5


On Mon, Sep 23, 2013 at 8:41 AM, Johnson, Duane (NIH/OD/ORS) [C] <
[email protected]> wrote:

> How many sprinklers are you flowing?
>
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Contractor)
> Office of Research Services
> National Institutes of Health
> 301-496-0487
>
> "Protecting Science - One Sprinkler at a Time"
>
>
> -----Original Message-----
> From: Greg McGahan [mailto:[email protected]]
> Sent: Monday, September 23, 2013 7:57 AM
> To: [email protected]
> Subject: Re: old 14.5k ecoh brass upright
>
> There are 8 heads in the room spaced at 20 x 20 - reducing the hose stream
> does not get us where we need to be.  The 80 gpm per head is killing the
> deal and I cannot make it work without extensive revamping...A little
> overkill just for 3 painted heads I think. However, legally I don't see a
> leg to stand on unless we can find the exact same heads to replace them
> with. I can't even replace the uprights in an adjacent room with the 14.0's
> and move the 14.5's ( I know that isn't even legal anymore) to work either.
>
> STUCK
>
>
> On Sun, Sep 22, 2013 at 8:48 PM, Steven Scandaliato <
> [email protected]
> > wrote:
>
> > How big is the storage room?  Is it just 3 heads or how many total.
> > Doing a set of supply calcs and showing how much density is going to
> > be provided if just those 3 sprinklers go off would be a strong
> > argument...how big is the room?
> >
> > Steven Scandaliato, SET CFPS
> > 520.971.2322 Cell
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> > Scott A Futrell
> > Sent: Sunday, September 22, 2013 6:39 PM
> > To: [email protected]
> > Subject: RE: old 14.5k ecoh brass upright
> >
> > Sometimes...just sometimes, the AHJ might accept reduced hose streams
> > if you can get the calcs to work otherwise. It might be worth the try.
> > 1) they shouldn't need hose except for mop up and 2) it shouldn't take
> > all the sprinklers operating in the design area to control it, so if
> > everything works as programmed a few sprinklers will control it and
> > the FF's will have enough water to mop up.
> >
> > Scott Futrell
> >
> > (763) 425-1001 x12 Office
> > (612) 759-5556 Cell
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> > Greg McGahan
> > Sent: Sunday, September 22, 2013 6:53 PM
> > To: [email protected]
> > Subject: Re: old 14.5k ecoh brass upright
> >
> > We can't make the curve period..if we change the K factor
> >
> > On Sep 22, 2013, at 6:47 PM, "rongreenman ." <[email protected]>
> > wrote:
> >
> > > Did the AHJ require that ever popular 10% cushion in the original
> > > calcs. Do you make the curve without the 10% cushion if required?
> > >
> > >
> > > On Sun, Sep 22, 2013 at 4:37 PM, Greg McGahan
> > > <[email protected]>
> > wrote:
> > >
> > >> We need to replace 3 painted heads in an existing storage room that
> > >> currently has 14.5 k heads. Going to the closest Equivalent head
> > >> changes the K factor to 14.0 and it makes enough of a difference
> > >> that the calks no longer work..
> > >>
> > >> Even if we replace all of the heads in that area with 14.0's it
> > >> will not work.  Does anyone happen to have these laying around?
> > >>
> > >> Question - if we can't find them, what should we do? The calcs do
> > >> not work due to a combination of a slightly degraded water supply
> > >> and being incorrectly calculated by the original installing
> > >> contractor  - we have the original drawings and they used a .15
> > >> density throughout the building instead of the required .20. (yes-
> > >> even when originally installed). The difference is only a few
> > >> pounds, but it goes from slightly positive to negative. The AHJ has
> > >> closed his ears and eyes and said "get the painted heads replaced".
> > >>
> > >> Thanks for your help.
> > >> Greg
> > >> _______________________________________________
> > >> Sprinklerforum mailing list
> > >> [email protected]
> > >>
> > >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
> > >> nk
> > >> ler.org
> > >>
> > >
> > >
> > >
> > > --
> > > Ron Greenman
> > > Instructor
> > > Fire Protection Engineering Technology Bates Technical College
> > > 1101 So. Yakima Ave.
> > > Tacoma, WA 98405
> > >
> > > [email protected]
> > >
> > > http://www.bates.ctc.edu/fireprotection/
> > >
> > > 253.680.7346
> > > 253.576.9700 (cell)
> > >
> > > Member:
> > > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> > >
> > > They are happy men whose natures sort with their vocations. -Francis
> > > Bacon, essayist, philosopher, and statesman (1561-1626)
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> > > er.org
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> >
>
>
>
> --
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org