How many sprinklers are you flowing?

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Greg McGahan [mailto:[email protected]] 
Sent: Monday, September 23, 2013 7:57 AM
To: [email protected]
Subject: Re: old 14.5k ecoh brass upright

There are 8 heads in the room spaced at 20 x 20 - reducing the hose stream does 
not get us where we need to be.  The 80 gpm per head is killing the deal and I 
cannot make it work without extensive revamping...A little overkill just for 3 
painted heads I think. However, legally I don't see a leg to stand on unless we 
can find the exact same heads to replace them with. I can't even replace the 
uprights in an adjacent room with the 14.0's and move the 14.5's ( I know that 
isn't even legal anymore) to work either.

STUCK


On Sun, Sep 22, 2013 at 8:48 PM, Steven Scandaliato <[email protected]
> wrote:

> How big is the storage room?  Is it just 3 heads or how many total.  
> Doing a set of supply calcs and showing how much density is going to 
> be provided if just those 3 sprinklers go off would be a strong 
> argument...how big is the room?
>
> Steven Scandaliato, SET CFPS
> 520.971.2322 Cell
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> Scott A Futrell
> Sent: Sunday, September 22, 2013 6:39 PM
> To: [email protected]
> Subject: RE: old 14.5k ecoh brass upright
>
> Sometimes...just sometimes, the AHJ might accept reduced hose streams 
> if you can get the calcs to work otherwise. It might be worth the try. 
> 1) they shouldn't need hose except for mop up and 2) it shouldn't take 
> all the sprinklers operating in the design area to control it, so if 
> everything works as programmed a few sprinklers will control it and 
> the FF's will have enough water to mop up.
>
> Scott Futrell
>
> (763) 425-1001 x12 Office
> (612) 759-5556 Cell
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> Greg McGahan
> Sent: Sunday, September 22, 2013 6:53 PM
> To: [email protected]
> Subject: Re: old 14.5k ecoh brass upright
>
> We can't make the curve period..if we change the K factor
>
> On Sep 22, 2013, at 6:47 PM, "rongreenman ." <[email protected]>
> wrote:
>
> > Did the AHJ require that ever popular 10% cushion in the original 
> > calcs. Do you make the curve without the 10% cushion if required?
> >
> >
> > On Sun, Sep 22, 2013 at 4:37 PM, Greg McGahan 
> > <[email protected]>
> wrote:
> >
> >> We need to replace 3 painted heads in an existing storage room that 
> >> currently has 14.5 k heads. Going to the closest Equivalent head 
> >> changes the K factor to 14.0 and it makes enough of a difference 
> >> that the calks no longer work..
> >>
> >> Even if we replace all of the heads in that area with 14.0's it 
> >> will not work.  Does anyone happen to have these laying around?
> >>
> >> Question - if we can't find them, what should we do? The calcs do 
> >> not work due to a combination of a slightly degraded water supply 
> >> and being incorrectly calculated by the original installing 
> >> contractor  - we have the original drawings and they used a .15 
> >> density throughout the building instead of the required .20. (yes- 
> >> even when originally installed). The difference is only a few 
> >> pounds, but it goes from slightly positive to negative. The AHJ has 
> >> closed his ears and eyes and said "get the painted heads replaced".
> >>
> >> Thanks for your help.
> >> Greg
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
> >> nk
> >> ler.org
> >>
> >
> >
> >
> > --
> > Ron Greenman
> > Instructor
> > Fire Protection Engineering Technology Bates Technical College
> > 1101 So. Yakima Ave.
> > Tacoma, WA 98405
> >
> > [email protected]
> >
> > http://www.bates.ctc.edu/fireprotection/
> >
> > 253.680.7346
> > 253.576.9700 (cell)
> >
> > Member:
> > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> >
> > They are happy men whose natures sort with their vocations. -Francis 
> > Bacon, essayist, philosopher, and statesman (1561-1626) 
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > kl
> > er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to