He told me over lunch many years ago. I forgot that he later to the story
on the Forum. Very funny stuff.


On Mon, Jul 7, 2014 at 9:24 AM, Brad Casterline <[email protected]>
wrote:

> Search 'Ed vining deluge' Craig, you'll get there.
> Very funny stuff!
>
> > On Jul 7, 2014, at 11:08 AM, <[email protected]> wrote:
> >
> > There's nothing at the link.
> >
> > Craig L. Prahl
> > Fire Protection Group Lead
> > CH2MHILL
> > Lockwood Greene
> > 1500 International Drive
> > Spartanburg, SC  29303
> > Direct - 864.599.4102
> > Fax - 864.599.8439
> > CH2MHILL Extension  74102
> > [email protected]
> >
> >
> > -----Original Message-----
> > From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Brad
> Casterline
> > Sent: Monday, July 07, 2014 12:02 PM
> > To: [email protected]
> > Subject: Re: Identification of preaction system types
> >
> >
> https://www.mail-archive.com/[email protected]&q=subject:%22Re%3A+Gridded+pre%26%2345%3Baction+and+dry%22
> >
> > Well I got impatient so I searched the archives for Ed vining deluge
> >
> >> On Jul 7, 2014, at 10:02 AM, Brad Casterline <[email protected]>
> wrote:
> >>
> >> your cue Ed... talk to us...
> >>
> >>> On Jul 7, 2014, at 9:12 AM, "rongreenman ." <[email protected]>
> wrote:
> >>>
> >>> Craig,
> >>>
> >>> Ed Vining has a good story about deluge and pre-action systems and
> >>> how contractors leap for dollars where wiser men fear to tread.
> >>>
> >>>
> >>> On Mon, Jul 7, 2014 at 7:06 AM, Brad Casterline
> >>> <[email protected]>
> >>> wrote:
> >>>
> >>>> Craig, when I first read this post I thought "HUH, PREACTION
> WAREHOUSE?"
> >>>> No experience with that. I think the details of a combined DRY and
> >>>> PREACTION system are still in 13. Maybe ~25 years ago that is what
> >>>> this was, when computers cost 20k.
> >>>>
> >>>>>> On Jul 7, 2014, at 7:45 AM, Brad Casterline
> >>>>>> <[email protected]>
> >>>>> wrote:
> >>>>>
> >>>>> I guess you could start a fire, and follow the sequence of events,
> >>>> taking measurements on this and that here and there.
> >>>>>
> >>>>>> On Jul 7, 2014, at 7:26 AM, <[email protected]> wrote:
> >>>>>>
> >>>>>> I have provided all of the information that I have.  The
> >>>>>> functionality
> >>>> of the system as a whole is questionable.  Without contractor shop
> >>>> drawings there is no way to surmise the type of system or how it was
> actually
> >>>> designed other than by what you can physically see.   There is a list
> of
> >>>> "why did they do that", "how did they come up with that number" and
> >>>> other various design and installation questions that just don't make
> good sense.
> >>>>>>
> >>>>>> So thanks for all the input but that's about all we've got.
> >>>>>>
> >>>>>> Craig L. Prahl
> >>>>>> Fire Protection Group Lead
> >>>>>> CH2MHILL
> >>>>>> Lockwood Greene
> >>>>>> 1500 International Drive
> >>>>>> Spartanburg, SC  29303
> >>>>>> Direct - 864.599.4102
> >>>>>> Fax - 864.599.8439
> >>>>>> CH2MHILL Extension  74102
> >>>>>> [email protected]
> >>>>>>
> >>>>>>> On Jul 3, 2014, at 6:52 PM, Mike Cabral
> >>>>>>> <[email protected]>
> >>>> wrote:
> >>>>>>>
> >>>>>>> Supervisory air is a necessary component for single interlock. No
> >>>> supervisory air and it's not even a dry pipe system. We are not
> >>>> getting required information regarding this installation.
