Brad, What the hell are you talking about?

My girlfriend says that there is nothing about moving heat in NFPA 13, and
I sure couldn't find nothing.

Tony P


On Sun, Mar 23, 2014 at 12:45 PM, Brad Casterline
<[email protected]>wrote:

> One more thing Anthony, if the head is under this moving heat, it will not
> activate in those critical 10 to 15 minutes it takes the Heros to get
> there, so they are useless as a pool cue hard on both ends but soft in the
> middle.
>
> > On Mar 23, 2014, at 10:34 AM, Brad Casterline <[email protected]>
> wrote:
> >
> > Sal, I believe years ago, for a very brief time, Potter-Roemer had a
> listed heat collector. I called them Dust Pans.
> > Tony, for 30 years I was a designer for contractors and the last 10 I
> have worked for a Consulting Firm. I desperately miss the smell of warm
> cutting oil on smoke breaks out in the shop. Instead of heat collecting
> around a head, picture it moving across a head.
> > Cecil, I think I see what you did there. No question or request for more
> details-- I simply thought you would appreciate the results I got from
> modeling my question of myself "which activates faster, a 155 SR or a 200
> QR? if I used Dr. Floyd's excellent set-up instead of my own. I had gotten
> the same result using my own- 155 SR wins, but I had more confidence in the
> results using Jason's set-up.
> >
> >> On Mar 23, 2014, at 9:38 AM, Tony Palmero <[email protected]>
> wrote:
> >>
> >> Thanks, Mr. Izzo.  THAT's what I was askin'.  It seems like maybe I DO
> >> understand.  I appreciate that.
> >>
> >> Tony
> >>
> >>
> >> On Sun, Mar 23, 2014 at 9:33 AM, Tony Palmero <[email protected]
> >wrote:
> >>
> >>> Yo, Bradley!
> >>>
> >>> Thanks for the explaination.  But to be honest, I didn't understand
> none
> >>> of that.  What I think I heard you say was that sprinklers at the
> ceiling
> >>> is enuff to make the heads work right.  Am i correct over here?
> >>>
> >>> I don't know how you have the time to design sprinkler systems AND do
> >>> tests for sprinklers and jet engines.    I can barely make it in time
> to
> >>> the elementary school to run the lights after puttin away the threadin
> >>> machine.  Do yous guys need any fitters?  I think I could really learn
> alot
> >>> about something that has nothing to do with sprinklers over there and
> that
> >>> would be a nice break.  ya know?
> >>>
> >>> sencerely,
> >>>
> >>> Anthony S. Palmero
> >>>
> >>>
> >>>
> >>>
> >>>
> >>>
> >>> On Sun, Mar 23, 2014 at 8:56 AM, Brad Casterline <
> [email protected]>wrote:
> >>>
> >>>> Tony,
> >>>>
> >>>> I spent some time figuring out why heat collectors did not work and
> came
> >>>> up with:
> >>>> They are installed horizontal, parallel to the floor and 'ceiling
> jet'.
> >>>> If they were vertical, like a 'baffle', with the head ~6" below and
> from
> >>>> center they would work, but we would call them heat director.
> >>>> For years I imagined the heat rising, banking straight down off the
> roof
> >>>> deck and when it finally filled the 12" distance to the head it would
> pop.
> >>>> But if that is what is happening, the emergency is not in that area--
> the
> >>>> emergency is where the ~200 degree air is moving horizontally across
> the
> >>>> head at 5 to 10 feet/second. We would need 2 'baffles', in a "+"
> shape, to
> >>>> account for the direction the jet is moving when it gets to the
> >>>> head/director.
> >>>>
> >>>> Brad Casterline, SET
> >>>>
> >>>> Warning: I am a good example of the 'bad' posters Greg mentioned.
> >>>>
> >>>>>> On Mar 23, 2014, at 7:44 AM, Greg McGahan <[email protected]>
> >>>>> wrote:
> >>>>>
> >>>>> Tony,
> >>>>>
> >>>>> He was being sincere and you are incorrect. The "heat collectors" can
> >>>> delay
> >>>>> the operation of a head from what I have learned not only on the
> forum
> >>>> but
> >>>>> also from other sources...The fire marshall is falling for one of the
> >>>>> classic blunders.....the other being never start a land war in
> >>>> Asia...(that
> >>>>> was a joke)
> >>>>>
> >>>>> I am silent much of the time on this forum but you quickly get a feel
> >>>> for
> >>>>> who knows what they are talking about and who is just talking. I
> tend to
> >>>>> listen to to RG. You seem sincere and curious, good for you. I would
> be
> >>>>> careful who I listen to.
