Multiple systems. All have TWO  2 1/2" hose valves after backflow and  
alarm valve. Very similar to a test header on a fire pump.
 
 
In a message dated 7/29/2013 4:58:14 P.M. Eastern Daylight Time,  
[email protected] writes:

DJ  Numbers:

Yo.... How many? You did use plural, but the way you put it  suggests
multiple systems also. So, multiple systems with one 2-1/2 each,  one system
with multiple 1-1/2s, or multiple systems each with multiple  2-1/2s?And
what size riser(s) please? Just curious.


On Mon, Jul  29, 2013 at 1:48 PM, <[email protected]> wrote:

> Is this  "forward flow test" now part of the required code? I was just on 
a
> job  the other day. New Construction. I noticed that all the systems had a
>  setup  with (2) 2 1/2" hose valves after the backflow and alarm valve,  
in
> addition to  the 2" main drain. I take it that these 2 1/2's  are for this
> test?
>
>
> In a message dated  7/29/2013 3:57:24 P.M. Eastern Daylight Time,
> [email protected]  writes:
>
> That  isn't what the intent of the code is as  stated.....just flow at
> system
> demand. I can only speak for  us, but we do a LOT of risers with only  a 
250
> gpm or so  demand...sometimes even less.
>
> A 4" drain is well  over  what we need to open it up enough for system
> demand. I would bet a  2"  drain gets really close.
>
>
> On Mon, Jul 29, 2013  at 2:52 PM, David  Autry <[email protected]> wrote:
>
>  > Wouldn't it be easier, if  you have a 4" backflow preventer you run  4"
> out
> > the wall, 3" BFP, 3"  out the wall,  etc...
> > That should open her up all the  way.
>  >
> >
> > David Autry
> >
> > Meininger  Fire  Protection Inc.
> > 2521 W L St. Suite No.4
> >  Lincoln, Ne  68522
> > Voice (402) 466-2616
> > Fax  (402) 466-2617
> >  [email protected]
> >
> >  -----Original Message-----
> > From:   [email protected]
> >   [mailto:[email protected]] On Behalf Of
>  Greg
> > McGahan
> > Sent: Monday, July 29, 2013 2:35  PM
> > To:  [email protected]
> >  Subject: Re: SIGN for Backflow  Prevention Assembly Forward Flow  Test
> >
> > What would be simple and  helpful would be  a table similar to the one
> used
> > for sizing fire  pump  Suction/Discharge/Relief Valve Piping etc.
> >
>  > Since you are not  measuring pressure, you could say 2" up to X  
gallons,
> > 2.5" for Y  etc....
> >
> > A  2-1/2" Main drain is much easier and cheaper than  some of the
>  > arrangments left / required on backflow  preventers.
>  >
> > Greg
> >
> >
> > On Mon, Jul 29,  2013  at 12:46 PM, Ron Greenman
> >   <[email protected]>wrote:
> >
> > > Better but  it is  still interpretable as requiring a measured flow be
> >  > established  (if using the main drain location then the BOR  design
> data).
> > > Then  you'd need a port that  flowed that much, main drain or 
otherwise,
> > >  and then  measure your annual test against anticipated flow to make
> >   > sure you are meeting or exceeding the required flow. Or am I   
missing
> > > something? I'm pretty certain that newer fire  service  rated 
backflows
> > > don't fail any more often than  normal FS checks,  and that that type 
of
> > > failure is  either catastrophic (doesn't  open or barely opens) 
wouldn't
> >  > a simple main drain test with  decent flow demonstrate that the  
valve
> > > is working? just a Forum  question as this is a  done deal and I 
wasn't
> > > invited to join the   exclusive
> > > 25 club.
> > >
> >  >
> > > On Mon,  Jul 29, 2013 at 7:11 AM, Roland  Huggins
> > >   <[email protected]>wrote:
> > >
> > >  > the  next edition has been cleaned-up on this issue.
