Tony, Not required by NFPA 13, as it has no roof, assuming that it is not sitting under a combustible roof overhang;
but that does not mean it is a good idea to have a garbage enclosure next the building. I was involved with a fire in a compactor attached to a mercantile No sprinklers in the compactor, as it is a piece of equipment on the exterior of the building. Smoke damage caused a loss estimated at $1 million (actual loss unknown). Dwight ________________________________ From: A.P.Silva <[email protected]> To: [email protected] Sent: Thursday, October 3, 2013 1:42 AM Subject: Garbage Enclosure An office building (NFPA 13) has a garbage enclosure outside the building, but attached to it. The garbage enclosure has no access from the building It is fenced with gates from outside and does not have a roof.As it is attached to the building, is it required to be sprinklered? Tony _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org