> >>>>>>>
> >>>>>>> This might be a Supertex system using HAD's. From what I recall
> >>>>>>> from
> >>>> the thread there was no releasing panel or no access to the panel
> >>>> very strange, now no supervisory air? What's the compressor for?
> >>>>>>>
> >>>>>>> A photo of the riser would be helpful.
> >>>>>>>
> >>>>>>> Mike
> >>>>>>>
> >>>>>>> Happy Holliday
> >>>>>>>
> >>>>>>>
> >>>>>>>
> >>>>>>> Sent from my iPhone
> >>>>>>>
> >>>>>>>> On Jul 3, 2014, at 5:01 PM, Kenneth Berman
> >>>>>>>> <[email protected]>
> >>>> wrote:
> >>>>>>>>
> >>>>>>>> If there's no pneumatic supervision of piping, and there's been
> >>>>>>>> no mention of a pilot line, it sounds like a single interlock.
> >>>>>>>>
> >>>>>>>>
> >>>>>>>>> On Mon, Jun 30, 2014 at 10:32 AM, <[email protected]> wrote:
> >>>>>>>>>
> >>>>>>>>> OK, there we are.
> >>>>>>>>>
> >>>>>>>>> One other thing I just discovered,  there is no pneumatic
> >>>>>>>>> supervision of the piping.  The only air compressor served a
> >>>>>>>>> dry
> >>>> standpipe system.
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>> Craig L. Prahl
> >>>>>>>>> Fire Protection Group Lead
> >>>>>>>>> CH2MHILL
> >>>>>>>>> Lockwood Greene
> >>>>>>>>> 1500 International Drive
> >>>>>>>>> Spartanburg, SC  29303
> >>>>>>>>> Direct - 864.599.4102
> >>>>>>>>> Fax - 864.599.8439
> >>>>>>>>> CH2MHILL Extension  74102
> >>>>>>>>> [email protected]
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>> -----Original Message-----
> >>>>>>>>> From: Sprinklerforum [mailto:
> >>>>>>>>> [email protected]] On Behalf Of
> >>>>>>>>> Johnson, Duane (NIH/OD/ORS) [C]
> >>>>>>>>> Sent: Monday, June 30, 2014 11:13 AM
> >>>>>>>>> To: '[email protected]'
> >>>>>>>>> Subject: RE: Identification of preaction system types
> >>>>>>>>>
> >>>>>>>>> 1999 has 30% increase for dry and preaction systems protecting
> >>>>>>>>> rack storage 7-4.1.5.2 and 7-4.1.5.3. There is a bar next to
> >>>>>>>>> the
> >>>> paragraphs.
> >>>>>>>>> There is also an exception that says the requirement does not
> >>>>>>>>> apply to preaction systems where it can be demonstrated that
> >>>>>>>>> the detection system activates the system as quickly as a wet
> >>>>>>>>> pipe system. Sounds like the beginning of a new requirement...
> >>>>>>>>>
> >>>>>>>>> Duane Johnson, PE
> >>>>>>>>> Program Manager
> >>>>>>>>> Division of the Fire Marshal (Contractor) Office of Research
> >>>>>>>>> Services National Institutes of Health
> >>>>>>>>> 301-496-0487
> >>>>>>>>>
> >>>>>>>>> "Protecting Science - One Sprinkler at a Time"
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>> -----Original Message-----
> >>>>>>>>> From: [email protected] [mailto:[email protected]]
> >>>>>>>>> Sent: Monday, June 30, 2014 11:07 AM
> >>>>>>>>> To: [email protected]
> >>>>>>>>> Subject: RE: Identification of preaction system types
> >>>>>>>>>
> >>>>>>>>> That's what I'm trying to track down.  When did that provision
> >>>>>>>>> go
> >>>> away?