> >  > >
> > >  >  _______________________________________________________________
>  >  > > 25-271
> > > Log
> > > > #CP15  Final Action:  Accept
> > > > (13.6.2.1, 13.6.2.2  (New))
> > > >   _______________________________________________________________
> >  >  Submitter:
> > > > Technical Committee on  Inspection, Testing, and  Maintenance of
> > >  Water-Based
> > > > Systems,
> >  >  >
> > > > Recommendation: Revise 13.6.2.1 to read as   follows:
> > > > 13.6.2.1 All backflow preventers installed in  fire  protection 
system
> > > > piping shall be exercised  annually by  conducting a forward flow 
test
> > > > at a  minimum flow rate of the  system design.
> > > > Add new  13.6.2.2 and renumber subsequent  sections accordingly:
> > >  > 13.6.2.2 Where hydrants or inside hose  stations are located
>  > > > downstream of the backflow preventer,  the forward flow  test shall
> > > > include hose stream demand.   Substantiation: This change was needed
> > > > to better  reflect  that the backflow preventer is not a precise 
test
> >  > > whereby  the flow through it must be measured but effort to  
exercise
> > > >  the device at flows as near as
>  > > possible
> > > > to the  system demand.
>  > > > Committee Meeting Action: Accept
> > >  >  Number Eligible to Vote: 33
> > > > Ballot Results:   Affirmative: 32 Negative: 1 Explanation of 
Negative:
> > >  >
> >  > > RAY, R.: This proposal should have been  accepted in principle:  
the
> > > wording
> > >  > "at a minimum flow rate" is  confusing and should be  reworded.
> > > >   _______________________________________________________________
> >  >  > 25-272
> > > Log
> > > > #121 Final  Action:  Accept
> > > >
> > > >  (13.6.2.1.1)
> > >  >
> > > >   _______________________________________________________________
> >  >  Submitter:
> > > > Roland J. Huggins, American Fire  Sprinkler  Association, Inc.
> > > > Recommendation:  Delete the following  text:
> > > >
> > > >  13.6.2.1.1 For backflow preventers  sized 2 in. (50 mm) and  under,
> > > > the forward flow test shall  be acceptable  to conduct without
> > > > measuring flow, where the  test  outlet is of a size to flow the
> system
> > demand.
>  > > >  Substantiation: This section implies that a measured flow  is
> > > >  required for Backflow preventers (BFP) larger  than 2 in when 
nothing
> >  > > in 13.6.2.1
> >  > states
> > > > such a  requirement. There are other  means to identify that the
> > > >  system demand is  flowing through the BFP as discussed in 
A.13.6.2.1
> >  >  > It also
> > > needs
> > > > to be kept in mind  that  we are simply exercising the BFP to ensure
> > > >  it
> > >  will
> > > > fully open at  approximately the system demand. A high  degree of
> > > >  accuracy regarding the volume of water is not  warranted.
> >  > > Additionally, BFP's are subjected to an annual  internal  
inspection
> > > > as part of the cross
> > >   connection
> > > > protection program. Committee Meeting  Action:  Accept Number 
Eligible
> > > > to Vote: 33 Ballot  Results:  Affirmative: 33
> > > >
> > >  >
> > > >
> >  > > Roland Huggins, PE -  VP Engineering
> > > >
> > >  > American  Fire Sprinkler Assn.       ---     Fire  Sprinklers Saves
> > Lives
> > > > Dallas,   TX
> > > > http://www.firesprinkler.org
> > >  >
> >  > >
> > > >
> > >  >
> > > >
> > >  > On Jul 26, 2013, at  2:57 PM, Dwight Havens  
<[email protected]>
> > >  wrote:
> > > >
> >  > > > Then they  ought to say that in the code language.
> > >  >  >
> > > > > Dwight
> > > > >
>  > >  > >
> > > > >
> > > >  >
> > > > >   ________________________________
> > > > > From: John  Denhardt  <[email protected]>
> > > >  > To:  "[email protected]" <
> > >  >  [email protected]>
> > > >  > Sent:  Thursday, July 25, 2013 3:07 PM
> > > > >  Subject: RE: SIGN for  Backflow Prevention Assembly Forward Flow
>  > > > > Test
> >  > > >
> > >  > >
> > > > > While I do  disagree to some extent  of what the NFPA 25 committee
> > > > >  has
>  > > > done, Roland statement is correct.  I have had   numerous 
discussions
> > > > with NFPA 25 committee members  where  they have stated the intent 
was
> > > > to
>  > >  exercise
> > > > the device at near system  demand.  The key  word to me was
> "Exercise".
