Keep in mind that 10.6.8.1 states, "The requirement of 10.6.8 (prohibition against using UG piping as a ground) shall not preclude the bonding of the underground piping to the lightning protection grounding system as required by NFPA 780 in those cases where lightning protection is provided for the structure."
Steve Leyton -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Taylor, Galen Sent: Thursday, December 05, 2013 1:32 PM To: [email protected] Subject: RE: Grounding Think about ... grounding is a term used for "earth" on old electrical diagrams. An electrical system is not "grounded" unless it goes to earth. And if you're talking about fire sprinkler piping, it's not permitted to be used for electrical grounding. Galen Taylor County of Los Angeles Fire Department Fire Prevention Engineering 323-890-4339 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Brandon Hunsinger Sent: Thursday, December 05, 2013 1:22 PM To: [email protected] Subject: Grounding Can aboveground piping be used for grounding or bonding electrical systems. I see where underground pipe can be used for bonding but not grounding... Columbus Automatic Sprinkler, Brandon Hunsinger 706 358 2535 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org