Mark,

We had one of these Car Stacker Systems installed here in Charleston SC earlier 
this year.  Our building was a parking garage plus 5 story hotel of type IIB 
construction.

Mr. Schultz was very kind to forward to me a copy of the British testing report 
for assistance.  Also, on this side of the pond, San Francisco Fire has their 
own interior city design criteria for the car stacker systems.

The end result we agreed upon here in Charleston was 11.2K ECOH HSW sprinkler 
protection around the group of three car stackers located 12" below the car 
stacker when in the high position.  The issue we had to work with here in 
Charleston was the car stacker was a last minute addition and not covered under 
the original sprinkler permit.  The garage was already a black pipe, dry system 
being supplied by a fire pump that was installed and certified when the car 
stackers were installed.  The secondary objective for our project was a 
solution that will provide the objective of NFPA 13 for control, and not 
removing most if not all of the garage and fire pump system.

I wish I had a better solution for you.