> >  > > >
> > > > >  John
> > > >  >
> > > > > John August Denhardt, P.E.,   FSFPE
> > > > > Strickland Fire Protection  Incorporated
> >  > > > 5113 Berwyn Road
> >  > > > College Park, Maryland  20740
> > > > >  Office Telephone Number:  301-474-1136  Mobile Telephone  Number:
> > > > > 301-343-1457 FIRE SPRINKLERS  SAVE  LIVES - Can you live without
> > > > > them?
> >  >  > >
> > > > > -----Original  Message-----
> > > >  > From:  [email protected] [mailto:
> >   > > [email protected]] On Behalf  Of
>  Forest
> > > Wilson
> > > > >  Sent: Thursday, July 25,  2013 2:42 PM
> > > > >  To:  [email protected]
> > > > >  Subject: Re:  SIGN for Backflow Prevention Assembly Forward Flow
>  > > > >  Test
> > > > >
> > >  > > Here is an email on this  topic that Roland addressed in the  
past:
> > > > >
> > >  > > Im not  going to say it was one of those casual assumptions  that
> >  > > > all systems are calculated nor that all risers  have  placards.  
The
> > > > > main thing to keep in  mind  that the intent is simply to fully
> > > > >  EXERCISE the BFP at  what os expected to be the system demand.   
If
> > > > > no  data available, a discussion with the  AHJ is warranted.  As 
for
> >  > > > benchmarks,  only the flow is pertinent and pressure is
>  irrelevant.
>  > > > >
> > > > > Roland
> > >   > >
> > > > > On Dec 22, 2009, at 2:44 PM, Matthew  J.  Willis wrote:
> > > > >
> > > >  >>>
> >  > > >>> On a more important  matter: If a system was retrofitted  with 
a
> > > >  >>> backflow,
> > > > >>  and
> >  > > >>> there is no hydraulic calc plaque attached  to the  riser, and
> > > > >>> NFPA requires forward  flow  testing of backflows, how can you
> > > >  >>> conduct the  test without a benchmark to test  against?
> > > >  >>>
> > > >  >>> What is the recommended practice  in this scenario?
>  > > > >>> Forest Wilson
> > >  >  >
> > > > > Sent from my iPhone
> > >  >  >
> > > > > On Jul 25, 2013, at 12:16 PM, Ron  Greenman  
<[email protected]
> >
> > > >  wrote:
> > > >  >
> > > > >> Then  subjective good flow demonstrates a  working valve? If so 
all
>  > > > >> the numbers bantered  around are pretty  meaningless.
> > > > >>
> > > >   >>
> > > > >>
> > > > >> On  Thu, Jul 25,  2013 at 8:07 AM, Forest Wilson
> > > >  >>  <[email protected]
> > > >  >wrote:
> > > >  >>
> > > >  >>> No.
> > > > >>> The  intent is not  to pitot the output but to exercise the 
valve.
> > > >   >>>
> > > > >>>
> > > >  >>>  Sent from my iPhone
> > > >  >>>
> > > >  >>> On Jul 25, 2013, at  10:56 AM, Ron Greenman
> > > >  >>>  <[email protected]>
> > > > wrote:
> >   > > >>>
> > > > >>>> Forest. What  were  you flowing to discover these failures? 
Main
> > >  >  >>>> drain
> > > > or
> > >  > >>>>  some special test header? Would a sign with the  data 
requested
> > >  > >>>> by
> >  > the
> > > > >>>>  customer that started  this thread have had any utility in
> > > >   >>>> helping
> > > you
> > > >  >>>>  discover the problem?
> > > >  >>>>
> > > >  >>>> Then back to  that perennial question of what's a "full flow  
"
> > > >  >>>> test
> > > and
> > > >   >>> how
> > > > >>>> do you do one? I  think  Roland said the intent was to flow an
> > > >  equivalent
> >  > > >>> to
> > > >  >>>> the design  discharge criteria. How do you do this? Do  we 
run a
> > > >  >>>> pitot somewhere on the  system? Do we catch and  measure
> > > > >>>>  discharge? If so,
> > > >  from
> > > >  >>>> where? How do we arrange the test  port(s)? Do we flow  the
> > > > >>>> design
> > >   area
> > > > or
> > > > >>>>  simulate it  elsewhere? Do we need results of at least or 
better
>  > > >  >>>> flow
> > > > or
>  > > > >>>>  right on the money flow? If not either  of those how do we
> judge?