> >>>>>
> >>>>> Just my two cents worth......
> >>>>> Greg
> >>>>>
> >>>>>
> >>>>>
> >>>>> Greg McGahan
> >>>>> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> >>>>> 1160 McKenzie Road
> >>>>> Cantonment, FL 32533
> >>>>> 850-937-1850
> >>>>> fax 850-937-1852
> >>>>>
> >>>>>
> >>>>> On Sat, Mar 22, 2014 at 11:23 PM, Tony Palmero <
> [email protected]
> >>>>> wrote:
> >>>>>
> >>>>>> Dr. Greenman,
> >>>>>>
> >>>>>> I had a fire marshal make me put dem on sprinklers before.  Since I
> >>>> don't
> >>>>>> really know much about fire dynamicks (isn't dat what yous guys call
> >>>> it?),
> >>>>>> I always thought the pie pans made hot air go to the head faster.
> >>>>>>
> >>>>>> Tony Palmero
> >>>>>>
> >>>>>>
> >>>>>>
> >>>>>>
> >>>>>> On Sat, Mar 22, 2014 at 11:04 PM, Steve Leyton
> >>>>>> <[email protected]>wrote:
> >>>>>>
> >>>>>>> Okay, giant oops there. Inside joke, meant to send that to Ron
> only.
> >>>> Memo
> >>>>>>> to self - don't use phone for email.
> >>>>>>>
> >>>>>>>
> >>>>>>> Sent from my Verizon Wireless 4G LTE smartphone
> >>>>>>>
> >>>>>>> -------- Original message --------
> >>>>>>> From: Steve Leyton <[email protected]>
> >>>>>>> Date:03/22/2014  9:01 PM  (GMT-08:00)
> >>>>>>> To: [email protected]
> >>>>>>> Subject: RE: Quick response
> >>>>>>>
> >>>>>>> What kinda fuckstick dreamed THAT shit up?
> >>>>>>>
> >>>>>>>
> >>>>>>> Sent from my Verizon Wireless 4G LTE smartphone
> >>>>>>>
> >>>>>>> -------- Original message --------
> >>>>>>> From: "rongreenman ." <[email protected]>
> >>>>>>> Date:03/22/2014  8:57 PM  (GMT-08:00)
> >>>>>>> To: [email protected]
> >>>>>>> Subject: Re: Quick response
> >>>>>>>
> >>>>>>> I was thinking Tony. So-called "heat collectors" have been known to
> >>>> slow
> >>>>>>> the response of sprinkler heads by forming an aerodynamic phenomena
> >>>>>> whereby
> >>>>>>> the head is actually protected from the heat reaching it due to a
> >>>> pocket
> >>>>>>> stagnant air  that surrounds the head and deflects much of the
> >>>> convected
> >>>>>>> heat. perhaps putting pie pans over the heads would help.
> >>>>>>>
> >>>>>>>
> >>>>>>> On Sat, Mar 22, 2014 at 8:00 PM, Tony Palmero <
> >>>> [email protected]
> >>>>>>>> wrote:
> >>>>>>>
> >>>>>>>> Thanks, Dr Greenman!
> >>>>>>>>
> >>>>>>>> Yes, the lights are hot.  Sitting in that stupid chair makes me
> >>>> sweat a
> >>>>>>>> lot. I have to be careful not to drip on the other parents below.
> >>>>>>>>
> >>>>>>>> Someday it would be great to try running lights in Hollywood!  But
> >>>> for
> >>>>>>> now,
> >>>>>>>> it'll have to be only at Spring Concerts at night and hanging
> >>>> sprinkler
> >>>>>>>> pipe during the day. Do the Hollywood studios have fitters on the
> >>>>>>> payroll?
