Steven,

I have never received a contractor shop drawing that covered things to the 
detail you describe.  It's often a wonder to get the basic information on the 
drawings like pipe elevations and hangers let alone anything to the depth you 
describe.

I don't disagree with your statement just saying, I've never seen it happen.  

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steven 
Scandaliato
Sent: Thursday, February 20, 2014 11:00 AM
To: [email protected]
Subject: RE: seismic bracing calcs

Wait...hold on...just to make sure, and Craig I am sure you probably know 
this...BUT we have a lot more than just calcs for braces that have to be 
addressed.  We have 4 other design features that have to be addressed.
Cplgs, clearance, separation and restraint.  This is a weakest link kinda 
thing...so just because we have braced a system does not mean it is designed 
for seismic...we have to put flex and rigid cplgs where they go, we have to 
show that we have accounted for clearance where it applies, we have to 
acknowledge that there is no separation required if applicable and we have to 
show and space b'line restraint.  Seismic design demands its own sheets and 
symbols and sheet installation notes etc.  Do not try and pile all of this onto 
an already unreadable piping plan.  EOR or Shop design, all of these categories 
must be addressed in the documents....and by the way, putting 4-ways and every 
change of direction is not a design feature required or intended by 9.3.  I see 
a lot of contractors do that thinking they are in compliance.  This may be a 
great cost saver or standardized thing you want to do with your fitters but it 
does not automatically put you in compliance with 9.3....just sayin.

One other note while I am on this, we all need to pay better attention to 
restraint.  I still have many AHJs and contractors alike that haven't heard of 
it.  If seismic is required then restraint is required.  This isn't optional.  
And pay attention to the spacing requirements for it.  Many, including myself, 
have fallen into the "end of line" mentality and think that is the only place 
we have to have it...but if you have long branchlines, you definitely will have 
more than "end of line" locations.

With Sicilian Love,

Steven Scandaliato, SET CFPS
520.971.2322 Cell
Skype: steven.scandaliato


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
rongreenman .
Sent: Thursday, February 20, 2014 9:41 AM
To: [email protected]
Subject: Re: seismic bracing calcs

Cliff's opinion is right.


On Thu, Feb 20, 2014 at 6:49 AM, Cliff Whitfield
<[email protected]>wrote:

> Craig,
>
> If you don't calc it, how do you know it works?  That would be like 
> sending in drawings with 'hydraulically calculated pipe sizes' with no 
> hydraulic calcs to prove the sizes are correct.  Just not happening.
>
> A lot of 'East Coast' contractors/designers (I fit in that category 
> even though I now live in Colorado) just show braces on their drawings 
> but it's not even close to being the correct way to do it.  They need 
> to take the time to learn from the AFSA classes that Ken Wagonner and 
> others do so that they can do it right.  I've had to take it 3 times 
> because I don't use it very often and it easy to forget without the 
> repetition but it's just something you have to do if you are doing 
> your
job correctly.
>
> Simply my opinion (but I think it's right!)
>
> Cliff Whitfield, SET
> President
> Fire Design, Inc.
> Ph: 719-488-3479
>
>
>
> [email protected]
> www.fire-design.com
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Thursday, February 20, 2014 7:27 AM
> To: [email protected]
> Subject: seismic bracing calcs
>
> Seismic design category C, contractor submittal package,
>
> Do you provide a calc sheet for EQ bracing or just locate per NFPA 13 
> and send typical catalog data sheets?
>
> FM Global project, BTW.
>
> Craig L. Prahl, CET
> Fire Protection Group Lead
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to