Mike,
>From the current available tools to predict activation times, and my current 
>"guess" at what LOW from NFPA 13, 5.2 is, I think the activation time 
>difference between a 155F QR and a 200F QR is about 6 seconds per foot of 
>ceiling height. I looked at 10 through 20 foot clg hgt, so at 10 ft the diff 
>is 6 sec, at 12-6 the diff is 15 sec, etc, so I appreciate the fact that temp 
>is not one of the 4 criteria for QR Reduction. I try not to predict the 
>outcome of modeling calcs ( bcoz I usually get it bassakwards), but I would 
>think with a 2'-6" ceiling height Ord thru High Temp, SR or QR, would provide 
>a reasonable degree of protection. But being NICET certified means we don't 
>have to think, we just have to do it by the book, which I also appreciate!

brad

> On Apr 19, 2014, at 4:30 PM, Brad Casterline <[email protected]> wrote:
> 
> It sure would be nice if the book said something like "for 30" tall attics, 
> stub some dry uprights up in there at about 10x10 spacing, at about 15" 
> deflector, and tell the concealed space Marketeers to have a nice day :)
> 
>> On Apr 19, 2014, at 4:14 PM, Travis Mack <[email protected]> wrote:
>> 
>> 30" deep may require the use of specially listed concealed space sprinklers 
>> if it is a roof with slope of less than 2:12. 
>> 
>> But to your original question, temp does not negate the use of the qr 
>> reduction.  
>> 
>> Travis Mack, SET
>> MFP Design, LLC
>> 
>> Sent from my iPhone
>> 
>>> On Apr 19, 2014, at 1:53 PM, <[email protected]> wrote:
>>> 
>>> Brad,
>>> 
>>> That was my thought also.
>>> 
>>> 
>>> Mike Bell
>>> Senior Designer, S.E.T. Lvl IV
>>> Aero Automatic Sprinkler Company
>>> 21605 N Central Ave
>>> Phoenix AZ 85024
>>> PH: (623) 580-7848
>>> FX: (623) 580-5230
>>> Mobile: (623) 229-4980
>>> [email protected]
>>> 
>>> 
>>> 
>>> 
>>> -----Original Message-----
>>> From: [email protected] 
>>> [mailto:[email protected]] On Behalf Of Brad 
>>> Casterline
>>> Sent: Saturday, April 19, 2014 1:47 PM
>>> To: [email protected]
>>> Subject: Re: Intermediate Q.R. Sprinklers
>>> 
>>> No, there are 4 criteria to meet, and temp is not one.
>>> 
>>>> On Apr 19, 2014, at 3:43 PM, <[email protected]> wrote:
>>>> 
>>>> Does the use of a 200deg Q.R. sprinkler negate the Design Area Reduction 
>>>> for the remote area?
>>>> I am calculating an unused attic of a school trailer approximately 2'-6" 
>>>> deep. Heads above & below with the greater number of sprinklers in the 
>>>> attic area.
>>>> 
>>>> Mike B
>>>> Aero Fire
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to