Below is specified in Australia National Standards, is worth to consider? On my 
site, I don’t remove 10% but just a few further heads on each floor.

Water quality tests

Function: To demonstrate that the
sprinkler system water is clean and free
from foreign matter, including sand,
sediments and other impurities.

Discharge test: Inspect water discharged
from at least one of the flushing valves,
for foreign matter.

Sprinkler head test: Remove at least 10%
of the sprinkler heads, at designated
locations, and inspect them for foreign
matter lodged across the orifices of the
heads.

Test failure: If foreign matter is observed
in quantities likely to impair the
functioning of the sprinkler system
- drain the system;
- open and clean the alarm valve and
strainer; and
- recharge the system.

Regards,
Le Vu Phong
Mobile:  +84 (0) 902 363 525
                      





phong_indochineengineering


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Timothy W 
Goins
Sent: Tuesday, July 30, 2013 7:39 AM
To: [email protected]
Subject: Re: Flushing

I suggest an obstruction/flushing test of the system. If ANY debris is found 
then I think he has cause. The obstruction/flushing test can be done with the 
heads in place.

"For I am not ashamed of the gospel , , because it is God’s power for salvation 
to everyone who believes..." HCS Romans 1:16

On Jul 29, 2013, at 12:35 PM, Ron Greenman <[email protected]> wrote:

> I'm really not suggesting that you do this, but ask him if he'll 
> require the same procedure for every possibly affected system anytime 
> the city works on the municipal piping since debris could enter the 
> pipe (a real problem we see over and over). If that's his intent I'd 
> bet tar and feathering and a ride out of town on a rail might become a 
> one-time reinstated social comment made by the citizens to the 
> government and it's representatives.
> 
> 
> On Mon, Jul 29, 2013 at 7:45 AM, <[email protected]> wrote:
> 
>> Keep in mind that NFPA #13 now requires that all removed sprinklers 
>> be replaced with new so it could really get expensive.
>> 
>> Ron F
>> 
>> -----Original Message-----
>> From: [email protected] [mailto:
>> [email protected]] On Behalf Of Forest 
>> Wilson
>> Sent: Monday, July 29, 2013 7:34 AM
>> To: [email protected]
>> Subject: Re: Flushing
>> 
>> Re: permit XXX
>> 
>> Dear Sir,
>> 
>> Recently your Department requested that my company remove all of the 
>> sprinklers we installed on this project and inspect for debris inside 
>> of the piping.
>> 
>> As a licensed contractor we practice due diligence in our installations.
>> Our employees on this project have completed an apprenticeship 
>> program through the state. In this apprenticeship they received 
>> training on how to handle pipe on the job.
>> 
>> It is standard practice for the fabrication shops to drop ship pipe 
>> without protective covers to the job site. Our employees are trained 
>> to inspect the interior of the piping for any obstructions and to 
>> remove debris prior to installation.
>> 
>> If you like I am more than willing to meet with you and discuss our 
>> quality control standards.
>> 
>> I respectfully request that you rescind your Departments request to 
>> have all sprinklers removed and reinstalled,which would result in 
>> unreasonable expense to the system owner and our company.
>> 
>> Respectfully,
>> 
>> 
>> 
>> Sent from my iPhone
>> 
>> On Jul 29, 2013, at 10:12 AM, Mike Hairfield <[email protected]> wrote:
>> 
>>> Have a project where the building official has an on-site inspector, 
>>> he has made a statement that there is a potential that debris might 
>>> have entered the piping since the fabricator did not install 
>>> protective
>> plugs on the weld-o-lets and caps on the ends of the piping.
>>> 
>>> He is demanding that all of the sprinkler heads be removed and 
>>> inspected for damage, the pipes be flushed/cleaned prior to
>> re-installation of the heads.
>>> 
>>> How does one go about changing his mind without stepping on his toes?
>>> 
>>> Thanks,
>>> 
>>> Mike Hairfield
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kl
>>> er.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org
> 
> 
> 
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis 
> Bacon, essayist, philosopher, and statesman (1561-1626) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to