Thanks, sent this to the AHJ we tested at 20 psi everyone is happy.

Richard L. Mote
Rowe Sprinkler Systems, Inc.
7994 Route 522, Suite 1
PO Box 407
Middleburg, PA 17842
P 570-837-7647
F 570-837-6335

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Pete Schwab
Sent: Tuesday, February 25, 2014 1:17 PM
To: [email protected]
Subject: RE: Air Testing CPVC Piping

From Spears

http://origin.library.constantcontact.com/download/get/file/1102520706304-39/FG+Air+Test+Provision.pdf


Peter Schwab
VP of Purchasing & Engineering Technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com



Celebrating over 34 years of life safety


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jim 
Davidson
Sent: Tuesday, February 25, 2014 1:10 PM
To: [email protected]
Subject: RE: Air Testing CPVC Piping

Most CPVC manufacturers advise against air testing a CPVC piping system since 
pipe failures usually are very dangerous because of the plastic fragments 
produced by the pipe failure. There is a lot of energy store in a pipe system 
being tested with air. The stored energy is capable of causing a fatality due 
to flying pipe shards. 

I would recommend against  testing with air.

Regards

Jim



Sent from my Galaxy S®III

-------- Original message --------
From: Richard Mote <[email protected]> 
Date:2014/02/25  13:00  (GMT-05:00) 
To: [email protected] 
Subject: Air Testing CPVC Piping 

We have an AHJ requiring a 50 psi test on CPVC piping, we think that is 
excessive, and have always used 20 psi max. I know the best practice is to do a 
hydrostatic test, but thanks to the polar vortex we are having freezing 
temperatures and the builder needs to close up his walls. Right now we are 
looking for chapter and verse as to what the maximum recommended pressure is 
for an air test. Have looked through 3 different CPVC installation handbooks 
but the number is not jumping out at me. The TYCO Residential Dry System runs 
10 - 15 psi pressure. Note: This is not  a residential dry system we are trying 
to air test a system so the drywall can go on. When the building gets the heat 
turned on it will be a wet system.

Richard L. Mote
Rowe Sprinkler Systems, Inc.
7994 Route 522, Suite 1
PO Box 407
Middleburg, PA 17842
P 570-837-7647
F 570-837-6335

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to