> > >  >  >>>>
> > > > >>>> Doesn't the  hydraulic  data plate note the required psi per 
the
> > >  > >>>>  calcs
> > > > at
> > >  > >>> the
> > >  > >>>> BOR and  the static? Isn't the difference the residual  drop 
at
> > >  > >>>> that
> > > >  point
> >  > > >>>> relative to the design area? Wouldn't  a main  drain with good
> > > > >>>> flow
> > >  at  a
> > > > >>> psi
> > > >  >>>> around  the BOR rating, and returning to close to the  noted
> > > >  >>>> static
> > >  when
> > > > >>>>  terminated suggest a fully  open valve, or an adequately open
> > > >   >>>> valve
> > > if
> > > > the
>  > > >  >>>> UG is oversized? In the latter case the  partially open valve
>  is
> > > > >>>  equivalent
> > > >  >>>> to fully open for the  system I just described. Am I  missing
> > >  something
> > > > >>> here?
> >  >  > >>>> An erroneous a priori? My understanding of   hydraulics 
wrong?
> > > > >>>> Main
> >  > >  drains
> > > > >>>> are too small  to simulate the result  of all design area heads
> > >  flowing
> > > > as
> >  > >  >>>> the water passes through the BOR?
> > >  >  >>>>
> > > > >>>>
>  > > >  >>>> On Thu, Jul 25, 2013 at 7:34 AM, Forest  Wilson <
> >  > [email protected]
> > >  > >>>> wrote:
> >  > >  >>>>
> > > > >>>>> I still  have  the check valve from a Ames that failed to 
open.
> > >  >  >>>>> It was jammed shut, discovered when I was  called out  
because
> > > > >>>>>  they
> > > >  >>> couldn't
> > > >  >>>>> do the fire pump  test.
> > > >  >>>>>
> > > >  >>>>> In  another case, I tested a backflow and it failed (on a  
Best
> >  > > >>>>> Buy
> > > > >>>   store).
> > > > >>>>> I opened the valve up and  the  check was damaged, would only
> > > >  >>>>> open  a
> > > > >>>  third.
> > > >  >>>>>
> > >  > >>>>>
> > > >   >>>>>
> > > > >>>>> Sent from  my  iPhone
> > > > >>>>>
> > >  >  >>>>> On Jul 24, 2013, at 8:53 PM, Ron  Greenman
> > >  > >>>>>  <[email protected]>
> > > >  >>>  wrote:
> > > > >>>>>
> > >  >  >>>>>> Worked well for plumbing and process  piping  applications 
as
> > > > >>>>>>  they
> > >  are
> > > >  >>>>>> constantly being  exercised.
> > >  > >>>>>>
> > > >   >>>>>>
> > > > >>>>>> On  Wed,  Jul 24, 2013 at 5:12 PM, Dwight Havens <
> > >  >  [email protected]
> > > >  >>>>>>  wrote:
> > > >  >>>>>>
> > > >   >>>>>>> I do remember the ones with the rods in the   center of 
the
> > > > >>>>>>>  valve
> >  > > being
> > > >  >>>>>>> particularly  poor.
