At 4 hydrants simultaneously if they're on the same water supply, or in 
combination of public and private or at however many hydrants you have if fewer 
than 4 and those being the sole source of fire flow.

As other comments, I would reiterate that the Table B fire flow is for outside 
hose streams only and completely separate and apart from any hydraulic demand 
related to building sprinkler systems.

Steve L.




<div>-------- Original message --------</div><div>From: [email protected] 
</div><div>Date:12/05/2014  6:29 PM  (GMT-08:00) </div><div>To: 
[email protected] </div><div>Subject: Re: A Poll of the 
Experienced </div><div>
</div>I think I agree with you, but to be very specific, let's assume I'm 
designing a new building on a greenfield site which is served by a public water 
system. The building is type V construction, 600,000 square feet and fully 
protected with ESFR sprinklers. Table B105.2 indicated a fire flow rate of 8000 
GPM, reduced to 4000 GPM for sprinkler credit, at minimum 20psi. My question 
is, WHERE is this 4000 GPM at 20 psi measured? At the city water main 
connection? Or at the fire pump discharge? 

Mark at Aero
602 820-7894

Sent from my iPhone

> On Dec 5, 2014, at 7:17 PM, "Cahill, Christopher" <[email protected]> 
> wrote:
> 
> Neither.  It's the flow you need for a building. You might get it from a muni 
> or private. Absolutely nothing to do with sprinklers except you get a 
> reduction if building is sprinklered.
> 
> 
> Chris Cahill
> Fire Protection Engineer
> Burns & McDonnell
> 952-656-3652
> [email protected]
> 
> 
> -------- Original message --------
> From: [email protected]
> Date:12/05/2014 8:12 PM (GMT-06:00)
> To: [email protected]
> Subject: A Poll of the Experienced
> 
> Over this weekend I'd like to ask the opinion of those forumites experienced 
> in the reading and understanding of the "International Fire  Code" on the 
> topic of "Fire Flow" described in Chapter 5, and further prescribed in 
> Appendix B. Is the available flow rate and residual pressure referenced, 
> intended to describe these values of the municipal or private water supply 
> available to the building site? Or, the minimum output of any fire pump 
> associated specifically with the automatic sprinkler system in the building?
> Any takers? Questions? Clarifications?
> Thanks for any answers.
> 
> Mark at Aero
> 602 820-7894
> 
> Sent from my iPhone
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to