Most PIV's out there in the real world are not monitored electrically. Where supervised by locking and chaining, you are still dependent on periodic inspection to ensure the valve is properly left in the wide open position; but, if the testing company "forgot" to open the valve after performing inspection, testing and maintenance, they also forgot to perform the main drain test required after reopening the valve.
Dwight ________________________________ From: Thomas Watt <[email protected]> To: [email protected] Sent: Saturday, August 10, 2013 1:53 PM Subject: RE: Trash Transfer Station How does this happen? Is the piv not monitored? Close valve, receive trouble at panel. Open valve, clear trouble. Move on. Simple right? On Aug 10, 2013 1:31 PM, "Tom Duross" <[email protected]> wrote: > Oops.. typo. > Yes, and also would like to share the cause or the organic storage (also > barged to composting facility in NJ) building burning to the ground this > past spring. Unofficially told that the testing company left the isolation > piv closed that feeds that building. Still in litigation. Couldn't get > in, > very curious as to what hazard they used. > TD > > Tom, > > Just a clarification...I assume you mean to type 0.60/2000. And the > placard > indicated they were using an adjustment for a dry system, which in my book > is a 30% design areas increase, bringing the system design to 0.60/2600 > ft2. Of course the pump wasn't designed for this, or even the 0.60/2000, > but was certainly adequate to control the fire that occurred with 8 heads > operating at a minimum of 60 gpm. > > I think that it would be useful to capture actual system performance in > these challenging storage fires, to provide feedback to the protection > committee. > > Dwight > > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org