use non-comb insulation! :)

-----Original Message-----
From: Todd - Work [mailto:[email protected]] 
Sent: Thursday, September 12, 2013 10:21 AM
To: [email protected]
Subject: small concealed space

NFPA 13 required sprinklers in concealed spaces where the space is in excess
of 6" between the bottom of the joists and the ceiling. It also requires
that sprinklers listed for use in concealed spaces under 36" deep be used.
The Viking Coin, Tyco CC1 and 2 and the new Reliable concealed space
sprinkler are listed for spaces from 12" to 36" deep. What are you supposed
to do when the space is only 9" deep?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com