NFPA 101(2012) 4.3.2 Single Fire Source. The fire protection methods of this 
Code assume a single fire source.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: rongreenman . [mailto:[email protected]] 
Sent: Thursday, December 05, 2013 12:57 PM
To: [email protected]
Subject: Re: Stockham Fittings

I don't know if Roland is following this thread or not, but.... We all know 
that a basic design consideration is the one-fire at a time concept. Roland 
talks about this all the time when we're hit by the "but what if...?"
scenarios. I looked for a written reference (since if it's written it must be 
truer than if just said, even by the same person), but I couldn't find one in 
the couple of minutes I dedicated to the task. Anyone (Roland) have something? 
It would be useful over and over.


On Thu, Dec 5, 2013 at 8:24 AM, ampeck <[email protected]> wrote:

> These stories are so incredibly funny! And you're right Ron. I drew a 
> blank when he asked about listing of fittings and that they just had 
> to be according to the ASME/ASTM/AWWA. I have to hammer that in my 
> head so the next time I don't look like a deer in the head lights.
>
> Not about listing or approvals but I think I pissed off a owners fire 
> engineer, I knew he was one because he couldn't say enough of how long 
> he's been in the business and how he was the first in Florida or 
> something to that effect. He asked me why I didn't run ALL the 
> multiple hydraulic calculations at the same time. There was a truck 
> wash, office, maintenance bay and small oil storage. When I asked 
> "why?" he said "Well what if multiple fires develop at the same 
> time?". I literally burst out with "well if you have multiple fires at 
> the same you have worse problems and the building is gone!" I further 
> went on to say "sure we could do that but we'd have to have  high pressure, 
> multiple pumps and a much bigger water tank".
> The owner was there also, awkward silence for a few seconds and then 
> he moved on to something else. Only afterwards did I think I should 
> have been more diplomatic in my answer.
> Sent from iCloud
>
>
> On Dec 05, 2013, at 08:26 PM, [email protected] wrote:
>
> Another thing is the increasing number of AHJ's that think every piece 
> of material used in a sprinkler system has the "Listed". AHJ's now 
> want to know where is the listing for the angle iron used In the 
> trapeze hanger or the listing of flange bolts. I can remember when the 
> only List FDC available was a 4" 2 way wye type. Best one for me was 
> the AHJ that said we couldn't use a top beam clamp on a bar joist 
> because it was only listed for beams.
> Ron F
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of John 
> O'Connor
> Sent: Thursday, December 05, 2013 7:47 AM
> To: [email protected]
> Subject: RE: Stockham Fittings
>
> This reminds me of a conversation with a young FM rep asking what kind 
> of dielectric fittings we were planning on using where we transition 
> to galvanized pipe and black pipe. This was shortly after FM began 
> calling for galvanized pipe on all dry systems. I responded with "the 
> same kind of transition used between the zinc coating and the steel 
> pipe on every piece of galvanized pipe". He hesitated, in silence, 
> then caught his error, and apologized for being stupid. I doubt you 
> will get an apology from this AHJ for being stupid. Even after these 
> Stockham fittings have served under pressure for 40 years. What else 
> will these people think up to justify their jobs?
> John O'Connor
> National Fire Sprinklers, Nashville TN
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Forest 
> Wilson Fire Sprinkler Contractor
> Sent: Thursday, December 05, 2013 8:25 AM
> To: [email protected]
> Subject: RE: Stockham Fittings
>
> That's wonderful. Now hundreds of dollars must be spent so a local 
> official can be convinced that these fittings manufactured by a major 
> industry are suitable for a job installed decades ago.
> I suppose the only thing you can do is write to Obama and explain that 
> a council needs to be appointed to see if these fittings were supposed 
> to be manufactured because a guy from the city doesn't know.
> All at contractor expense, of course
>
>
> Forest Wilson
> Fire Sprinkler Contractor
> 937-736-0425
>
> Notice:
> This message is confidential. It may also be privileged or otherwise 
> protected by work product immunity or other legal rules. If you have 
> received it by mistake, please let us know by e-mail reply and delete 
> it from your system; you may not copy this message or disclose its 
> contents to anyone. Please send us by fax any message containing 
> deadlines as incoming e-mails are not screened for response deadlines. 
> The integrity and security of this message cannot be guaranteed on the 
> Internet.
>
>
> -------- Original message --------
> From: [email protected] Date: 12/05/2013 8:39 AM (GMT-05:00) To:
> [email protected] Subject: RE: Stockham Fittings 
> Fittings don't have to be "Listed". If they are that's great but 
> fittings only have to meet the ASME, ASTM or AWWA publications listed 
> in NFPA 13. I would think most major brand manufacturers would have 
> met those requirements. Ya gotta love the enthusiasm of some AHJ's.
> Ron F
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of ampeck
> Sent: Thursday, December 05, 2013 12:12 AM
> To: [email protected]
> Subject: Stockham Fittings
>
> I was wondering if anyone had an idea about listing of early 1970 
> Stockham fittings.
>
> We're doing a renovation and the AHJ had brought up about the fitting 
> listing and quality. Now it was before my time but even after 40 years 
> these fittings look in perfect shape. During that time were there 
> listings/approvals on them? And if so how can I go about finding it? 
> I've already exhausted google out lol
>
> I believe it's a none issue of course but you know how it goes.
>
> Thanks!
> Sent from iCloud
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 10.0.1432 / Virus Database: 3658/6392 - Release Date: 
> 12/04/13
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to