>>>
> > >  >>>>>>>
> > > >>>>>
>  > > >>>
> > >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> > > >>>>>>>  _______________________________________________
> > >  >>>>>>> Sprinklerforum mailing list
> > >  >>>>>>> [email protected]
>  > > >>>>>>>
> > >  >>>>>>>
> > > >>>>>
>  > > >>>
> > >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> > > >>>>>>>
> > >  >>>>>>
> > > >>>>>>
>  > > >>>>>>
> > > >>>>>>  --
> > > >>>>>> Ron Greenman
> > >  >>>>>> Instructor
> > > >>>>>>  Fire Protection Engineering Technology Bates Technical
> > >  >>>>>> College
> > > >>>>>>  1101 So. Yakima Ave.
> > > >>>>>> Tacoma, WA  98405
> > > >>>>>>
> > >  >>>>>> [email protected]
> > >  >>>>>>
> > > >>>>>>  http://www.bates.ctc.edu/fireprotection/
> > >  >>>>>>
> > > >>>>>>  253.680.7346
> > > >>>>>> 253.576.9700  (cell)
> > > >>>>>>
> > >  >>>>>> Member:
> > > >>>>>>  ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC,
> > >  >>>>>> WFSC
> > >  >>>>>>
> > > >>>>>> They are  happy men whose natures sort with their vocations.
> >  -Francis
> > > >>>>> Bacon,
> > >  >>>>>> essayist, philosopher, and statesman  (1561-1626)
> > > >>>>>>  _______________________________________________
> > >  >>>>>> Sprinklerforum mailing list
> > >  >>>>>> [email protected]
> >  > >>>>>>
> > > >>>>>
>  > > >>>
> > >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> > > >>>>>  _______________________________________________
> > >  >>>>> Sprinklerforum mailing list
> > >  >>>>> [email protected]
> > >  >>>>>
> > > >>>>>
> > >  >>>
> > >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> > > >>>>>
> > >  >>>>
> > > >>>>
> > >  >>>>
> > > >>>> --
> > >  >>>> Ron Greenman
> > > >>>>  Instructor
> > > >>>> Fire Protection Engineering  Technology Bates Technical College
> > > >>>> 1101 So.  Yakima Ave.
> > > >>>> Tacoma, WA 98405
> >  > >>>>
> > > >>>>  [email protected]
> > > >>>>
> > >  >>>> http://www.bates.ctc.edu/fireprotection/
> > >  >>>>
> > > >>>> 253.680.7346
> >  > >>>> 253.576.9700 (cell)
> > >  >>>>
> > > >>>> Member:
> > >  >>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM,  WFC,
> > > >>>> WFSC
> > >  >>>>
> > > >>>> They are happy men whose  natures sort with their vocations.
> > > >>>>  -Francis
> > > >>> Bacon,
> > >  >>>> essayist, philosopher, and statesman (1561-1626)
> >  > >>>> _______________________________________________
>  > > >>>> Sprinklerforum mailing list
> > >  >>>> [email protected]
> > >  >>>>
> > > >>>
> > >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> > > >>>  _______________________________________________
> > > >>>  Sprinklerforum mailing list
> > > >>>  [email protected]
> > > >>>
>  > > >>>
> > >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> > > >>>
> > > >>
>  > > >>
> > > >>
> > > >>  --
> > > >> Ron Greenman
> > > >>  Instructor
> > > >> Fire Protection Engineering Technology  Bates Technical College
> > > >> 1101 So. Yakima  Ave.
> > > >> Tacoma, WA 98405
> > >  >>
> > > >> [email protected]
> > >  >>
> > > >>  http://www.bates.ctc.edu/fireprotection/
> > > >>
>  > > >> 253.680.7346
> > > >> 253.576.9700  (cell)
> > > >>
> > > >> Member:
>  > > >> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM,  WFC, WFSC
> > > >>
> > > >> They are happy  men whose natures sort with their vocations.
> > > >>  -Francis
> > > Bacon,
> > > >> essayist,  philosopher, and statesman (1561-1626)
> > > >>  _______________________________________________
> > > >>  Sprinklerforum mailing list
> > > >>  [email protected]
> > > >>
> >  >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> > > >  _______________________________________________
> > > >  Sprinklerforum mailing list
> > > >  [email protected]
> > > >
> >  >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> > > >  _______________________________________________
> > > >  Sprinklerforum mailing list
> > > >  [email protected]
> > > >
> >  >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> > > >  _______________________________________________
> > > >  Sprinklerforum mailing list
> > > >  [email protected]
> > > >
> >  >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> > >
> > >  _______________________________________________
> > >  Sprinklerforum mailing list
> > >  [email protected]
> > >
> >  >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> > >
> >
> >
> >
>  > --
> > Ron Greenman
> > Instructor
> > Fire  Protection Engineering Technology Bates Technical College
> > 1101  So. Yakima Ave.
> > Tacoma, WA 98405
> >
> >  [email protected]
> >
> >  http://www.bates.ctc.edu/fireprotection/
> >
> >  253.680.7346
> > 253.576.9700 (cell)
> >
> >  Member:
> > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM,  WFC, WFSC
> >
> > They are happy men whose natures sort with  their vocations. -Francis
> > Bacon, essayist, philosopher, and  statesman (1561-1626)
> >  _______________________________________________
> > Sprinklerforum  mailing list
> > [email protected]
>  >
> >  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  > er.org
> >
>
>
>
> --
> Greg  McGahan
> Living Water Fire Protection, LLC  <http://www.livingwaterfp.com>
> 1160 McKenzie Road
>  Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
>  _______________________________________________
> Sprinklerforum mailing  list
> [email protected]
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
>  rg
> _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



--  
Greg McGahan
Living Water Fire Protection, LLC  <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL  32533
850-937-1850
fax  850-937-1852
_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to