FDC sizing is not calculated, and 8.17.2.3 prescribes the sizes based on the riser size ( >4" use 4", <4" use the size of the riser pipe). The annex material is further clarifying that the intent is not to hydraulically calculate the FDC piping to meet the system demand, the FDC is considered supplemental for automatic sprinkler systems so it's size is not calculated.
Mike Morey, CFPS, SET Planner Scheduler/Designer BMWC Constructors, Inc. 1740 W. Michigan St, Indianapolis, IN 46222 O: 317.651.0596 | C: 317.586.8111 [email protected] | www.bmwc.com ________________________________________ From: Sprinklerforum <[email protected]> on behalf of Cory Power <[email protected]> Sent: Tuesday, November 25, 2014 8:39 AM To: [email protected] Subject: Contradiction if FDC codes? NFPA 13 2013 Could someone explain to me the intent behind this code and if the Annex is contradicting? 8.17.2* Fire Department Connections. 8.17.2.3* Size. The size of the pipe for the fire department connection shall be in accordance with one of the following: (3) For hydraulically calculated systems, the fire department connection shall be permitted to be less than 4 in. (100 mm) and no less than the size of system riser, where serving one system riser. A.8.17.2.3 The purpose of a fire department connection is to supplement the pressure to an automatic fire sprinkler system. It is not the intent to size the fire department connection piping based on system demand. For multiple system risers supplied by a manifold, the fire department connection need not be larger than that for an individual system. --- This email has been checked for viruses by Avast antivirus software. http://www.avast.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org