A good example of the tough time a Standard has covering all the bases; a
light hazard (.1) calc'd at .15, and if it was a small gift shop OHII (.2)
it could be calc'd at .15 ! I feel for A.H.J.s

Brad

-----Original Message-----
From: Duane Johnson [mailto:[email protected]] 
Sent: Monday, August 25, 2014 6:46 AM
To: [email protected]
Subject: RE: limited area system calcs

This provision is for a room serving no more than 6 sprinklers and comes
from:

NFPA 101:9.7.1.2 [2012] Sprinkler piping serving not more than six
sprinklers
for any isolated hazardous area shall be permitted to be
connected directly to a domestic water supply system having
a capacity sufficient to provide 0.15 gpm/ft2 (6.1 mm/min)
throughout the entire enclosed area. An indicating shutoff
valve, supervised in accordance with 9.7.2 or NFPA 13,
Standard for the Installation of Sprinkler Systems, shall be
installed in an accessible, visible location between the sprinklers
and the connection to the domestic water supply.

The handbook states that each room (of 6 sprinklers or less) can be
calculated separately. 

Duane Johnson

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Todd Williams
Sent: Sunday, August 24, 2014 1:21 PM
To: [email protected]
Subject: Re: limited area system calcs

The issue is that they have to be calculated to a .15 density and we have a
2" supply. 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com


> On Aug 24, 2014, at 11:46 AM, Brad Casterline <[email protected]>
wrote:
> 
> Ok thanks. Might as well just calc them all. How demanding can 3 to 6
sprinklers be anyhow?
> 
>> On Aug 24, 2014, at 10:20 AM, Todd - Work <[email protected]> wrote:
>> 
>> This is a fairly ornate house from the late 1800s that is being converted
to a B&B. The CT FIre Safety Code eliminates most requirements for
sprinklers in B&Bs (good lobby effort), but since they want to use the 3rd
floor with the open stair tower, some additional protection is being
required. 
>> 
>> Todd G Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> www.fpdc.com
>> 860-535-2080 (ofc)
>> 
>>> On Aug 24, 2014, at 6:50 AM, Brad Casterline <[email protected]>
wrote:
>>> 
>>> I would I suppose Todd, because I can, but I am curious;
>>> 
>>> This is a new installation in a building with a stair tower, yet it is a
limited Area System? 
>>> 
>>> If it is not too proprietary, will you paint a bigger picture?
>>> 
>>> Thanks, Brad.
>>> 
>>> 
>>> 
>>>> On Aug 20, 2014, at 7:30 PM, Todd - Work <[email protected]> wrote:
>>>> 
>>>> I am working on a project where they are installing a limited area
system per NFPA 101. The section calls for all of the heads within the
compartment to be included in the calculation. Does that apply if the
compartment is a stair tower and there are sprinklers on multiple levels?
Would you calculate all heads within the tower?
>>>> 
>>>> Todd G Williams, PE
>>>> Fire Protection Design/Consulting
>>>> Stonington, CT
>>>> www.fpdc.com
>>>> 860-535-2080 (ofc)
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to