I'd like to suggest one change:  "Chapter 3 - The EOR shall do chapter 1 and
chapter 2 and create bid documents accordingly before the project goes out
for bids."

Every bidding fire protection contractor shouldn't have to track down that
info and the local AHJ shouldn't have to answer the same questions over &
over & over. 

Ed Kramer
Lawrence, KS

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steven
Scandaliato
Sent: Wednesday, February 19, 2014 1:01 PM
To: [email protected]
Subject: RE: 100 PSI requirement at top of Standpipe

Bingo....the title for NFPA 14 should be changed to "Standard for the
Installation of Standpipe Systems"....Chapter 1 - Call the guy who is going
to fight the fire and ask him what he wants".  Chapter 2 - "don't argue with
the guy who is fighting the fire; rather give him what he is asking for".
Chapter 3 - Do chapter 1 and chapter 2 BEFORE you bid the job.

Peace,

Steven Scandaliato, SET CFPS
520.971.2322 Cell
Skype: steven.scandaliato


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Casterline
Sent: Wednesday, February 19, 2014 10:56 AM
To: [email protected]
Subject: RE: 100 PSI requirement at top of Standpipe

Thanks Jim and Duane.
Wow, define "Standard" where it comes to NFPA 14! :) brad

-----Original Message-----
From: Johnson, Duane (NIH/OD/ORS) [C] [mailto:[email protected]]
Sent: Wednesday, February 19, 2014 10:46 AM
To: [email protected]
Subject: RE: 100 PSI requirement at top of Standpipe

Hey Jim, interestingly enough, the Annex tells the fire department to choose
an appropriate nozzle based on the standpipe in lieu of the designer
contacting the fire department...

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor) Office of Research Services
National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Johnson, Duane (NIH/OD/ORS) [C]
Sent: Wednesday, February 19, 2014 11:38 AM
To: [email protected]
Subject: RE: 100 PSI requirement at top of Standpipe

NFPA 14:A.7.8 (2013) Where determining the pressure at the outlet of the
remote hose connection, the pressure loss in the hose valve should be
considered.

It is very important that fire departments choose an appropriate nozzle type
for their standpipe fire-fighting operations. Constant pressure-
(automatic-) type spray nozzles (see NFPA 1964, Standard for Spray Nozzles)
should not be used for standpipe operations because many of these types
require a minimum of 100 psi (6.9 bar) of pressure at the nozzle inlet to
produce a reasonably effective fire stream. In standpipe operations, hose
friction loss could prevent the delivery of 100 psi
(6.9 bar) to the nozzle.

In high-rise standpipe systems with pressure-reducing hose valves, the fire
department has little or no control over hose valve outlet pressure.

Many fire departments use combination (fog and straight stream) nozzles
requiring 100 psi (6.9 bar) residual pressure at the nozzle inlet with 11/2
in., 13/4 in., or 2 in. (40 mm, 44 mm, or 50 mm) hose in lengths of up to
150 ft (45.7 m). Some use 21/2 in. (65 mm) hose with a smooth bore nozzle or
a combination nozzle.

Some departments use 50 ft (15.2 m) of 21/2 in. (65 mm) hose to a gated wye,
supplying two 100 ft (30.5 m) lengths of 11/2-2 in. (40-50 mm) hose with
combination nozzles, requiring 120-149 psi (8.3-0.3 bar) at the valve
outlet. (See Table A.7.8.) Also see NFPA 1901, Standard for Automotive Fire
Apparatus.

There is also Table A7.8 that indicates pressure requirements of common
nozzle/hose arrangements.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor) Office of Research Services
National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"

-----Original Message-----
From: Jim Davidson [mailto:[email protected]]
Sent: Wednesday, February 19, 2014 11:26 AM
To: [email protected]
Subject: RE: 100 PSI requirement at top of Standpipe

Rick and Brad,

The original intent of NFPA 14 pre 1990's editions was to provide a 250 gpm
hose stream for fire department use at the floor of fire department
operations with a residual pressure of 65 psi flowing 250 gpm. This was
based on high rise hose pack that the fire department were using which
consisted of 2 1/2 inch hose, 100 ft pre-connected, with a non-automatic
2 1/2 inch Rockwood hose nozzle (solid/spray). With a residual pressure of
65 psi at the fire dept hose valve on the standpipe the Rockwood nozzle
could throw a 250 gpm stream a minimum of 50 ft.

At the One Merridian Fire the fire department high-rise hose pack consisted
of 1 3/4 inch hose with 1 1/2 inch couplings, 100 to 150 ft of pre connected
hose, with 1 1/2 inch, automatic Task Force nozzles.
Actual testing after the fire indicated that the combination of 1 3/4 inch
hose and automatic nozzle could not produce the 250 gpm flow that the old 2
1/2 inch hose and Rockwood nozzle combination could produce at
65 psi residual pressure at the fire dept hose valve. In some of the testing
pressures in excess of 300 psi at the fire dept hose valve was required to
produce a flow in the vicinity of 200 + gpm with the TTF nozzle and 1 3/4
hose combination. 