> > > >  >>>>>>>
> > > >   >>>>>>> Dwight
> > > >   >>>>>>>
> > > >   >>>>>>>
> > > >   >>>>>>>
> > > >   >>>>>>>
> > > >  >>>>>>>  ________________________________
>  > > >  >>>>>>> From: Ron Greenman   <[email protected]>
> > > >  >>>>>>>  To:  [email protected]
> > > >   >>>>>>> Sent: Tuesday, July 23, 2013 11:25 PM
>  >  > > >>>>>>> Subject: Re: SIGN for  Backflow  Prevention Assembly 
Forward
> > > >  >>>>>>>  Flow
> > > > Test
>  > > >  >>>>>>>
> > > >   >>>>>>>
> > > >  >>>>>>> By  the mid-nineties you have the early Ames  models 
purpose
> > > >  >>>>>>>  built
> > > > for
> > > >   >>>>>>> sprinklers readily available, but many  units  being
> installed
> > > >  >>>>>>> are
> >  > > still
>  > > > >>>>> not
> > > >   >>>>>>> listed for fire service as many  jurisdictions  don't
> consider
> > > >  >>>>>>> the
> > >  > fire
>  > > > >>>>> line
> > > >   >>>>>>> a fire line until after the backflow, and a  n  on-listed
> > > > >>>>>>> device  is
> >  > > >>>>> cheaper
> > >  >  >>>>>>> than a listed one. Plus many go back  to the  seventies 
and
> > > > >>>>>>>  many
> > >  used
> > > > >>>>>  weights
> > > >  >>>>>>> instead of  springs and complicated lever systems  for
> joining
> >  > > >>>>>>> the
> > >  >  >>>>> clappers
> > > >   >>>>>>> and weights. Wish I could post a picture.
>  >  > > >>>>>>>
> > > >   >>>>>>>
> > > >  >>>>>>> On  Tue, Jul 23, 2013 at 7:33 PM, Dwight  Havens <
> > > >  [email protected]
> >  > > >>>>>>>>  wrote:
> > > >  >>>>>>>
> > > >   >>>>>>>> Give me a time frame. My best recollection  is  the mid
> '90's.
> > > >  >>>>>>>>
> > >  >  >>>>>>>> Dwight
> > > >   >>>>>>>>
> > > >   >>>>>>>>
> > > >   >>>>>>>>
> > > >   >>>>>>>>
> > > >   >>>>>>>> ________________________________
> >  >  > >>>>>>>> From: Ron Greenman   <[email protected]>
> > > >   >>>>>>>> To:   [email protected]
> > > >   >>>>>>>> Sent: Tuesday, July 23, 2013 9:12 PM
>  >  > > >>>>>>>> Subject: Re: SIGN for  Backflow  Prevention Assembly 
Forward
> > > >  >>>>>>>>  Flow
> > > >  Test
> > > >  >>>>>>>>
>  > > >  >>>>>>>>
> > >  >  >>>>>>>> Were these the plumbing type  before fire  service listed
> > > >  >>>>>>>>  devices
> > > >  >>>>> existed.
> > > >   >>>>>>>>
> > > >   >>>>>>>>
> > > >   >>>>>>>> On Tue, Jul 23, 2013 at 4:32 PM, Dwight   Havens <
> > > > >>> [email protected]
>  > >  > >>>>>>>>> wrote:
> >  > >  >>>>>>>>
> > > >   >>>>>>>>> Yes, yes, and yes.  The  original  proposal was based on
> > > >  >>>>>>>>>  observed
> > > >  >>>>>>> failures
> > >  >  >>>>>>>>> of BFPAs to operate properly during   main drain 
testing.
> > > >   >>>>>>>>>
> > > >   >>>>>>>>> Glendale, AZ public library  specifically  comes to 
mind.
> > > >  >>>>>>>>>
> >  > >  >>>>>>>>> Dwight
> > > >   >>>>>>>>>
> > > >   >>>>>>>>>
> > > >   >>>>>>>>>
> > > >   >>>>>>>>>
> > > >   >>>>>>>>> ________________________________
>  >  > > >>>>>>>>> From: Todd  Williams  <[email protected]>
> > > >  >>>>>>>>>  To:  "[email protected]" <
> > > >   >>>>>>>>>   [email protected]>
> > > >   >>>>>>>>> Sent: Monday, July 22, 2013 9:32   PM
> > > > >>>>>>>>> Subject: Re:  SIGN  for Backflow Prevention Assembly 
Forward
> > >  >  >>>>>>>>> Flow
> > > >  Test
> > >  > >>>>>>>>>
>  > > >  >>>>>>>>>
> > >  >  >>>>>>>>> Has there ever been an  instance of system  failure due 
to
> > > >  >>>>>>>>>  the
> > > >  >>> backflow
> > > >   >>>>>>> not
> > > >   >>>>>>>>> properly opening? How about detection  of  a BFP problem
> > > >  >>>>>>>>> during  a
> > > >  full
> > > > >>>>>>>  flow
>  > > > >>>>>>>>> test. How about   something subsequent to the initial
> > acceptance?
