I really like this one.

8.15.7.5* ('13)   Sprinklers shall be installed under exterior projections 
greater than 2 ft (0.6 m) wide over areas where combustibles are stored.

Had a project with a 3'-11" noncombustible canopy attached to a 48' high 8.5" 
thick concrete tilt panel wall. The canopy is to keep rain off the doors used 
by truck trailers at a very large distribution center. The AHJ and an 
interpretation from AFSA said it had to be sprinklered. No exterior unloading 
or handling, no exterior storage and no truck dock, only sky above the canopy. 
If the canopy wasn't there would be no sprinklers. We had to install about 100 
heads to protect a noncombustible canopy from the last 3'-11" of a semitrailer.

Ron F

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ed Kramer
Sent: Thursday, October 03, 2013 5:05 PM
To: [email protected]
Subject: RE: Garbage Enclosure

If it weren't for the balcony, there would be nothing but stars above the 
dumpster.  The balcony is the 'roof'.  I've contacted the AHJ to get his 
opinion.

Ed Kramer
Lawrence, KS

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tony Silva
Sent: Thursday, October 03, 2013 6:56 PM
To: [email protected]
Subject: Re: Garbage Enclosure

Even without the balcony, won't you have a roof overhang above the dumpster?
I'm curious to know why you're sprinklering below the balcony. was it your 
judgement or request from EOR?

Tony

----- Original Message -----
From: "Kramer Design, LLC" <[email protected]>
To: [email protected]
Sent: Thursday, October 3, 2013 12:53:34 PM
Subject: RE: Garbage Enclosure

Tony, as an owner or EoR, you certainly could request it, but since there is no 
roof/canopy above it, NFPA 13 doesn't require sprinklers.  

I'm currently working on a 5-story commercial building that has a dumpster 
enclosure (no roof) immediately adjacent to the 1st floor exterior wall.
There just happens to be a noncombustible balcony located over the dumpster on 
the 4th floor.  Bottom of this balcony is 41' above grade.  Looks like I'll be 
sprinklering beneath this balcony, though I question how much value it adds.

Ed Kramer
Lawrence, KS

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tony Silva
Sent: Thursday, October 03, 2013 12:27 PM
To: [email protected]
Subject: Re: Garbage Enclosure

Ron, exactly. It is a dumpster pushed up against the building wall. In this 
case two walls due to the way the wall jogs in an "L" shape. My concern is
13 requires sprinklering of roofs and canopies where combustibles are stored or 
handled (NFPA 13, 2002 section 8.14.7.4). Won't the intent cover this situation 
also? No, the location of the dumpster can't be changed.

Tony  

----- Original Message -----
From: "rongreenman ." <[email protected]>
To: [email protected]
Sent: Thursday, October 3, 2013 7:50:30 AM
Subject: Re: Garbage Enclosure

Sounds like a fence surrounding a dumpster pushed up against the side of the 
building on three sides to me. Is it a threat? Fire in a container against a 
concrete wall? Under the intake air opening at the combustible dust factory?
Death penalty law for burning any garbage, even by accident.
Seriously, what can be damaged, what exposure threat is there to neighboring 
properties, how would you detect it and at what cost sans roof, any rules 
requiring it (I know, that's the question you're asking Tony), can you moc=ve 
the actual hazard a few feet away, etc.?


On Wed, Oct 2, 2013 at 10:42 PM, A.P.Silva <[email protected]> wrote:

> An office building (NFPA 13) has a garbage enclosure outside the 
> building, but attached to it. The garbage enclosure has no access from 
> the building It is fenced with gates from outside and does not have a 
> roof.As it is attached to the building, is it required to be 
> sprinklered?
>
> Tony
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to