30" deep may require the use of specially listed concealed space sprinklers if 
it is a roof with slope of less than 2:12. 

But to your original question, temp does not negate the use of the qr 
reduction.  

Travis Mack, SET
MFP Design, LLC

Sent from my iPhone

> On Apr 19, 2014, at 1:53 PM, <[email protected]> wrote:
> 
> Brad,
> 
> That was my thought also.
> 
> 
> Mike Bell
> Senior Designer, S.E.T. Lvl IV
> Aero Automatic Sprinkler Company
> 21605 N Central Ave
> Phoenix AZ 85024
> PH: (623) 580-7848
> FX: (623) 580-5230
> Mobile: (623) 229-4980
> [email protected]
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Brad 
> Casterline
> Sent: Saturday, April 19, 2014 1:47 PM
> To: [email protected]
> Subject: Re: Intermediate Q.R. Sprinklers
> 
> No, there are 4 criteria to meet, and temp is not one.
> 
>> On Apr 19, 2014, at 3:43 PM, <[email protected]> wrote:
>> 
>> Does the use of a 200deg Q.R. sprinkler negate the Design Area Reduction for 
>> the remote area?
>> I am calculating an unused attic of a school trailer approximately 2'-6" 
>> deep. Heads above & below with the greater number of sprinklers in the attic 
>> area.
>> 
>> Mike B
>> Aero Fire
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to