Not necessarily conflicting. 

Mercantile areas can be OH2.

Storage areas are per the storage chapters. Mattresses are Class III and Group 
A. After going through the decision trees based on storage arrangement, 
heights, etc., you can end up back to OH2.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Vince Sabolik [mailto:[email protected]] 
Sent: Tuesday, August 13, 2013 10:19 AM
To: [email protected]
Subject: Re: Sleep on it!

Good morning, and time's up and the answers are as conflicted as I thought.

Being less than 12 ft I suppose ORD II would fit, but knowing what these are 
made of ....

At 05:58 PM 8/12/2013, you wrote:
>Hey forum --
>
>Has anyone done a design for a small retail mattress store?
>
>Would Class III, Group A really apply? Not really storage...
>
>Thanks!
>
>Vince Sabolik, West Tech Fire Protection, Inc.
>11351 Pearl Road / Strongsville, Ohio 44136       440 
>238-4800     Fax 440 238-4876
>____________________________________________________________________
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkle
>r.org

Vince Sabolik, West Tech Fire Protection, Inc.
11351 Pearl Road / Strongsville, Ohio 44136       440 
238-4800     Fax 440 238-4876
____________________________________________________________________


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to