How would that be different in the same daycare center with central
heating? It would have to be a very large daycare to comprise more than one
fire zone I think.


On Mon, Aug 5, 2013 at 6:15 PM, AKS-Gmail-IMAP <[email protected]> wrote:

> This GC may also be getting a tit near a wringer on some other things
> regarding space separation above the ceiling and having a common return
> plenum where smoke can travel from one space to the next, especially in a
> day care center that may be subject to state inspection by someone looking
> out for more than the average wood residential construction rules.
>
> Allan Seidel
> St. Louis, MO
>
> On Aug 5, 2013, at 10:24 AM, "Johnson, Duane (NIH/OD/ORS) [C]" <
> [email protected]> wrote:
>
> > Plenums are covered in NFPA 90A section 4-3.11 (2012). Sprinklers are
> not required, but everything in the space must be noncombustible, including
> any electrical wiring, cables, and sprinkler pipe serving other areas...
> >
> > For sprinklers:
> > 4.3.11.2.6.3    Nonmetallic fire sprinkler piping shall be listed as
> having a maximum peak optical density of 0.5 or less, an average optical
> density of 0.15 or less, and a maximum flame spread distance of 1.5 m (5
> ft) or less when tested in accordance with ANSI/UL 1887, Standard for
> Safety Fire Test of Plastic Sprinkler Pipe for Visible Flame and Smoke
> Characteristics.
> >
> > Duane Johnson, PE
> > Program Manager
> > Division of the Fire Marshal (Contractor)
> > Office of Research Services
> > National Institutes of Health
> > 301-496-0487
> >
> > "Protecting Science - One Sprinkler at a Time"
> >
> >
> > -----Original Message-----
> > From: Brian Harris [mailto:[email protected]]
> > Sent: Monday, August 05, 2013 11:00 AM
> > To: [email protected]
> > Subject: RE: Special Situations (8.15)
> >
> > 10-4, I'll suggest the plenum be enclosed with type "x" in order to
> apply 8:15. For my own future reference is standard drywall considered
> limited combustible in any case?
> >
> > Brian Harris, CET
> > BVS Systems Inc.
> > bvssytemsinc.com
> >
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> [email protected]] On Behalf Of Ron Greenman
> > Sent: Monday, August 05, 2013 10:54 AM
> > To: [email protected]
> > Subject: Re: Special Situations (8.15)
> >
> > Type X
> >
> >
> > On Mon, Aug 5, 2013 at 7:41 AM, Brian Harris <[email protected]
> >wrote:
> >
> >> I guess the big question then is standard 5/8" GWB considered limited
> >> or non-combustible. If memory serves me correct I believe it has a
> >> 1hour fire rating?
> >>
> >> Brian Harris, CET
> >> BVS Systems Inc.
> >> bvssytemsinc.com
> >>
> >> -----Original Message-----
> >> From: [email protected] [mailto:
> >> [email protected]] On Behalf Of Reed A.
> >> Roisum, C.E.T.
> >> Sent: Monday, August 05, 2013 10:38 AM
> >> To: [email protected]
> >> Subject: RE: Special Situations (8.15)
> >>
> >> Correct.  If indeed the plenum created is a noncombustible concealed
> space.
> >>
> >> Reed A. Roisum, C.E.T. | Karges-Faulconbridge, Inc. | Fire Protection
> >> Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 |
> >> http://www.kfiengineers.com
> >>
> >> -----Original Message-----
> >> From: [email protected] [mailto:
> >> [email protected]] On Behalf Of Brian
> >> Harris
> >> Sent: Monday, August 05, 2013 9:27 AM
> >> To: [email protected]
> >> Subject: Special Situations (8.15)
> >>
> >> All-
> >> I recently finished a design for a wood structure day care facility,
> >> (1) level of attic heads and (1) level of ceiling heads. The GC has
> >> now decided in an effort to save money on the HVAC to attach drywall
> >> to the bottom of the wood joist and use the area between this drywall
> >> and the suspended ceiling as a return air plenum. If I'm reading
> >> 8.1.1.2.1 & 8.15.1.2.2 correctly I do not need to add a 3rd level of
> protection in this "plenum"
> >> area correct?
> >>
> >> Brian Harris, CET
> >> BVS Systems Inc.
> >> Sprinkler Division
> >> bvssystemsinc.com<http://bvssystemsinc.com/>
> >> Phone: 704.896.9989
> >> Fax: 704.896.1935
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> >> er.org
> >>
> >> ______________________________________________________________________
> >> This email has been scanned by the Symantec Email Security.cloud
> service.
> >> For more information please visit
> >> http://www.symanteccloud.com__________________________________________
> >> ____________________________
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> >> er.org _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> >> er.org
> >>
> >
> >
> >
> > --
> > Ron Greenman
> > Instructor
> > Fire Protection Engineering Technology
> > Bates Technical College
> > 1101 So. Yakima Ave.
> > Tacoma, WA 98405
> >
> > [email protected]
> >
> > http://www.bates.ctc.edu/fireprotection/
> >
> > 253.680.7346
> > 253.576.9700 (cell)
> >
> > Member:
> > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> >
> > They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to