I agree Lamar, especially for Dry Systems-- nothing more aggravating and
senseless than to have 1000 Gallon capacities and be 50 pounds under the
curve!

Brad 

-----Original Message-----
From: Lamar Vaughn [mailto:[email protected]] 
Sent: Tuesday, September 16, 2014 12:04 PM
To: Sprinkler Forum
Subject: Re: Water Velocity

It would really be good if this thread could be shared with the engineering
community at large. I STILL get specifications that require a maximum
velocity of 20 fps. Very costly, especially when you have a good water
supply.

Lamar Vaughn, SET

On Tue, Sep 16, 2014 at 12:03 PM, Roland Huggins <[email protected]
> wrote:

> actually the difference between the results for D-W and H-W does not vary
> consistently (alas there is not a linear relationship).  To require using
> D-W at very high velocities is unnecessarily conservative.  At these
> velocities the pressure loss is so high that it is self regulating so
> typically occurs only is limited sections of the system.  With all the
> averaging etc that our process entails, why get anal on ONE piece of the
> puzzle?  Having said that, one could argue that one should account for the
> velocity pressure in the discharge calc at high velocities BUT that is
> needed only when you really have such velocities (like in a water spray
> deluge) verses seeing an assigned value from our process.
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
>
>
>
>
>
> On Sep 15, 2014, at 1:56 PM, Damien Shannon <[email protected]> wrote:
>
> > So purely along the lines of Andy Rooney's 'have you ever wondered why'
> :)
> > ... FM Datasheet 2-0, while not limiting the allowable velocity, does
> > require that when velocity exceed 30ft/sec, that the calculation be
> > performed via the Darcy-Weisbach Method rather than the Hazen-Williams.
> > Entertainment value only, but would seem that the variance between
> results
> > in Hazen-Williams versus Darcy-Weisbach become more apparent with higher
> > velocities.
> > The 30ft/sec limitation (for application of Hazen-Williams calculations)
> in
> > FM 2-0 is strangely close to the 10m/sec (32.8ft/sec) limitation in EN
> > 12845 Rules for Automatic Sprinkler Installations (previously BS 5306).
> >
> >
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to