Tony,
If I understand your post, you are being asked to remove the sprinkler system
from the wood frame combustible Attic space?
Ask them to show you that in NFPA 13.
My copy of 13 states sprinklers may be omitted in an unused Attic of
non-combustible construction.
Regards,
G. Tim Stone
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638 TEL: (802) 434-2968 Fax: (802) 434-4343
[email protected]
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of Tony Liddic
Sent: Wednesday, November 19, 2014 8:44 AM
To: sprinklerforum
Subject: Frat House Attic Space
Just received a correction letter regarding a Frat House at a local university.
The 3 story building is a steel/concrete except for the Roof Structure which is
all FRT wood materials. No sprinklers required per NFPA
13 in concealed attic space.
How do I argue with this "logic"???
"3. Add sprinklers to attic space. This location has a history of residents
accessing the attic area and also breaching the ceiling and walls of the rooms
to "expand their living space" into the attic."
I guess we should have done more research on this project before bidding the
job with no attic sprinklers???
Thanks,
Tony Liddic, CET
MRH Sprinkler Design LLC
356 Laurel Glen Dr.
Springboro, OH 45066
937-369-7926
http://mrhsprinklerdesign.com
[email protected]
ᐧ
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org