Hello Phong,

What is the pressure in the standpipe feeding these when the fire pump is at 
churn?

From the Victaulic cut sheet for this head:
Max. Working Pressure: 
175 psi/1200 kPa FM Global
250 psi/1725 kPa UL
Factory Hydrostatic Test: 100% @ 500 psi/3450 kPa


Also a chance the heads were hit with something during construction after they 
were installed, Or the installer could have dropped a head.

Saturday, October 5, 2013, 6:35:07 AM, you wrote:

> The model of the head is V2710 (K5,6) of Victaulic


> Regards,
> Le Vu Phong
> Mobile:  +84 (0) 902 363 525
>                       





> phong_indochineengineering



> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Phong - 
> Indochine Engineering
> Sent: Saturday, October 05, 2013 5:29 PM
> To: [email protected]
> Subject: RE: Sprinkler broken in 05 star hotel guest rooms

> But it is still a chance that during the construction, some heads are 
> installed by another brand...


> Regards,
> Le Vu Phong
> Mobile:  +84 (0) 902 363 525
>                       





> phong_indochineengineering



> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Phong - 
> Indochine Engineering
> Sent: Saturday, October 05, 2013 5:06 PM
> To: [email protected]
> Subject: RE: Sprinkler broken in 05 star hotel guest rooms

> Exactly Steven.


> Regards,
> Le Vu Phong
> Mobile:  +84 (0) 902 363 525
>                       





> phong_indochineengineering



> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steven 
> Scandaliato
> Sent: Saturday, October 05, 2013 4:50 PM
> To: [email protected]
> Subject: RE: Sprinkler broken in 05 star hotel guest rooms

> So I am assuming each floor is fed from the same standpipe and
> supplied by the same fire pump...and the same sprinkler head type from same 
> manufacturer??

> Steven Scandaliato, SET CFPS
> 520.971.2322 Cell


> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Phong - 
> Indochine Engineering
> Sent: Saturday, October 05, 2013 3:47 AM
> To: [email protected]
> Subject: RE: Sprinkler broken in 05 star hotel guest rooms

> Thanks Steven,

> The rooms are on different floors: L9, L14, L16, and L22.

> Regards,
> Le Vu Phong
> Mobile:  +84 (0) 902 363 525
>                       





> phong_indochineengineering



> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steven 
> Scandaliato
> Sent: Saturday, October 05, 2013 4:46 PM
> To: [email protected]
> Subject: RE: Sprinkler broken in 05 star hotel guest rooms

> Le Vu,
> Can you tell me, were the sprinklers that activated in consecutive
> rooms...side by side or one right next to the other or are they on
> different floors or at different locations on the same floor?


> Steven Scandaliato, SET CFPS
> 520.971.2322 Cell

> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Phong - 
> Indochine Engineering
> Sent: Saturday, October 05, 2013 3:08 AM
> To: [email protected]
> Subject: Sprinkler broken in 05 star hotel guest rooms

> Hello,

> In a 04 year old 05 star hotel of Starwood in Asia, recently side
> wall sprinklers of 03 different guest rooms are broken with unknown
> reasons in the morning about 10am. There is no fire at all. What are
> all brainstormed possible reasons?

> Typical report of the scenes:

> 09’14am the fire pump has been active. Security and engineering has responded 
> to check.
> - 09’14am Mr. Kiet (Bellman) informed to GSC to raise code 888 –
> since he has been informed by Guests  (R.092) that the water came
> out in her room and her properties were wet.
> - 09’16am at the scene Mr. Trung discovered sprinkler in R.902 was
> broken and the water came out immediately he turned off the power in
> R.902 and closed the valve of the pipe
> - 09’18am ERT team came to the R1605 ERT focused on clearing the
> water and removing all items from the room.
> - 09’18am Mr. Huy (Duty Manager) & Ms. Kieu (Assistant Housekeeping
> Manager) assisted Guests to move to R.920.
> - 09’21am Management team responded to the scene, calm down the
> guest and we have listed the wet items to send for washing & drying (see 
> below list)
> - 12’30pm Mr. Sinh (Maintenance manager) replaced sprinkler and smoking 
> detector in R902


> Information from Guests (R0902):
> 9’12am: When Guest came back room 0902, they discovered the
> sprinkler released and water came out in their room. Then Ms. Jiang
> Yuting went to in front of lifts lobby and reported to Mr. Kiet(Bellman) 
> about this case



> Regards,
> Le Vu Phong
> Mobile:  +84 (0) 902 363 525
>                       
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



-- 
Best regards,