Hence why some in the electrical sphere of influencing want to change
the term to "earthing" here in the colonies, yep earthing.

Article 250 of the NEC is most likely the most misunderstood section of
the code, guess that's why guys like soares, iaei and the like publish
books 3/4" thick on the topic, add in Ufer grounds (concrete encased
electrodes), csst bonds (gas tubing) , isolated grounds (the orange
receptacles) with a sprinkle of derived sources (generators that break
the neutral on transfer) and finished with fault currents (what it takes
to open the breaker) and heads start a spinning, reminiscent of the
engineer of the silver strings submarine band who smashes all the fuses
in the panelboard with a hammer.

But in a nutshell;

Bonding = Connect all (which includes pipes) the different metal stuff
together with straps, screws, bolts, fittings or jumpers.  The whole
idea is that if an energized conductor (hot wire) makes contact with the
metal stuff sufficient current (fault current) will flow back to the
(source) panelboard overcurrent device (fuse or circuit breaker) and
trip it deenergizing the circuit instantly.

Grounding = Connect it to earth.  Typical DIP Fire Service undergrounds
DO NOT COUNT as a grounding electrode pursuant to the NEC which clearly
defines them and DIP isn't one (please don't anyone make the mistake of
one of our tired posters and ask about PVC and CPVC).  A sharp
electrical inspector will say hey it looks good but it doesn't count.
The idea here is to provide a reference to stabilize voltage and provide
a bleed path for lightning.   In order to do that the pipe metal MUST be
in DIRECT contact with earth and the DIP coating prevents that.

Hope that helps,  happy electrons to all.

John

John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Borough of Red Bank, New Jersey
Office: 732-530-2760 X 331
Cell/Text: 732-904-6823
Email: [email protected]
http://www.redbanknj.org



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Taylor, Galen
Sent: Thursday, December 05, 2013 4:32 PM
To: [email protected]
Subject: RE: Grounding

Think about ... grounding is a term used for "earth" on old electrical
diagrams. An electrical system is not "grounded" unless it goes to
earth. And if you're talking about fire sprinkler piping, it's not
permitted to be used for electrical grounding.

Galen Taylor
County of Los Angeles Fire Department
Fire Prevention Engineering
323-890-4339
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Brandon Hunsinger
Sent: Thursday, December 05, 2013 1:22 PM
To: [email protected]
Subject: Grounding

 Can aboveground piping be used for grounding or bonding electrical
systems. I see where underground pipe can be used for bonding but not
grounding...

Columbus Automatic Sprinkler, Brandon Hunsinger
706 358 2535

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to