> >>>>>>>>>
> >>>>>>>>> I know today's requirements, just need verification of design
> >>>>>>>>> requirements or allowances in 1982.
> >>>>>>>>>
> >>>>>>>>> I have a copy of NFPA 231 from 1978 but it doesn't address NFPA
> >>>>>>>>> 13 issues nor speak of preaction systems.
> >>>>>>>>>
> >>>>>>>>> Craig L. Prahl
> >>>>>>>>> Fire Protection Group Lead
> >>>>>>>>> CH2MHILL
> >>>>>>>>> Lockwood Greene
> >>>>>>>>> 1500 International Drive
> >>>>>>>>> Spartanburg, SC  29303
> >>>>>>>>> Direct - 864.599.4102
> >>>>>>>>> Fax - 864.599.8439
> >>>>>>>>> CH2MHILL Extension  74102
> >>>>>>>>> [email protected]
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>> -----Original Message-----
> >>>>>>>>> From: Sprinklerforum [mailto:
> >>>>>>>>> [email protected]] On Behalf Of
> >>>>>>>>> John Denhardt
> >>>>>>>>> Sent: Monday, June 30, 2014 10:56 AM
> >>>>>>>>> To: '[email protected]'
> >>>>>>>>> Subject: RE: Identification of preaction system types
> >>>>>>>>>
> >>>>>>>>> There is no increase in remote area on single interlocked back
> >>>>>>>>> in
> >>>> the day.
> >>>>>>>>> Several editions ago (??) that was deleted for storage.  Now
> >>>>>>>>> there is a 30% increase in remote area for all pre-action
> >>>>>>>>> systems in
> >>>> storage.
> >>>>>>>>> Thanks,
> >>>>>>>>>
> >>>>>>>>> John
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>> John August Denhardt, P.E., FSFPE
> >>>>>>>>>
> >>>>>>>>> Strickland Fire Protection Incorporated
> >>>>>>>>>
> >>>>>>>>> 5113 Berwyn Road
> >>>>>>>>>
> >>>>>>>>> College Park, Maryland 20740
> >>>>>>>>>
> >>>>>>>>> Office Telephone Number:  301-474-1136
> >>>>>>>>>
> >>>>>>>>> Mobile Telephone Number:  301-343-1457
> >>>>>>>>>
> >>>>>>>>> FIRE SPRINKLERS SAVE LIVES - Can you live without them?
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>> -----Original Message-----
> >>>>>>>>> From: Sprinklerforum [mailto:
> >>>>>>>>> [email protected]] On Behalf Of
> >>>>>>>>> [email protected]
> >>>>>>>>> Sent: Monday, June 30, 2014 10:55 AM
> >>>>>>>>> To: [email protected]
> >>>>>>>>> Subject: RE: Identification of preaction system types
> >>>>>>>>>
> >>>>>>>>> Thanks for all the input.
> >>>>>>>>>
> >>>>>>>>> I don't have access to the releasing panel.
> >>>>>>>>>
> >>>>>>>>> The hydraulic placard gives no indication of the system type.
> >>>>>>>>> Design data is 0.26/4000 but that lines up exactly with the
> >>>>>>>>> 1978 NFPA 231 for Class IV commodities so no real help there.
> >>>>>>>>> It doesn't appear they provided for the 30% increase for dry
> system.
> >>>>>>>>>
> >>>>>>>>> I thought I had seen at some point in time within NFPA 13 that
> >>>>>>>>> one of the preaction system types (I believe it was single
> >>>>>>>>> interlock) were considered the same as wet due to water filling
> >>>>>>>>> pipes before sprinkler operation and therefore did not require
> >>>>>>>>> the 30% increase in design area.  I can't seem to find that
> >>>>>>>>> verbiage in past or present NFPA 13 Standards now that I'm
> >>>>>>>>> looking for it.  Any clues or
> >>>> was I mislead?