> >>>>>>>>
> >>>>>>>> Tony Palmero
> >>>>>>>>
> >>>>>>>>
> >>>>>>>>
> >>>>>>>>
> >>>>>>>> On Sat, Mar 22, 2014 at 9:37 PM, rongreenman . <
> >>>> [email protected]
> >>>>>>>>> wrote:
> >>>>>>>>
> >>>>>>>>> How about an empirical answer. If these lights are similar to
> those
> >>>>>>> used
> >>>>>>>> in
> >>>>>>>>> movie production the answer is yes. Has happened a lot. I was
> only
> >>>>>>>> involved
> >>>>>>>>> with one movie, but I was involved because they decided they
> needed
> >>>> a
> >>>>>>>>> sprinkler guy because they'd had several discharges in the past
> and
> >>>>>> the
> >>>>>>>>> building they were using for a sound stage had relatively (about
> >>>> 30')
> >>>>>>>>> ceilings. They initially hired me to turn the system off every
> day
> >>>> at
> >>>>>>> the
> >>>>>>>>> beginning of work and come back to turn it on at night. Obviously
> >>>>>> this
> >>>>>>>> was
> >>>>>>>>> not a solution, which the lead production guy understood and
> took my
> >>>>>>>> advice
> >>>>>>>>> to change the heads to high temps while they were using the
> building
> >>>>>>> and
> >>>>>>>> to
> >>>>>>>>> return and make them standard temp when filming was done.
> Numbers?
> >>>>>>> Don't
> >>>>>>>>> know. The ones you use must be hot or you wouldn't be asking. I'd
> >>>>>> talk
> >>>>>>> to
> >>>>>>>>> the maintenance guys from the school  and ask if they've ever
> had a
> >>>>>>>>> problem, and if so, how they've solved it.
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>> On Sat, Mar 22, 2014 at 4:38 PM, Fire Protection Services <
> >>>>>>>>> [email protected]> wrote:
> >>>>>>>>>
> >>>>>>>>>> Yes Brad I will
> >>>>>>>>>>
> >>>>>>>>>> Sent from my iPhone
> >>>>>>>>>>
> >>>>>>>>>>> On Mar 22, 2014, at 6:22 PM, Brad Casterline <
> >>>>>>>> [email protected]>
> >>>>>>>>>> wrote:
> >>>>>>>>>>>
> >>>>>>>>>>> True Jamie and Tony that's why I said I am wrong. I tend to
> >>>>>>>> over-think
> >>>>>>>>>> things. Something to consider though is it is not just QR you
> have
> >>>>>> to
> >>>>>>>>> worry
> >>>>>>>>>> about- i would love to do some actual tests but I believe a 155
> SR
> >>>>>>>> would
> >>>>>>>>>> activate quicker than a 200 QR, under the same conditions.
> Chris,
> >>>>>>> could
> >>>>>>>>> ask
> >>>>>>>>>> your instructor about that?
> >>>>>>>>>>>
> >>>>>>>>>>>> On Mar 22, 2014, at 5:55 PM, Jamie Seidl <
> [email protected]
> >>>>>>>
> >>>>>>>>> wrote:
> >>>>>>>>>>>>
> >>>>>>>>>>>> There are rules for heat sources, ie 250w lights, sky lights
> >>>>>>> ect...
> >>>>>>>>> Sun
> >>>>>>>>>> light exposure requires an increase in temperature just as
> >>>>>> proximity
> >>>>>>> to
> >>>>>>>>>> hear sources.
> >>>>>>>>>>>>
> >>>>>>>>>>>> Sent from my iPhone
> >>>>>>>>>>>>
> >>>>>>>>>>>>> On Mar 22, 2014, at 6:52 PM, Tony Palmero <
> >>>>>>> [email protected]
> >>>>>>>>>
> >>>>>>>>>> wrote:
> >>>>>>>>>>>>>
> >>>>>>>>>>>>> Brad,
> >>>>>>>>>>>>>
> >>>>>>>>>>>>> WTF?  What does a skylight have to do with it if the light
> >>>>>> would
> >>>>>>>> have
> >>>>>>>>>> to be
> >>>>>>>>>>>>> touching the sprinkler to set it off?
> >>>>>>>>>>>>>
> >>>>>>>>>>>>> Is there a rule in NFPA 13 for this kind of stuff?  I just
> want
> >>>>>>> to
> >>>>>>>>> get
> >>>>>>>>>> pipe
> >>>>>>>>>>>>> in the air and do it right. Theoretically speakin'.
