Could someone explain to me the intent behind this code and if the Annex is contradicting?
8.17.2* Fire Department Connections. 8.17.2.3* Size. The size of the pipe for the fire department connection shall be in accordance with one of the following: (3) For hydraulically calculated systems, the fire department connection shall be permitted to be less than 4 in. (100 mm) and no less than the size of system riser, where serving one system riser. A.8.17.2.3 The purpose of a fire department connection is to supplement the pressure to an automatic fire sprinkler system. It is not the intent to size the fire department connection piping based on system demand. For multiple system risers supplied by a manifold, the fire department connection need not be larger than that for an individual system. --- This email has been checked for viruses by Avast antivirus software. http://www.avast.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
