Tony, as an owner or EoR, you certainly could request it, but since there is
no roof/canopy above it, NFPA 13 doesn't require sprinklers.  

I'm currently working on a 5-story commercial building that has a dumpster
enclosure (no roof) immediately adjacent to the 1st floor exterior wall.
There just happens to be a noncombustible balcony located over the dumpster
on the 4th floor.  Bottom of this balcony is 41' above grade.  Looks like
I'll be sprinklering beneath this balcony, though I question how much value
it adds.

Ed Kramer
Lawrence, KS

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tony
Silva
Sent: Thursday, October 03, 2013 12:27 PM
To: [email protected]
Subject: Re: Garbage Enclosure

Ron, exactly. It is a dumpster pushed up against the building wall. In this
case two walls due to the way the wall jogs in an "L" shape. My concern is
13 requires sprinklering of roofs and canopies where combustibles are stored
or handled (NFPA 13, 2002 section 8.14.7.4). Won't the intent cover this
situation also? No, the location of the dumpster can't be changed.

Tony  

----- Original Message -----
From: "rongreenman ." <[email protected]>
To: [email protected]
Sent: Thursday, October 3, 2013 7:50:30 AM
Subject: Re: Garbage Enclosure

Sounds like a fence surrounding a dumpster pushed up against the side of the
building on three sides to me. Is it a threat? Fire in a container against a
concrete wall? Under the intake air opening at the combustible dust factory?
Death penalty law for burning any garbage, even by accident.
Seriously, what can be damaged, what exposure threat is there to neighboring
properties, how would you detect it and at what cost sans roof, any rules
requiring it (I know, that's the question you're asking Tony), can you
moc=ve the actual hazard a few feet away, etc.?


On Wed, Oct 2, 2013 at 10:42 PM, A.P.Silva <[email protected]> wrote:

> An office building (NFPA 13) has a garbage enclosure outside the 
> building, but attached to it. The garbage enclosure has no access from 
> the building It is fenced with gates from outside and does not have a 
> roof.As it is attached to the building, is it required to be 
> sprinklered?
>
> Tony
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org