Could someone explain to me the intent behind this code and if the Annex
is contradicting?

8.17.2* Fire Department Connections.

8.17.2.3* Size. The size of the pipe for the fire department
connection shall be in accordance with one of the following:

(3) For hydraulically calculated systems, the fire department
connection shall be permitted to be less than 4 in.
(100 mm) and no less than the size of system riser, where
serving one system riser.

A.8.17.2.3 The purpose of a fire department connection is to
supplement the pressure to an automatic fire sprinkler system.
It is not the intent to size the fire department connection piping based
on system demand. For multiple system risers supplied by a manifold, the
fire department connection need not be larger than that for an
individual system.

---