The designer of the standpipe system needs to discuss in detail with the
appropriate fire department operations personal as to the real high-rise
operations and hose stream deployment tactics actually used on the fire
ground.

The standpipe system was designed to NFPA 14 1984 Edition requirements as
per City of Philadelphia requirements, at time the high rise pack consisted
of 2 1/2 inch hose with Rockwood 2 1/2 inch nozzle. At time of fire the high
rise pack consisted of 1 3/4 inch hose w 1 1/2 inch couplings, with 1 1/2
inch TFT automatic nozzles which completely changed the original intent of
NFPA 14 to provide 250 gpm for fire hose stream operations and hydraulic
requirements to produce the 250 gpm through the 1 3/4 hose. The standpipe
system is a very important part of the fire departments operations at a high
rise building and the fire department needs to be consulted about the fire
ground operations SOP in order to address the particular high rise pack
equipment used by the fire department and any unusual hydraulic requirements
these operations introduce into the design of the standpipe system.

Have a fire safe day!

Regards

Jim     

          

DAVIDSON ASSOCIATES

Fire Protection Engineering     P. O. Box 4010
Code Consultants        Greenville, DE  19807-0010
Medical Gas Systems Engineering (302) 994-9500
        Fax (302) 994-3414

CONFIDENTIALITY
This report and any attachments are confidential and also may be privileged.
If you are not the named recipient, or have otherwise received this report
in error, please destroy the report, notify the sender immediately, and do
not disclose its contents to any other person, use them for any purpose, or
store or copy them in any medium.
Thank you for your cooperation.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Matsuda, Richard
Sent: Wednesday, February 19, 2014 10:45 AM
To: [email protected]
Subject: RE: 100 PSI requirement at top of Standpipe

Brad,
Here is my explanation of the 100-psi requirement, and I apologize to any
one that I might offend with such a long opinionated response. This is my
pet peeve, and I have tried my best to educate the fire service as to what
they could expect during a high-rise fire condition.

The old standpipe pressure requirement was 65-psi. This changed in the late
1980's or early 1990's after the One Merridian Place fire where two
firefighters died whiile they were searching several floors above the fire.
The lack of pressure avaiable in the standpipe allowed the fire to grow and
extend to their search area. The standpipe system had PRV hose valves
installed which were improperly adjusted to a pressure too low for fire
operations.

The NFPA-14 committee decided that since the automatic nozzles in use at
that time required an optimum 100-psi nozzle pressure, that this magic
number (100-psi) would be a good starting point. There was a long discussion
with numerous tests of various nozzles and hoses. Too little pressure did
not provided enough water and too much pressure made it very difficult to
manuver the hose around corners. The minimum 100-psi at the hose valve was a
"reasonable" pressure to allow "adequate"
pressure to the nozzle while flowing a "sufficient" quantity of water taking
into account different friction losses for different lengths and diameters
of hose that the different fire departments would use. The maximum 175-pis
was used to match the existing maximum pressure for the sprinkler systems
connected to the standpipe, and also allow a range for minimum and maximum
pressures that the PRV's could satisfy.

Since then, numerous changes have been made in  fire department operations.
There are now low pressure automatic nozzles, low friction loss hoses, and
many departments just use a non-automatic adjustable nozzle in their
high-rise packs. Since the older buildings may only have
50 to 65-psi at the hose valve while the newer buildings have 100-psi, the
manufacturers also have produced an in-line pressure gauge that can be
installed at the hose valve so the firefighter can see the pressure
available from the hose valve and make adjustments accordingly. 

Presently, it's really up to each AHJ to decide on an SOP for high-rise
fires in their jurisdication knowing that the standpipe systems have
pressures that can vary from 50 to 100-psi and may be equipped with
pressure-restricting or pressure-reducing valves which may or may not be
properly set. They need to pre-fire plan the buildings to learn how each
building standpipe system was designed.
rick matsuda
city of dallas

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Casterline
Sent: Wednesday, February 19, 2014 8:51 AM
To: [email protected]
Subject: 100 PSI requirement at top of Standpipe

Does anyone know why the technical committee settled on 100 PSI minimum at
the 2.5" hose valve?

It used to be 75 PSI, and for High Rise retrofit I have seen AHJs accept 75.

I am just curious because I think with about 60 PSI at the 2.5"
connection
to the standpipe we could get about 250 GPM at the nozzle, figuring the Pf
for the T, 2.5x0-6 nip, hose valve, and 100 feet of 2.5" hose.

A 15 psi safety factor seems reasonable, but 40 psi???

I know the F.D. might want to use a 2.5x1.5 reducer and 1.5" hose, but with
150 GPM flowing through 100 feet of 1.5" hose the Pf in the hose alone is
about 162 PSI!

So, I don't get it, but I am likely missing some simple explanation, so I'm
asking.

thanks,
Brad Casterline, NICET IV
Fire Protection Division

FSC, Inc.
P: 913-722-3473
[email protected]
www.fsc-inc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to