Tony,

Not required by NFPA 13, as it has no roof, assuming that it is not sitting 
under a combustible roof overhang;

but that does not mean it is a good idea to have a garbage enclosure next the 
building.  I was involved with a fire in a compactor attached to a mercantile  
No sprinklers in the compactor, as it is a piece of equipment on the exterior 
of the building.  Smoke damage caused a loss estimated at $1 million (actual 
loss unknown).

Dwight




________________________________
 From: A.P.Silva <[email protected]>
To: [email protected] 
Sent: Thursday, October 3, 2013 1:42 AM
Subject: Garbage Enclosure
 

An office building (NFPA 13) has a garbage enclosure outside the building,
but attached to it. The garbage enclosure has no access from the building It
is fenced with gates from outside and does not have a roof.As it is attached
to the building, is it required to be sprinklered?

Tony