> >>>>>>>>>
> >>>>>>>>> I have Engineer's drawings from 1982, no contractor shop
> >>>>>>>>> drawings or calculations.
> >>>>>>>>>
> >>>>>>>>> There are no data sheets.
> >>>>>>>>>
> >>>>>>>>> There are no test reports.
> >>>>>>>>>
> >>>>>>>>> Yes, I love impossible
> >>>>>>>>> challenges.......................................to
> >>>>>>>>> a point.
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>> Craig L. Prahl
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>> -----Original Message-----
> >>>>>>>>> From: Sprinklerforum [mailto:
> >>>>>>>>> [email protected]] On Behalf Of
> >>>>>>>>> Izzo, Salvatore
> >>>>>>>>> Sent: Monday, June 30, 2014 10:25 AM
> >>>>>>>>> To: [email protected]
> >>>>>>>>> Subject: RE: Identification of preaction system types
> >>>>>>>>>
> >>>>>>>>> If the warehouse is unheated, that is, if there is a chance of
> >>>>>>>>> freezing, it is my opinion that it would be doubtfulto find a
> >>>>>>>>> single interlock preaction system; therefore, it would likely
> >>>>>>>>> be a double interlock.  You could look at the design area on
> >>>>>>>>> the hydraulic placard ( if there is one) as one way of making
> the determination.
> >>>>>>>>> Take a look at the trim, and if you do not see a pneumatic
> >>>>>>>>> actuator in addition to the solenoid, it is likely that it is
> >>>>>>>>> an electric-electric type double interlock system.  This can be
> >>>>>>>>> verified by looking at the releasing panel input zones and
> >>>>>>>>> determining if the low air pressure switch is wired into an
> >>>>>>>>> alarm zone rather than a low air supervisory zone. Of course,
> >>>>>>>>> you can
> >>>> verify the manufacturer and compare to the data sheets as well.
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>> Regards,
> >>>>>>>>>
> >>>>>>>>> Salvatore J. Izzo III, P.E.  SFPE Manager - QA/QC Operations
> >>>>>>>>> Insurance Services Office Verisk Commercial Real Estate
> >>>>>>>>> 545 Washington Blvd.
> >>>>>>>>> Jersey City, NJ 07310 - 1686
> >>>>>>>>> t 201.469.2486
> >>>>>>>>> f 201.748.1942
> >>>>>>>>> c 732.533.7927
> >>>>>>>>> [email protected]
> >>>>>>>>> www.verisk.com/insurance
> >>>>>>>>>
> >>>>>>>>> Verisk Insurance Solutions ● ISO | AIR Worldwide | Xactware
> >>>>>>>>> -----Original
> >>>>>>>>> Message-----
> >>>>>>>>> From: Sprinklerforum [mailto:
> >>>>>>>>> [email protected]] On Behalf Of
> >>>>>>>>> [email protected]
> >>>>>>>>> Sent: Monday, June 30, 2014 9:13 AM
> >>>>>>>>> To: [email protected]
> >>>>>>>>> Subject: RE: Identification of preaction system types
> >>>>>>>>>
> >>>>>>>>> Ok, So what would be the tell-tale difference?
> >>>>>>>>>
> >>>>>>>>> Craig L. Prahl
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>>
> >>>>>>>>> -----Original Message-----
> >>>>>>>>> From: Sprinklerforum [mailto:
> >>>>>>>>> [email protected]] On Behalf Of
> >>>>>>>>> Johnson, Duane (NIH/OD/ORS) [C]
> >>>>>>>>> Sent: Monday, June 30, 2014 9:12 AM
> >>>>>>>>> To: '[email protected]'
> >>>>>>>>> Subject: RE: Identification of preaction system types
> >>>>>>>>>
> >>>>>>>>> Nope. You have to look at the trim on the preaction valve.
> >>>>>>>>>
> >>>>>>>>> Duane Johnson, PE
> >>>>>>>>> Program Manager
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)