> > >  >  >>>>>>>>>
> > > >   >>>>>>>>> Todd G Williams, PE
> > >  >  >>>>>>>>> Fire Protection  Design/Consulting  Stonington, CT
> > > >  >>>>>>>>>  860-535-2080
> > > >  >>>>>>>>>  www.fpdc.com
> > > >  >>>>>>>>>
> >  > >  >>>>>>>>>   _______________________________________________
> > > >   >>>>>>>>> Sprinklerforum mailing list
> >  >  > >>>>>>>>>   [email protected]
> > > >   >>>>>>>>>
> > > >   >>>>>>>>>
> > > >   >>>>>>>>
> > > >   >>>>>>>
> > > >  >>>>>
> >  > > >>>
> >  > >
> > >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > > >  >>>>>>>>>   _______________________________________________
> > > >   >>>>>>>>> Sprinklerforum mailing list
> >  >  > >>>>>>>>>   [email protected]
> > > >   >>>>>>>>>
> > > >   >>>>>>>>>
> > > >   >>>>>>>>
> > > >   >>>>>>>
> > > >  >>>>>
> >  > > >>>
> >  > >
> > >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > > >  >>>>>>>>>
> >  > >  >>>>>>>>
> > > >   >>>>>>>>
> > > >   >>>>>>>>
> > > >   >>>>>>>> --
> > > >   >>>>>>>> Ron Greenman
> > > >   >>>>>>>> Instructor
> > > >   >>>>>>>> Fire Protection Engineering Technology  Bates  Technical
> > > > >>>>>>>>  College
> >  > > >>>>>>>> 1101 So.  Yakima Ave.
> > >  > >>>>>>>>  Tacoma, WA 98405
> > > >   >>>>>>>>
> > > >   >>>>>>>> [email protected]
> > >  >  >>>>>>>>
> > > >   >>>>>>>>   http://www.bates.ctc.edu/fireprotection/
> > > >   >>>>>>>>
> > > >   >>>>>>>> 253.680.7346
> > > >   >>>>>>>> 253.576.9700 (cell)
> > >  >  >>>>>>>>
> > > >   >>>>>>>> Member:
> > > >   >>>>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA,  AFAA,  NIBS, WSAFM,
> > > >  >>>>>>>> WFC,
> >  > WFSC
>  > > > >>>>>>>>
> > > >   >>>>>>>> They are happy men whose natures sort  with  their
> vocations.
> > > > -Francis
>  > > >  >>>>>>> Bacon,
> > >  >  >>>>>>>> essayist, philosopher, and  statesman  (1561-1626)
> > > >  >>>>>>>>   _______________________________________________
> > > >   >>>>>>>> Sprinklerforum mailing list
> > >  >  >>>>>>>>   [email protected]
> > > >   >>>>>>>>
> > > >   >>>>>>>>
> > > >   >>>>>>>
> > > >  >>>>>
> >  > > >>>
> >  > >
> > >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > > >  >>>>>>>>   _______________________________________________
> > > >   >>>>>>>> Sprinklerforum mailing list
> > >  >  >>>>>>>>   [email protected]
> > > >   >>>>>>>>
> > > >   >>>>>>>>
> > > >   >>>>>>>
> > > >  >>>>>
> >  > > >>>
> >  > >
> > >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > > >  >>>>>>>>
> > >  >  >>>>>>>
> > > >   >>>>>>>
> > > >   >>>>>>>
> > > >  >>>>>>>  --
> > > >  >>>>>>> Ron Greenman
> > >  >  >>>>>>> Instructor
> > > >   >>>>>>> Fire Protection Engineering Technology  Bates  Technical
> > > > >>>>>>>  College
> > >  > >>>>>>> 1101 So.  Yakima Ave.
> > > >  >>>>>>> Tacoma,  WA 98405
> > > >  >>>>>>>
>  > > > >>>>>>>   [email protected]
> > > >  >>>>>>>
> >  > >  >>>>>>>   http://www.bates.ctc.edu/fireprotection/
> > > >   >>>>>>>
> > > >  >>>>>>>  253.680.7346
> > > >  >>>>>>> 253.576.9700  (cell)
> > > >  >>>>>>>
> > > >   >>>>>>> Member:
> > > >   >>>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA,  NIBS,  WSAFM,
> WFC,
> > > >  >>>>>>> WFSC
> > >  >  >>>>>>>
> > > >   >>>>>>> They are happy men whose natures sort with  their  
vocations.
