I am traveling but there is a statement that the heads can be used outside 
their listing for such cases I believe

Sent from my iPhone

On Sep 12, 2013, at 4:27 PM, "Brad Casterline" <[email protected]> wrote:

> use non-comb insulation! :)
> 
> -----Original Message-----
> From: Todd - Work [mailto:[email protected]] 
> Sent: Thursday, September 12, 2013 10:21 AM
> To: [email protected]
> Subject: small concealed space
> 
> NFPA 13 required sprinklers in concealed spaces where the space is in excess
> of 6" between the bottom of the joists and the ceiling. It also requires
> that sprinklers listed for use in concealed spaces under 36" deep be used.
> The Viking Coin, Tyco CC1 and 2 and the new Reliable concealed space
> sprinkler are listed for spaces from 12" to 36" deep. What are you supposed
> to do when the space is only 9" deep?
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com