NFPA  13 is a minimum design /installation Standard, NOT A CODE.

Fire department Pump Trucks are equipped with variable pressure pumps which
enables the pump operator to increase extra boost when needed.
I don't see any contradiction.
 
Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

                117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
                           [email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Cory Power
Sent: Tuesday, November 25, 2014 8:39 AM
To: [email protected]
Subject: Contradiction if FDC codes? NFPA 13 2013

Could someone explain to me the intent behind this code and if the Annex is
contradicting?

8.17.2* Fire Department Connections.

8.17.2.3* Size. The size of the pipe for the fire department connection
shall be in accordance with one of the following:

(3) For hydraulically calculated systems, the fire department connection
shall be permitted to be less than 4 in.
(100 mm) and no less than the size of system riser, where serving one system
riser.

A.8.17.2.3 The purpose of a fire department connection is to supplement the
pressure to an automatic fire sprinkler system.
It is not the intent to size the fire department connection piping based on
system demand. For multiple system risers supplied by a manifold, the fire
department connection need not be larger than that for an individual system.

---
This email has been checked for viruses by Avast antivirus software.
http://www.avast.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to