The change was made because reviewers were requiring many inlets when system 
demand was high (aka mains were being the 4”).  The old text said FDC shall be 
a minimum 4” so some extrapolated that to if supply main was bigger so should 
the FDC.  Supplement is technically incorrect since as you said 99.9% of the 
time only one or the other is feeding the system but it fixed the old 
misunderstanding.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Nov 25, 2014, at 6:12 AM, [email protected] wrote:
> 
> noun: supplement; plural noun: supplements - something that completes or 
> enhances something else when added to it.
> 
> How can the possibly pressure be supplemented? Using enough pressure to open 
> the FDC check valve will close the valve in the riser. The rule should be 
> changed to either calculated or just require a 4" 2-way FDC for everything.
> 
> There are buildings in Phoenix with 12 -  2 1/2 " FDC inlets because of an 
> old amendment requiring one 2.5" inlet for every 250 gpm system demand. The 
> rule was changed when the FD figured out that a pumper truck only carried 
> enough equipment to connect to four inlets.
> Ron F