Ok thanks. Might as well just calc them all. How demanding can 3 to 6 
sprinklers be anyhow?

> On Aug 24, 2014, at 10:20 AM, Todd - Work <[email protected]> wrote:
> 
> This is a fairly ornate house from the late 1800s that is being converted to 
> a B&B. The CT FIre Safety Code eliminates most requirements for sprinklers in 
> B&Bs (good lobby effort), but since they want to use the 3rd floor with the 
> open stair tower, some additional protection is being required. 
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 860-535-2080 (ofc)
> 
>> On Aug 24, 2014, at 6:50 AM, Brad Casterline <[email protected]> wrote:
>> 
>> I would I suppose Todd, because I can, but I am curious;
>> 
>> This is a new installation in a building with a stair tower, yet it is a 
>> limited Area System? 
>> 
>> If it is not too proprietary, will you paint a bigger picture?
>> 
>> Thanks, Brad.
>> 
>> 
>> 
>>> On Aug 20, 2014, at 7:30 PM, Todd - Work <[email protected]> wrote:
>>> 
>>> I am working on a project where they are installing a limited area system 
>>> per NFPA 101. The section calls for all of the heads within the compartment 
>>> to be included in the calculation. Does that apply if the compartment is a 
>>> stair tower and there are sprinklers on multiple levels? Would you 
>>> calculate all heads within the tower?
>>> 
>>> Todd G Williams, PE
>>> Fire Protection Design/Consulting
>>> Stonington, CT
>>> www.fpdc.com
>>> 860-535-2080 (ofc)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to