Thanks guys. That's good ammo for everyone that encounters this whit if
thinking.


On Thu, Dec 5, 2013 at 10:35 AM, Johnson, Duane (NIH/OD/ORS) [C] <
[email protected]> wrote:

> NFPA 101(2012) 4.3.2 Single Fire Source. The fire protection methods of
> this Code assume a single fire source.
>
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Contractor)
> Office of Research Services
> National Institutes of Health
> 301-496-0487
>
> "Protecting Science - One Sprinkler at a Time"
>
>
> -----Original Message-----
> From: rongreenman . [mailto:[email protected]]
> Sent: Thursday, December 05, 2013 12:57 PM
> To: [email protected]
> Subject: Re: Stockham Fittings
>
> I don't know if Roland is following this thread or not, but.... We all
> know that a basic design consideration is the one-fire at a time concept.
> Roland talks about this all the time when we're hit by the "but what if...?"
> scenarios. I looked for a written reference (since if it's written it must
> be truer than if just said, even by the same person), but I couldn't find
> one in the couple of minutes I dedicated to the task. Anyone (Roland) have
> something? It would be useful over and over.
>
>
> On Thu, Dec 5, 2013 at 8:24 AM, ampeck <[email protected]> wrote:
>
> > These stories are so incredibly funny! And you're right Ron. I drew a
> > blank when he asked about listing of fittings and that they just had
> > to be according to the ASME/ASTM/AWWA. I have to hammer that in my
> > head so the next time I don't look like a deer in the head lights.
> >
> > Not about listing or approvals but I think I pissed off a owners fire
> > engineer, I knew he was one because he couldn't say enough of how long
> > he's been in the business and how he was the first in Florida or
> > something to that effect. He asked me why I didn't run ALL the
> > multiple hydraulic calculations at the same time. There was a truck
> > wash, office, maintenance bay and small oil storage. When I asked
> > "why?" he said "Well what if multiple fires develop at the same
> > time?". I literally burst out with "well if you have multiple fires at
> > the same you have worse problems and the building is gone!" I further
> > went on to say "sure we could do that but we'd have to have  high
> pressure, multiple pumps and a much bigger water tank".
> > The owner was there also, awkward silence for a few seconds and then
> > he moved on to something else. Only afterwards did I think I should
> > have been more diplomatic in my answer.
> > Sent from iCloud
> >
> >
> > On Dec 05, 2013, at 08:26 PM, [email protected] wrote:
> >
> > Another thing is the increasing number of AHJ's that think every piece
> > of material used in a sprinkler system has the "Listed". AHJ's now
> > want to know where is the listing for the angle iron used In the
> > trapeze hanger or the listing of flange bolts. I can remember when the
> > only List FDC available was a 4" 2 way wye type. Best one for me was
> > the AHJ that said we couldn't use a top beam clamp on a bar joist
> > because it was only listed for beams.
> > Ron F
> > -----Original Message-----
> > From: [email protected] [mailto:
> > [email protected]] On Behalf Of John
> > O'Connor
> > Sent: Thursday, December 05, 2013 7:47 AM
> > To: [email protected]
> > Subject: RE: Stockham Fittings
> >
> > This reminds me of a conversation with a young FM rep asking what kind
> > of dielectric fittings we were planning on using where we transition
> > to galvanized pipe and black pipe. This was shortly after FM began
> > calling for galvanized pipe on all dry systems. I responded with "the
> > same kind of transition used between the zinc coating and the steel
> > pipe on every piece of galvanized pipe". He hesitated, in silence,
> > then caught his error, and apologized for being stupid. I doubt you
> > will get an apology from this AHJ for being stupid. Even after these
> > Stockham fittings have served under pressure for 40 years. What else
> > will these people think up to justify their jobs?
> > John O'Connor
> > National Fire Sprinklers, Nashville TN
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> > [email protected]] On Behalf Of Forest
> > Wilson Fire Sprinkler Contractor
> > Sent: Thursday, December 05, 2013 8:25 AM
> > To: [email protected]
> > Subject: RE: Stockham Fittings
> >
> > That's wonderful. Now hundreds of dollars must be spent so a local
> > official can be convinced that these fittings manufactured by a major
> > industry are suitable for a job installed decades ago.
> > I suppose the only thing you can do is write to Obama and explain that
> > a council needs to be appointed to see if these fittings were supposed
> > to be manufactured because a guy from the city doesn't know.
> > All at contractor expense, of course
> >
> >
> > Forest Wilson
> > Fire Sprinkler Contractor
> > 937-736-0425
> >
> > Notice:
> > This message is confidential. It may also be privileged or otherwise
> > protected by work product immunity or other legal rules. If you have
> > received it by mistake, please let us know by e-mail reply and delete
> > it from your system; you may not copy this message or disclose its
> > contents to anyone. Please send us by fax any message containing
> > deadlines as incoming e-mails are not screened for response deadlines.
> > The integrity and security of this message cannot be guaranteed on the
> Internet.
> >
> >
> > -------- Original message --------
> > From: [email protected] Date: 12/05/2013 8:39 AM (GMT-05:00) To:
> > [email protected] Subject: RE: Stockham Fittings
> > Fittings don't have to be "Listed". If they are that's great but
> > fittings only have to meet the ASME, ASTM or AWWA publications listed
> > in NFPA 13. I would think most major brand manufacturers would have
> > met those requirements. Ya gotta love the enthusiasm of some AHJ's.
> > Ron F
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> > [email protected]] On Behalf Of ampeck
> > Sent: Thursday, December 05, 2013 12:12 AM
> > To: [email protected]
> > Subject: Stockham Fittings
> >
> > I was wondering if anyone had an idea about listing of early 1970
> > Stockham fittings.
> >
> > We're doing a renovation and the AHJ had brought up about the fitting
> > listing and quality. Now it was before my time but even after 40 years
> > these fittings look in perfect shape. During that time were there
> > listings/approvals on them? And if so how can I go about finding it?
> > I've already exhausted google out lol
> >
> > I believe it's a none issue of course but you know how it goes.
> >
> > Thanks!
> > Sent from iCloud
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .
> > org
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .
> > org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .
> > org
> >
> > -----
> > No virus found in this message.
> > Checked by AVG - www.avg.com
> > Version: 10.0.1432 / Virus Database: 3658/6392 - Release Date:
> > 12/04/13
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .
> > org
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .
> > org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .
> > org
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
>
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)