See 3.9 for storage definitions including 3.9.1.14 for miscellaneous storage.  
Look also at 5.3 definitions of OH. And then look at 12.1 and 13.2. For the 
lower storage heights you are referring, you will likely end up with the same 
(or very, very similar) requirements no matter which decision tree you follow. 
Of course, you need to follow the appropriate tree(s).

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Greg McGahan [mailto:[email protected]] 
Sent: Tuesday, August 13, 2013 10:36 AM
To: [email protected]
Subject: Re: Sleep on it!

I agree - however - I disagree. I have been told on more than one occasion by 
an AHJ that if it enters a space and rests for 2 seconds, it is stored.......So 
I wish there was a formal definition of the word "Storage".
I do know that in retails stores where the commodities sit in one place for 
months or years, they are stored there. Without a definitive word from 13, I 
have been at the mercy of the AHJ's interpretation and just do not want to get 
burned again.

We just did a Mrecantile remodel where they added racks against a wall with 
rolled carpet and vinyl for sale on them - the AHJ considered that rack storage 
and I can't disagree because IF a fire broke out the, fire would not care if it 
was mercantile or storage.

I know it may costs us work but ...

Greg





On Tue, Aug 13, 2013 at 9:22 AM, Johnson, Duane (NIH/OD/ORS) [C] < 
[email protected]> wrote:

> Not necessarily conflicting.
>
> Mercantile areas can be OH2.
>
> Storage areas are per the storage chapters. Mattresses are Class III 
> and Group A. After going through the decision trees based on storage 
> arrangement, heights, etc., you can end up back to OH2.
>
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Contractor) Office of Research Services 
> National Institutes of Health
> 301-496-0487
>
> "Protecting Science - One Sprinkler at a Time"
>
>
> -----Original Message-----
> From: Vince Sabolik [mailto:[email protected]]
> Sent: Tuesday, August 13, 2013 10:19 AM
> To: [email protected]
> Subject: Re: Sleep on it!
>
> Good morning, and time's up and the answers are as conflicted as I thought.
>
> Being less than 12 ft I suppose ORD II would fit, but knowing what 
> these are made of ....
>
> At 05:58 PM 8/12/2013, you wrote:
> >Hey forum --
> >
> >Has anyone done a design for a small retail mattress store?
> >
> >Would Class III, Group A really apply? Not really storage...
> >
> >Thanks!
> >
> >Vince Sabolik, West Tech Fire Protection, Inc.
> >11351 Pearl Road / Strongsville, Ohio 44136       440
> >238-4800     Fax 440 238-4876
> >____________________________________________________________________
> >
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
> >le
> >r.org
>
> Vince Sabolik, West Tech Fire Protection, Inc.
> 11351 Pearl Road / Strongsville, Ohio 44136       440
> 238-4800     Fax 440 238-4876
> ____________________________________________________________________
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________