> >>>>>>>>>>>>>
> >>>>>>>>>>>>> Tony
> >>>>>>>>>>>>>
> >>>>>>>>>>>>>
> >>>>>>>>>>>>> On Sat, Mar 22, 2014 at 5:34 PM, Brad Casterline <
> >>>>>>>>>> [email protected]>wrote:
> >>>>>>>>>>>>>
> >>>>>>>>>>>>>> We do have to use higher temp heads in skylights though so I
> >>>>>> am
> >>>>>>>>> wrong!
> >>>>>>>>>>>>>> Don't shine it on the sprinklers or the kids too long at a
> >>>>>> time!
> >>>>>>>>>>>>>>
> >>>>>>>>>>>>>>>> On Mar 22, 2014, at 5:25 PM, Brad Casterline <
> >>>>>>>>>> [email protected]>
> >>>>>>>>>>>>>>> wrote:
> >>>>>>>>>>>>>>>
> >>>>>>>>>>>>>>> I think the light would have to be almost touching the
> >>>>>> element
> >>>>>>> to
> >>>>>>>>>> set it
> >>>>>>>>>>>>>> off (conduction). Response Time Index is a measure of the
> temp
> >>>>>>> AND
> >>>>>>>>>> velocity
> >>>>>>>>>>>>>> of the air (convection). The energy of the light itself
> drops
> >>>>>>>> like a
> >>>>>>>>>> rock
> >>>>>>>>>>>>>> (^4) with distance from the source. (the radiative
> component).
> >>>>>>>>>>>>>>> Of course I could be wrong Tony, and often am :).
> >>>>>>>>>>>>>>>
> >>>>>>>>>>>>>>>
> >>>>>>>>>>>>>>>> On Mar 22, 2014, at 4:50 PM, Tony Palmero <
> >>>>>>>>> [email protected]>
> >>>>>>>>>>>>>> wrote:
> >>>>>>>>>>>>>>>>
> >>>>>>>>>>>>>>>> Brad,
> >>>>>>>>>>>>>>>>
> >>>>>>>>>>>>>>>> I was wondering if lights could send enough heat to a
> >>>>>> element
> >>>>>>> to
> >>>>>>>>>> make
> >>>>>>>>>>>>>> it go
> >>>>>>>>>>>>>>>> off.  I run the spotlight at school plays at my kid's
> school
> >>>>>>> and
> >>>>>>>>> was
> >>>>>>>>>>>>>> just
> >>>>>>>>>>>>>>>> thinkin' about it.
> >>>>>>>>>>>>>>>>
> >>>>>>>>>>>>>>>> You guys on the forum are great.  I don't think any of
> this
> >>>>>>>> stuff
> >>>>>>>>>>>>>> matters
> >>>>>>>>>>>>>>>> to me putting pipe in the air, but it is fascinating.
> >>>>>>>>>>>>>>>>
> >>>>>>>>>>>>>>>> Tony Palmero
> >>>>>>>>>>>>>>>>
> >>>>>>>>>>>>>>>>
> >>>>>>>>>>>>>>>> On Sat, Mar 22, 2014 at 4:45 PM, Brad Casterline <
> >>>>>>>>>>>>>> [email protected]>wrote:
> >>>>>>>>>>>>>>>>
> >>>>>>>>>>>>>>>>> It depends on how fast the heated air is moving across
> it,
> >>>>>>>> which
> >>>>>>>>>>>>>> depends
> >>>>>>>>>>>>>>>>> on fire size and ceiling height. But this is true for
> >>>>>>> standard
> >>>>>>>>>> response
> >>>>>>>>>>>>>>>>> also. May I ask why you ask?
> >>>>>>>>>>>>>>>>>
> >>>>>>>>>>>>>>>>>>> On Mar 22, 2014, at 4:27 PM, Tony Palmero <
> >>>>>>>>>> [email protected]>
> >>>>>>>>>>>>>>>>>> wrote:
> >>>>>>>>>>>>>>>>>>
> >>>>>>>>>>>>>>>>>> How quick is a qwik resp sprinler?
