Vince,
No common sense allowed, but I think I can show him through 13 that the
requirements are all meet.  

Thank You,

Bob Knight, CET III
208-318-3057
www.Firebyknight.com



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Vince Sabolik
Sent: Friday, June 27, 2014 12:21 PM
To: [email protected]
Subject: Re: Cooler Calc

Of course cooler only or 900sf

                                         BUT

If he is an AHJ and he decides if you get a C of O, then he gets 1,500 sq
ft.
Another "Authority Having Jurisdiction", but no common sense. What's new?



On 6/27/2014 1:11 PM, Bob wrote:
> I have a 1,392 sf cooler.  I calc'ed the entire area of the cooler and
> submitted.  The AHJ is telling me that I need to calc additional
sprinklers
> at the ceiling to have a 1500 sf design area.  I don't think I need to do
> this, I was looking at this as a separate fire area, and I don't see it
> being much different than not adding heads below ducts or other large
> obstructions.  Do I need to calc additional sprinklers at the ceiling for
> this application?
>
> Thank You,
>
> Bob Knight, CET III
> 208-318-3057
> www.Firebyknight.com
>
>
>

-- 

West Tech Fire Protection, Inc.
11351 Pearl Road   / Strongsville, Ohio   44136
Phone 440 238-4800    Fax 440 238-4876
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org