> > > > -Francis
> > > >  >>>>>  Bacon,
> > > >  >>>>>>> essayist, philosopher,  and statesman  (1561-1626)
> > > > >>>>>>>   _______________________________________________
> > > >   >>>>>>> Sprinklerforum mailing list
> > >  >  >>>>>>>  [email protected]
> >  > >  >>>>>>>
> > > >   >>>>>>>
> > > >  >>>>>
> >  > > >>>
> >  > >
> > >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > > >  >>>>>>>   _______________________________________________
> > > >   >>>>>>> Sprinklerforum mailing list
> > >  >  >>>>>>>  [email protected]
> >  > >  >>>>>>>
> > > >   >>>>>>>
> > > >  >>>>>
> >  > > >>>
> >  > >
> > >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > > >  >>>>>>>
> > > >   >>>>>>
> > > >  >>>>>>
> >  > >  >>>>>>
> > > > >>>>>>   --
> > > > >>>>>> Ron Greenman
> >  > >  >>>>>> Instructor
> > > >  >>>>>>  Fire Protection Engineering Technology Bates  Technical
> > > >  >>>>>>  College
> > > > >>>>>>  1101 So. Yakima  Ave.
> > > > >>>>>> Tacoma, WA   98405
> > > > >>>>>>
> > >  >  >>>>>> [email protected]
> > >  >  >>>>>>
> > > >  >>>>>>   http://www.bates.ctc.edu/fireprotection/
> > > >   >>>>>>
> > > > >>>>>>   253.680.7346
> > > > >>>>>>  253.576.9700  (cell)
> > > >  >>>>>>
> > > >  >>>>>>  Member:
> > > > >>>>>>  ASEE, SFPE,  ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, 
WFC,
> > > >   >>>>>> WFSC
> > > >   >>>>>>
> > > > >>>>>> They  are  happy men whose natures sort with their vocations.
> >  >  -Francis
> > > > >>>>> Bacon,
>  > > >  >>>>>> essayist, philosopher, and  statesman  (1561-1626)
> > > >  >>>>>>   _______________________________________________
> > > >   >>>>>> Sprinklerforum mailing list
> > >  >  >>>>>>  [email protected]
> > >  >  >>>>>>
> > > > >>>>>
>  >  > > >>>
> > > >
> >  >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > > > >>>>>   _______________________________________________
> > > >   >>>>> Sprinklerforum mailing list
> > > >   >>>>> [email protected]
> > >  >  >>>>>
> > > >  >>>>>
> > > >  >>>
> >  > >
> > >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > > > >>>>>
>  > > >  >>>>
> > > >  >>>>
> > > >  >>>>
> >  > > >>>> --
> > > >  >>>>  Ron Greenman
> > > > >>>>  Instructor
>  > > > >>>> Fire Protection Engineering  Technology  Bates Technical 
College
> > > > >>>> 1101 So.   Yakima Ave.
> > > > >>>> Tacoma, WA 98405
>  > >  > >>>>
> > > >  >>>>  [email protected]
> > > >  >>>>
> > > >  >>>>  http://www.bates.ctc.edu/fireprotection/
> > > >   >>>>
> > > > >>>> 253.680.7346
>  > >  > >>>> 253.576.9700 (cell)
> > >  >  >>>>
> > > > >>>>  Member:
> > > >  >>>> ASEE, SFPE, ASCET, NFPA,  AFSA, NFSA, AFAA, NIBS, WSAFM,  WFC,
> > > >  >>>> WFSC
> > > >  >>>>
>  > > > >>>> They are happy men whose  natures sort  with their vocations.