> >>>>>>>>>>>>>>>>>> _______________________________________________
> >>>>>>>>>>>>>>>>>> Sprinklerforum mailing list
> >>>>>>>>>>>>>>>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>>>>>>>>>>>>>> _______________________________________________
> >>>>>>>>>>>>>>>>> Sprinklerforum mailing list
> >>>>>>>>>>>>>>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>>>>>>>>>>>>> _______________________________________________
> >>>>>>>>>>>>>>>> Sprinklerforum mailing list
> >>>>>>>>>>>>>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>>>>>>>>>>>> _______________________________________________
> >>>>>>>>>>>>>>> Sprinklerforum mailing list
> >>>>>>>>>>>>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>>>>>>>>>>> _______________________________________________
> >>>>>>>>>>>>>> Sprinklerforum mailing list
> >>>>>>>>>>>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>>>>>>>>>> _______________________________________________
> >>>>>>>>>>>>> Sprinklerforum mailing list
> >>>>>>>>>>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>>>>>>>>> _______________________________________________
> >>>>>>>>>>>> Sprinklerforum mailing list
> >>>>>>>>>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>>>>>>>> _______________________________________________
> >>>>>>>>>>> Sprinklerforum mailing list
> >>>>>>>>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>>>>>>> _______________________________________________
> >>>>>>>>>> Sprinklerforum mailing list
> >>>>>>>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>> --
> >>>>>>>>> Ron Greenman
> >>>>>>>>> Instructor
> >>>>>>>>> Fire Protection Engineering Technology
> >>>>>>>>> Bates Technical College
> >>>>>>>>> 1101 So. Yakima Ave.
> >>>>>>>>> Tacoma, WA 98405
> >>>>>>>>>
> >>>>>>>>> [email protected]
> >>>>>>>>>
> >>>>>>>>> http://www.bates.ctc.edu/fireprotection/
> >>>>>>>>>
> >>>>>>>>> 253.680.7346
> >>>>>>>>> 253.576.9700 (cell)
> >>>>>>>>>
> >>>>>>>>> Member:
> >>>>>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> >>>>>>>>>
> >>>>>>>>> They are happy men whose natures sort with their vocations.
> -Francis
> >>>>>>>> Bacon,
> >>>>>>>>> essayist, philosopher, and statesman (1561-1626)
> >>>>>>>>>
> >>>>>>>>> A problem well stated is a problem half solved. -Charles F.
> >>>>>> Kettering,
> >>>>>>>>> inventor and engineer (1876-1958)
> >>>>>>>>> _______________________________________________
> >>>>>>>>> Sprinklerforum mailing list
> >>>>>>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>>>>> _______________________________________________
> >>>>>>>> Sprinklerforum mailing list
> >>>>>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>>>>
> >>>>>>>
> >>>>>>>
> >>>>>>> --
> >>>>>>> Ron Greenman
> >>>>>>> Instructor
> >>>>>>> Fire Protection Engineering Technology
> >>>>>>> Bates Technical College
> >>>>>>> 1101 So. Yakima Ave.
> >>>>>>> Tacoma, WA 98405
> >>>>>>>
> >>>>>>> [email protected]
> >>>>>>>
> >>>>>>> http://www.bates.ctc.edu/fireprotection/
> >>>>>>>
> >>>>>>> 253.680.7346
> >>>>>>> 253.576.9700 (cell)
> >>>>>>>
> >>>>>>> Member:
> >>>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> >>>>>>>
> >>>>>>> They are happy men whose natures sort with their vocations.
> -Francis
> >>>>>> Bacon,
> >>>>>>> essayist, philosopher, and statesman (1561-1626)
> >>>>>>>
> >>>>>>> A problem well stated is a problem half solved. -Charles F.
> Kettering,
> >>>>>>> inventor and engineer (1876-1958)
> >>>>>>> _______________________________________________
> >>>>>>> Sprinklerforum mailing list
> >>>>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>>>> _______________________________________________
> >>>>>>> Sprinklerforum mailing list
> >>>>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>>>> _______________________________________________
> >>>>>>> Sprinklerforum mailing list
> >>>>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>>> _______________________________________________
> >>>>>> Sprinklerforum mailing list
> >>>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>> _______________________________________________
> >>>>> Sprinklerforum mailing list
> >>>>> [email protected]
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>> _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> [email protected]
> >>>>
> >>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to