It's not up to the contractor to determine or even theorize what gets 
sprinklered and what doesn't. The fact that the two structures are not attached 
is a factor, but a lot depends on how the two separate structures are justified 
in accordance with the building code. Therefore, you must ask the AHJ, who will 
review and approve your plans, whether or not the porte cochere should be 
protected. Actually, the architect should also know.

Galen Taylor
County of Los Angeles Fire Department
Fire Prevention Engineering
323-890-4339
[email protected]

"Ensuring Public Safety Through the Built Environment"

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tony Silva
Sent: Tuesday, September 16, 2014 12:04 PM
To: [email protected]
Subject: Porte Cochere

A building is designed to NFPA 13R. However, the local building code requires 
the sprinklering of "porches and balconies" notwithstanding the 13R permission 
for deletion. So say it is a 13 building. This building has a portico or porte 
cochere near the main entrance of the building, which is not attached to the 
building. I don't know the exact clearance between the two structures, but for 
argument sake, say they are 3 feet apart. The contractor claims the portico is 
not attached to the building, so doesn't need to be sprinklered. Any views from 
the forum?

Tony
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to