Ouch! .15 in an 'occupancy' where the majority of floor area is egress path? 
And even in fully Sprinklered heads at the top and bottom only?


> On Aug 24, 2014, at 12:21 PM, Todd Williams <[email protected]> wrote:
> 
> The issue is that they have to be calculated to a .15 density and we have a 
> 2" supply. 
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080
> www.fpdc.com
> 
> 
>> On Aug 24, 2014, at 11:46 AM, Brad Casterline <[email protected]> 
>> wrote:
>> 
>> Ok thanks. Might as well just calc them all. How demanding can 3 to 6 
>> sprinklers be anyhow?
>> 
>>> On Aug 24, 2014, at 10:20 AM, Todd - Work <[email protected]> wrote:
>>> 
>>> This is a fairly ornate house from the late 1800s that is being converted 
>>> to a B&B. The CT FIre Safety Code eliminates most requirements for 
>>> sprinklers in B&Bs (good lobby effort), but since they want to use the 3rd 
>>> floor with the open stair tower, some additional protection is being 
>>> required. 
>>> 
>>> Todd G Williams, PE
>>> Fire Protection Design/Consulting
>>> Stonington, CT
>>> www.fpdc.com
>>> 860-535-2080 (ofc)
>>> 
>>>> On Aug 24, 2014, at 6:50 AM, Brad Casterline <[email protected]> 
>>>> wrote:
>>>> 
>>>> I would I suppose Todd, because I can, but I am curious;
>>>> 
>>>> This is a new installation in a building with a stair tower, yet it is a 
>>>> limited Area System? 
>>>> 
>>>> If it is not too proprietary, will you paint a bigger picture?
>>>> 
>>>> Thanks, Brad.
>>>> 
>>>> 
>>>> 
>>>>> On Aug 20, 2014, at 7:30 PM, Todd - Work <[email protected]> wrote:
>>>>> 
>>>>> I am working on a project where they are installing a limited area system 
>>>>> per NFPA 101. The section calls for all of the heads within the 
>>>>> compartment to be included in the calculation. Does that apply if the 
>>>>> compartment is a stair tower and there are sprinklers on multiple levels? 
>>>>> Would you calculate all heads within the tower?
>>>>> 
>>>>> Todd G Williams, PE
>>>>> Fire Protection Design/Consulting
>>>>> Stonington, CT
>>>>> www.fpdc.com
>>>>> 860-535-2080 (ofc)
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to