> > > > >>>>   -Francis
> > > > >>> Bacon,
> > >  >  >>>> essayist, philosopher, and statesman  (1561-1626)
> > >  > >>>>  _______________________________________________
> >  > >  >>>> Sprinklerforum mailing list
> > > >   >>>> [email protected]
> > >  >  >>>>
> > > > >>>
> >  > >
> > >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > > > >>>   _______________________________________________
> > > >  >>>  Sprinklerforum mailing list
> > > >  >>>  [email protected]
> > >  > >>>
> >  > > >>>
> > >  >
> > >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > > > >>>
> > >  > >>
> >  > > >>
> > > >  >>
> > > > >>  --
> > > >  >> Ron Greenman
> > > > >>  Instructor
>  > > > >> Fire Protection Engineering Technology  Bates  Technical College
> > > > >> 1101 So. Yakima   Ave.
> > > > >> Tacoma, WA 98405
> > >  >  >>
> > > > >>  [email protected]
> > > >  >>
> >  > > >>  http://www.bates.ctc.edu/fireprotection/
> >  > > >>
> >  > > >> 253.680.7346
>  > > > >> 253.576.9700  (cell)
> > > >  >>
> > > > >> Member:
> >  > >  >> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM,   WFC,
> WFSC
> > > > >>
> > > >  >> They are happy  men whose natures sort with their  vocations.
> > > > >>  -Francis
> > >  > Bacon,
> > > > >> essayist,  philosopher, and  statesman (1561-1626)
> > > > >>   _______________________________________________
> > > >  >>  Sprinklerforum mailing list
> > > >  >>  [email protected]
> > > >  >>
> > >  >
> > >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > > > >   _______________________________________________
> > > >  >  Sprinklerforum mailing list
> > > > >   [email protected]
> > > > >
>  > >  >
> > >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > > > >   _______________________________________________
> > > >  >  Sprinklerforum mailing list
> > > > >   [email protected]
> > > > >
>  > >  >
> > >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > > > >   _______________________________________________
> > > >  >  Sprinklerforum mailing list
> > > > >   [email protected]
> > > > >
>  > >  >
> > >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > > >
> > > >   _______________________________________________
> > > >   Sprinklerforum mailing list
> > > >   [email protected]
> > > >
> >  >  >
> > >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > > >
> > >
> >  >
> > >
> >  > --
> > > Ron  Greenman
> > > Instructor
> > > Fire  Protection  Engineering Technology Bates Technical College
> > > 1101   So. Yakima Ave.
> > > Tacoma, WA 98405
> > >
>  > >  [email protected]
> > >
> >  >  http://www.bates.ctc.edu/fireprotection/
> > >
>  > >  253.680.7346
> > > 253.576.9700 (cell)
>  > >
> > >  Member:
> > > ASEE, SFPE, ASCET,  NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM,  WFC, WFSC
> > >
>  > > They are happy men whose natures sort with  their vocations.  
-Francis
> > > Bacon, essayist, philosopher, and  statesman  (1561-1626)
> > >   _______________________________________________
> > >  Sprinklerforum  mailing list
> > >  [email protected]
> >  >
> >  >
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>  >  > er.org
> > >
> >
> >
>  >
> > --
> > Greg  McGahan
> > Living Water  Fire Protection, LLC  <http://www.livingwaterfp.com>
> >  1160 McKenzie Road
> >  Cantonment, FL 32533
> >  850-937-1850
> > fax 850-937-1852
> >   _______________________________________________
> > Sprinklerforum  mailing  list
> > [email protected]
>  >
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
>  >  rg
> >  _______________________________________________
> >   Sprinklerforum mailing list
> >   [email protected]
> >
>  >
>
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>  >
>
>
>
> --
> Greg McGahan
> Living  Water Fire Protection, LLC  <http://www.livingwaterfp.com>
>  1160 McKenzie Road
> Cantonment, FL  32533
>  850-937-1850
> fax  850-937-1852
>  _______________________________________________
> Sprinklerforum   mailing  list
>  [email protected]
>
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>  _______________________________________________
> Sprinklerforum mailing  list
> [email protected]
>
>  http://lists.firesprinkler.o
rg/listinfo.cgi/sprinklerforum-firesprinkler.org
>



--  
Ron Greenman
Instructor
Fire Protection Engineering  Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA  98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700  (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS,  WSAFM, WFC, WFSC

They are happy men whose natures sort with their  vocations. -Francis Bacon,
essayist, philosopher, and statesman  (1561-1626)
_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to