There really is no locate per NFPA 13. You still have max of 40/80, 4 way at change in direction and laterals no more than 6' from end of cross main. But, with all of the other requirements in chapter 9, you must calculate the bracing spacing.
I consider it just like pipe sizing calcs any more. Travis Mack, SET MFP Design, LLC Sent from my iPhone > On Feb 20, 2014, at 7:26 AM, <[email protected]> wrote: > > Seismic design category C, contractor submittal package, > > Do you provide a calc sheet for EQ bracing or just locate per NFPA 13 and > send typical catalog data sheets? > > FM Global project, BTW. > > Craig L. Prahl, CET > Fire Protection Group Lead > CH2MHILL > Lockwood Greene > 1500 International Drive > Spartanburg, SC 29303 > Direct - 864.599.4102 > Fax - 864.599.8439 > CH2MHILL Extension 74102 > [email protected] > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org